raistrick said:
my children are starting to smell!!
Glad to see that your childrens' sense of smell is developing normally
Heres the relevant bumf out of the manual so you have the official version
If during the ignition attempt period (10 secs
approx.) the boiler fails to light, the ignition
control circuit will go to lockout. This is indicated
by the status LED (14) flashing red
accompanied by a flashing error code 01
shown in the temperature indicator (15). The
gas valve is de-energised, but leaves the fan
and pump running for approximately 2 minutes
after lockout.
01: Failure to ignite (see 6.5.5). To re-set
turn mode selector switch to re-set position
for approximately 10 seconds, then
back to original position.