i work for a maintenance firm as there inhouse electrician and we also have subbies
anyway i was looking at one of there pir,s and i noticed the readings on the ringmain sockets was a bit out on the continuity readings were
L=o.44ohms n= 0.67ohms and the cpc was= 0.77
doing the quick calculation i no that the n to n is to high
this report got a satisfactory result and nothing marked on the sheet about it ( no codes ect )
is this right or wrong me personaly i would fix the fault there and then
its a domestic flat