There are two lights on the receiver. Red and Green
The Red light shows that there is power present, and the Green light shows that the heating is (or should be) 'on'. [It looks to be on in your photo]
If you turn the thermostat up and down past the current room temperature, does the green light go 'on' and 'off' accordingly? Wait a few minutes each time, because the thermostat and receiver don't communicate with each other continually. If the green light does go 'on' and 'off' the thermostat is OK, but there is a problem with the receiver or boiler.
Only if the light does go 'on' and 'off' as dictated by the thermostat, and if you are capable of making a test safely you could try this. Isolate the power, access the wiring at the back of the receiver and you should see two terminals marked COM & NO. Note where the wires are connected so that you can put them back afterwards and then without disturbing the existing wires, either insert a wire to link the two terminals together, or put the wire(s) from NO into the COM terminal with the other wire(s) already there. Restore power and if the boiler works now, the receiver is faulty. if it doesn't there is a problem with the boiler, or its wiring. Don't do this test if you are not competent, or have any doubts. Any questions post back.
If the green light doesn't work as described the thermostat or receiver are at fault.