Hi all,
I know that questions similar to this have been asked before but I could not find a relevant answer so here goes...
I have an existing CU (early 90s with cartridge fuses) that is being replaced with a 15way unit as part of a house extension. The existing system was 'expanded' some time ago for a garage/office feed. The supply for the garage is fed through a 20A fuse and then into a ~20A 30ma RCD which is fitted to the side of the CU, it then goes via SWA to the garage where there is a DP isolator.
[there is a host of other switched stuff around the CU such as bell transformers and immersion heaters which will also be cleaned up in the process]
Given that we don't want to touch the garage side of things if at all possible is how to adequately protect the outbuilding and 'incorporate' the old RCD into the new CU?
I cannot seem to find a suitable DP RCCB (Wylex brand) so how best to configure the system.
My current thought would be to put a 20A DP MCB in the CU with the live feed then fed through an adjacent RCCB/RCBO?
I know that questions similar to this have been asked before but I could not find a relevant answer so here goes...
I have an existing CU (early 90s with cartridge fuses) that is being replaced with a 15way unit as part of a house extension. The existing system was 'expanded' some time ago for a garage/office feed. The supply for the garage is fed through a 20A fuse and then into a ~20A 30ma RCD which is fitted to the side of the CU, it then goes via SWA to the garage where there is a DP isolator.
[there is a host of other switched stuff around the CU such as bell transformers and immersion heaters which will also be cleaned up in the process]
Given that we don't want to touch the garage side of things if at all possible is how to adequately protect the outbuilding and 'incorporate' the old RCD into the new CU?
I cannot seem to find a suitable DP RCCB (Wylex brand) so how best to configure the system.
My current thought would be to put a 20A DP MCB in the CU with the live feed then fed through an adjacent RCCB/RCBO?