Tank thermostat feasibility.

Joined
5 Sep 2007
Messages
46
Reaction score
0
Location
Cheshire
Country
United Kingdom
My system uses a Honeywell ST699 programmer which is working fine. but there is only a two way valve employed which limits the flexibility a bit.

I have just purchased an ACL Drayton cylinder thermostat and would like to use it in the following way.

Presently the timer simply provides 240Volt mains to start the boiler, and also another seperate 240Volt supply to the 2 way valve motor when hot cylinder water is selected either via the timer switch or manually by pressing the button on the bottom slider.

The new cylinder thermostat has a pair of normally open and a pair of normally closed contacts, and my idea is simply to interupt the 2 way valve supply, and feed the live conductor via the thermostat normally closed contacts.

This will mean that until the tank water reaches the required temperature the programmer will still control the valve condition but at the preset point the supply will be opened giving the system both timed and temperature control for the hot water.

I am a fully qualified long term electronics engineer and know it will work, but would like to know from the plumbing point of view could it cause any problems.

The timer unit is easily accessed in the airing cupboard, as is the valve motor feed wiring, making it about an hours job, rather than tearing up the bedroom floor boards to fit a different valve.

Regards Ravel.
 
Sponsored Links
Presently the timer simply provides 240Volt mains to start the boiler, and also another seperate 240Volt supply to the 2 way valve motor when hot cylinder water is selected either via the timer switch or manually by pressing the button on the bottom slider.

Well if it really does that its unusual !!!

The normal way to wire it is to power the valve which opens and WHEN its open it operates a microswitch which powers the boiler and pump.

Perhaps you dont understand your system quite as well as you think?

Tony
 
This means that your central heating is on all the time the boiler is on.

Are you sure you understand how your system works? Are you Brahms?
 
Presently the timer simply provides 240Volt mains to start the boiler, and also another seperate 240Volt supply to the 2 way valve motor when hot cylinder water is selected either via the timer switch or manually by pressing the button on the bottom slider.

Well if it really does that its unusual !!!

The normal way to wire it is to power the valve which opens and WHEN its open it operates a microswitch which powers the boiler and pump.

Perhaps you dont understand your system quite as well as you think?

Tony

Hello Tony, and thanks for your reply, and I can assure you that's how my Worcester Greenstar 30CDi conventional is wired which is confirmed by the Worcester instruction manual, and there is no micro switch in the valve, just pipe in/pipe out, and switched 240V and earth.

The external pump is fed from terminal block "ST2" and the ST10 terminal block has permanent 240volts applied to "L&N" with a timer switched 240 volts live to "LR" sorry I omitted to mention this one
hence Simon in his post thinking the boiler was always on.

Regards Ravel.
 
Sponsored Links
This means that your central heating is on all the time the boiler is on.

Are you sure you understand how your system works? Are you Brahms?

Hi Simon please see my reply to Tony above which hopefully now makes more sense :D

Regards Ravel.
 