johnmf
hi......
ive got a 3 phase db to do some work on at work.
the mains supply is 3 phase (185mm conductors) protected by 315A bs88's which goes through a mains isolator. this isolator feeds a busbar chamber off which the board that needs working on is running.
problem is that the earth fault loop impedance readings at the board were below 0.01!!!!
likewise the pfc ( between any phase and earth) was above 19KA!!
at first these readings seemed unlikely but then i remembered that the substation is actually in the premises of the factory(about 20 metres away)!
wanted to fit a new board but dont think they'l be rated to 19KA. any ideas anyone?
ive got a 3 phase db to do some work on at work.
the mains supply is 3 phase (185mm conductors) protected by 315A bs88's which goes through a mains isolator. this isolator feeds a busbar chamber off which the board that needs working on is running.
problem is that the earth fault loop impedance readings at the board were below 0.01!!!!
likewise the pfc ( between any phase and earth) was above 19KA!!
at first these readings seemed unlikely but then i remembered that the substation is actually in the premises of the factory(about 20 metres away)!
wanted to fit a new board but dont think they'l be rated to 19KA. any ideas anyone?