I moved this boiler about 600mm over to one side
making it only 3 m of pipe work away form the meter with 4 elbows the pipe work is in 22mm
it has worked fine for years with more pipe work
as soon as I moved it it comes up with code 29 meaning low gas or no gas
the working press at the meter is 23mb
the standing at meter is 25mb
the standing at the inlet on gas valve is 24mb
the working at inlet on gas valve is 17mb at full rate
no blockages in pipe work
Taken the gas valve apart cleaned up put back still the same
Do you think the gas valve could be broke
I have run out of things to try and they have no boiler
Can any one help
Vaillant help line are rubbish
I am Corgi (300880) B F L
Thanks For your time