We've just spent an overnight in a hotel. In the bathroom it had an electric (oil filled I assume) heated towel rail/radiator. This was powered via a switched, fused spur with a flex outlet that was positioned approximately 6” off the floor and about 3” away from the bath panel at the opposite end to the taps. This spur was also controlled from one switch in a twin light switch outside the bathroom (the other switch controlled the bathroom lights). Seemed strange to me - was that legal?
 
Sponsored Links
Nothing to do with the law.

The regulations do not allow switches within 600mm. of the bath or similar. Unswitched FCU would be alright.
 
Thanks. No, I didn’t take a photo. I thought it didn’t seem right. I think I’ll let the hotel know.
 
Sponsored Links
Nothing to do with the law.

Fair point. Perhaps 'would that be compliant?' should be the question.

But as it's a hotel, a failure in electrical 'compliance' might just bring into question other legal requirements regarding the health and safety of their 'customers'.
 
Last edited:
This is what I got back:

Thank you for your email.

We organised for our nominated qualified electrical company to visit the hotel to look at the switch in room 34 to which you refer. It was found to be compliant, RCD protected.

Our guest enjoyment and safety is always a priority to us. We do appreciate you bringing this to our attention.

Assuring you of our best intention at all times


Oh well, didn’t seem right to me, a switched spur fitted a couple of inches from the bath but what the F do I know?
 
Switches within 600mm. of the edge of a bath are not compliant with BS7671 The Wiring Regulations.

701.512.3 Erection of switchgear, controlgear and accessories according to external
influences
The following requirements do not apply to switches and controls which are incorporated in fixed current-using
equipment suitable for use in that zone or to insulating pull cords of cord operated switches.
In zone 0:
switchgear or accessories shall not be installed.
In zone 1:
only switches of SELV circuits supplied at a nominal voltage not exceeding 12 V AC rms or 30 V ripple-free
DC shall be installed, the safety source being installed outside zones 0, 1 and 2.
In zone 2:
switchgear, accessories incorporating switches or socket-outlets shall not be installed with the exception of:
(i) switches and socket-outlets of SELV circuits, the safety source being installed outside zones 0, 1 and 2,
and
(ii) shaver supply units complying with BS EN 61558-2-5.
Except for SELV socket-outlets complying with Section 414 and shaver supply units complying with
BS EN 61558-2-5, socket-outlets are prohibited within a distance of 3 m horizontally from the boundary of zone 1.


The RCD is irrelevant.
 
Oh well, didn’t seem right to me, a switched spur fitted a couple of inches from the bath but what the F do I know?
More than them, and more than their "qualified electrical company", it would seem.

This is an image of the relevant page in the current version of the Wiring Regulations:

upload_2019-2-25_21-19-39.png


And here are diagrams showing the boundaries of the Zones:

upload_2019-2-25_21-22-5.png


upload_2019-2-25_21-22-56.png


That FCU is in Zone 2, and that hasn't been allowed for as long as anybody here can remember.

You should pursue this, ideally. Not because it's dangerous - in reality it probably isn't, but because this is outrageous:

Thank you for your email.

We organised for our nominated qualified electrical company to visit the hotel to look at the switch in room 34 to which you refer. It was found to be compliant, RCD protected.

Our guest enjoyment and safety is always a priority to us. We do appreciate you bringing this to our attention.

Assuring you of our best intention at all times

That's either a lie, or their "qualified electrical company" isn't, and needs a severe kicking.

You can understand the hotel being reluctant to have it found to be non-compliant - they may have at least 33 other rooms like it which they'd have to fix.

If you do decide to pursue it, also write to the local authority, as they are responsible for H&S enforcement (would do no harm to cc the HSE), and if it's a chain, also head office. Always write the letters so that each recipient knows full well who it's been copied to - the manager there is probably more likely to sit up and take notice if he knows that the council, the HSE and his head office have also been made aware of the problem.
 
I think I’m wasting my time. I sent them the info you both gave on here and this is the reply I’ve just received, pukka grammar too!

Thank you for all the information you have send to us regarding the towel rail in room 34 where you stayed.

We are currently dealing with this issue and can assure you that all British Safety Regulations are followed in our hotels. We only use certified electrical companies to do our Hard wire tests, PAT and any other electrical work in the hotels.

As Health and Safety Coordinator, I want to insure you that we take Health and Safety serious and that we are doing everything we can to ensure our guests is safe.

If you have any further questions or comments, please feel free to contact me on this email address and I will assist you as much as I can.

Kind Regards
Anja Shaw

Health and Safety Coordinator
The Hotel Folk
 
They are currently dealing with the issue... of course they are, so can you expect a further reply??

Nah.

I reckon we need a written report from the electrical contractor who has been investigating the issue.
 

DIYnot Local

Staff member

If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

Select the supplier or trade you require, enter your location to begin your search.


Are you a trade or supplier? You can create your listing free at DIYnot Local

 
Sponsored Links
Back
Top