Hi,
Came back to a cold house (digs) last night and the radiators were lukewarm. It's an old house and loses heat like it's going out of fashion so needs warm radiators. The CH temp on the front of the boiler is set to 75C and the radiators are probably reaching about 40C.
Cracked a couple of the bleed valves on the radiators upstairs and no air up there. So after a wrestle with the Vaillant manual had a look at what's going on on the boiler panel and found code S.53 showing "Appliance is within the waiting period of the operation block function due to water shortage (VL-RL spread too big)".
So that kind of diagnoses what's wrong (though with the system showing low water I'd have expected there to be some air in the upstairs rads). Can't find the fill loop anywhere round the boiler itself though! Not sure what VL-RL is as it's not explained, but I guess low water should be cured by refilling the system?
After reading the section of the manual covering test programs, I was wondering whether it needed a fill loop at all as it's quite a whizzy boiler, so tried activating the relevant ones:
P.0 Bleeding test program. The heating circuit and hot water circuit (when accessories are fitted) is bled via the automatic air vent (the cap on the automatic air vent must be loosened).
This one flashed up "HP" when activated and nowhere in the manual does it explain where the automatic air vent might be so I can loosen it. Nor does it explain what "HP" is.
P.6 Filling test program. The diverter valve moves to the centre position
I had assumed that this program would negate the need for a fill loop as I can't find one. When activated, the display flashes up "- bar" which I think means it's too low for it to read. Activating the test program did not result in any noises of water filling the system.
Think I've done all I can now, so any ideas?
Post the above and some googling on the VL-RL issue, I reset the d.0 part load to 28 (S.53 still came up). Reset it again to 20 and things seem to be better.
Also, went into the most recent Fault code storage and found two F.72 codes present - Flow and/or return NTC fault. Flow and/or return NTC is defective (tolerances too big). Also a F.24 code - Water shortage, temperature rise too quick. Pump blocked, insufficient pump output, air in appliance, water pressure too low
Came back to a cold house (digs) last night and the radiators were lukewarm. It's an old house and loses heat like it's going out of fashion so needs warm radiators. The CH temp on the front of the boiler is set to 75C and the radiators are probably reaching about 40C.
Cracked a couple of the bleed valves on the radiators upstairs and no air up there. So after a wrestle with the Vaillant manual had a look at what's going on on the boiler panel and found code S.53 showing "Appliance is within the waiting period of the operation block function due to water shortage (VL-RL spread too big)".
So that kind of diagnoses what's wrong (though with the system showing low water I'd have expected there to be some air in the upstairs rads). Can't find the fill loop anywhere round the boiler itself though! Not sure what VL-RL is as it's not explained, but I guess low water should be cured by refilling the system?
After reading the section of the manual covering test programs, I was wondering whether it needed a fill loop at all as it's quite a whizzy boiler, so tried activating the relevant ones:
P.0 Bleeding test program. The heating circuit and hot water circuit (when accessories are fitted) is bled via the automatic air vent (the cap on the automatic air vent must be loosened).
This one flashed up "HP" when activated and nowhere in the manual does it explain where the automatic air vent might be so I can loosen it. Nor does it explain what "HP" is.
P.6 Filling test program. The diverter valve moves to the centre position
I had assumed that this program would negate the need for a fill loop as I can't find one. When activated, the display flashes up "- bar" which I think means it's too low for it to read. Activating the test program did not result in any noises of water filling the system.
Think I've done all I can now, so any ideas?
Post the above and some googling on the VL-RL issue, I reset the d.0 part load to 28 (S.53 still came up). Reset it again to 20 and things seem to be better.
Also, went into the most recent Fault code storage and found two F.72 codes present - Flow and/or return NTC fault. Flow and/or return NTC is defective (tolerances too big). Also a F.24 code - Water shortage, temperature rise too quick. Pump blocked, insufficient pump output, air in appliance, water pressure too low