Assuming you mean a 32A fuse, it is the wrong size. 8.5kW is about 35A.8.5kw it has 6mm cable and the fuse is 32w
Both 8.5kW and 9kW showers really should be on 40A circuits. Also, as has been said/implied, you're really meant to get approval/permission from your electricity supplier before installing two electric showers in a domestic property.There are two fuses, one for each shower, both say 32B on them. Been there for at least 10 years, I am sure the other one is a 9kw. ... Is this a problem that i need to get looked at? There are a couple of spare 40A fuses I think after the new kitchen was put onto a different fusebox.
Actually, I think, about 8kW (at 230V, assuming that the 8kW relates to 240V). However, my point remains - that the OP would need 40A circuits for both 8.5kW and 9kW (at 240V) showers.A 32A circuit can only support a shower of 7.6kW (assuming a 240V rating, which most shower makers still quote).
I won't insult you by telling you the answer to that!240 x 32 = _________ ?
No problem. We all live in the same glasshouse, and you know what that means!Ah - I see your point - sorry.