They have 300mS to operate at I delta n if a BS EN type, or 200mS for older BS types. 40mS is only for 5I delta n where the RCD is being used to provide additional protection.
There are so many "what if" scenarios for something like this. I've used an isolation transformer for years for working on older live-chassis equipment, but you still have other hazards present which neither an isolation transformer on the supply nor an RCD/GFCI on the supply will reduce even if it's not live-chassis apparatus: HT supplies of hundreds of volts or several kilovolts in valve TV sets, transmitters, etc.
Meanwhile, away from the willy waving ...
I have a 110V wall mounted transformer sat in the corner of the garage that came out of a school when it closed down. Seemed like a good idea at the time. It's both centre tapped earth and has a current trip with several turns of the centre tap earth through it's sensing hole which IIRC takes the nominal trip current down to 10mA or could be something less.
At 6th form, IIRC they reckoned they had one or two items of equipment that would frequently trip the supply in the physics lab due to the sensitive nature of the protection.
That's a problem with the the 5mA GFCI devices here. They might be fine to protect an outlet in a bathroom but try feeding a dozen outlets on a test bench thtough one GFCI and you'll likely end up finding it impossible to run certain combinations of equipment simultaneously due to the ground current (by design, especially in some older pieces of equipment).