I am new to UK wiring, having done quite a bit of DIY in Canada, and was looking over the rules here.
I am looking at BS7671:2018 543.7.1.203 and it looks like circuits with sockets where the earth leakage can exceed 10mA require two paths to earth. This comes naturally with a ring circuit, but what about radial circuits? Since radials can be branched, do you need a separate earth path back to the CU from every leaf of the tree?
It also says in 543.2.6 that you can bond to other metal items as a path to earth. Does this mean that you can you just bond to the heating system piping if in copper? (assuming it is bonded to the earth in the CU).
We have a lot of computers and other devices with switched power supplies, so it could be possible to go over 10mA, I think.
I am looking at BS7671:2018 543.7.1.203 and it looks like circuits with sockets where the earth leakage can exceed 10mA require two paths to earth. This comes naturally with a ring circuit, but what about radial circuits? Since radials can be branched, do you need a separate earth path back to the CU from every leaf of the tree?