Voltage transformers are occasionally used to adapt voltage protective relays and instruments with nominal voltage of main circuit in low voltage switchgears.
In an electrical panel test program an interesting thing was observed. In the panel a three phase voltage transformer with following technical characteristics was used to adapt one 110 V AC under voltage relay with main bus bar voltage.



Voltage Ratio: 380/110 V

Connection: YnYn

Rated power: 60 VA

Construction: Core type

Accuracy class: 3P



The under voltage relay was three phase and microprocessor base made by an authentic company.

The acceptance tests on the individual relay were done successfully, but the under voltage relay in combination with voltage transformer didn’t have suitable reflection against actual one phase under voltage in primary system that was simulated by removing one of three phase fuses in primary side of the voltage transformer.(Really, no under voltage was observed

by the relay.) All wire interconnections and related circuits also voltage transformer was rechecked again and every thing was very well. The relevant test men couldn't explain the reason of behavior of circuit. It seemed that interface circuits or devices didn’t work correctly.



How can you explain the reason of non activity of that protection system against primary under voltage?
 
Sponsored Links
Iwould have thought the relay was designed to detect a volt drop on all three phases simultaneously, rather than just one individual phase going down, but I am no expert in this area.There are a lot smarter people on here who may be able to help you , but if you get no advice try here http://www.theiet.org/forums/forum/
 
As the three pairs of windings share the same magnetic core the secondary without an input to its primary will have an ouput and this could be high enough to be seen as "good" by the monitoring relay.

Also there could be a voltage on the phase without fuse due to other three phase equipment feeding back onto the open circuit phase.
 
Sponsored Links
bernardgreen said:
As the three pairs of windings share the same magnetic core the secondary without an input to its primary will have an ouput and this could be high enough to be seen as "good" by the monitoring relay.

Also there could be a voltage on the phase without fuse due to other three phase equipment feeding back onto the open circuit phase.


Thank you, your answer is correct.