Remember this? //www.diynot.com/forums/viewtopic.php?t=69140&postdays=0&postorder=asc&start=0
Well, I've had another case of RP at a different property...this time, unfortunately, we have not got to the bottom of it, so I am unable to satisfy you with the solution!
It is a house with subterranean TT and no incoming earth. The only connection is via the gas pipe, with a Zs of around 9 ohms.
There is no RCD.
Every circuit has RP. Also, the cellar room where the CU was lit up with a volt stick on everything, pipes, walls, floors, ceilings: everything! And the meter was going like stink. I mean really motoring.
Until, I discovered, one very warm 30A socket circuit fuse was removed. When this happened, polarity returned to normal, the meter slowed to a crawl & the volt stick stopped the red-alert.
I went round and disconnected everything I could find throughout the whole house as did the customers, but it was still going like the clappers.
Obviously a problem! Out of interest, I checked the line ring continuity. There were four 2.5 conductors in that fuseway, none of which showed any connection to the others. I then thought maybe there had been a mix up with some other conductors & checked continuity between these four and two other 2.5's in a 15A fuseway (the only other 2.5's in the board). There was continuity between one of the 30A conductors and one of the 15A ones, a reading of 221 Ohms, but >1999 between the others.
There were three things I was puzzling about - when this wiring was in circuit:
Why did polarity reverse?
Why did the CU room light up with a volt stick?
Why did the meter go mad, despite everything having been disconnected?
Could there have been a fault on that circuit with such a resistance that it was acting like a high-current load?
IR for that 30A, four-wire circuit was around 40Meg to earth, method 2, so I suppose that there must've been something there, to give such a comparitively low reading, but none of us could find what it was.
[Loyd Grossman voice] "David, it's over to you..."
Well, I've had another case of RP at a different property...this time, unfortunately, we have not got to the bottom of it, so I am unable to satisfy you with the solution!
It is a house with subterranean TT and no incoming earth. The only connection is via the gas pipe, with a Zs of around 9 ohms.
There is no RCD.
Every circuit has RP. Also, the cellar room where the CU was lit up with a volt stick on everything, pipes, walls, floors, ceilings: everything! And the meter was going like stink. I mean really motoring.
Until, I discovered, one very warm 30A socket circuit fuse was removed. When this happened, polarity returned to normal, the meter slowed to a crawl & the volt stick stopped the red-alert.
I went round and disconnected everything I could find throughout the whole house as did the customers, but it was still going like the clappers.
Obviously a problem! Out of interest, I checked the line ring continuity. There were four 2.5 conductors in that fuseway, none of which showed any connection to the others. I then thought maybe there had been a mix up with some other conductors & checked continuity between these four and two other 2.5's in a 15A fuseway (the only other 2.5's in the board). There was continuity between one of the 30A conductors and one of the 15A ones, a reading of 221 Ohms, but >1999 between the others.
There were three things I was puzzling about - when this wiring was in circuit:
Why did polarity reverse?
Why did the CU room light up with a volt stick?
Why did the meter go mad, despite everything having been disconnected?
Could there have been a fault on that circuit with such a resistance that it was acting like a high-current load?
IR for that 30A, four-wire circuit was around 40Meg to earth, method 2, so I suppose that there must've been something there, to give such a comparitively low reading, but none of us could find what it was.
[Loyd Grossman voice] "David, it's over to you..."