Ah, I see! The 'transformer' is, indeed, rated at 10-20W at 12V (as has been said, not enough for you). the 30V and 10A are merely the maximum ratings of the 'distributor' (basically just a junction box).
Ah, I see! The 'transformer' is, indeed, rated at 10-20W at 12V (as has been said, not enough for you). the 30V and 10A are merely the maximum ratings of the 'distributor' (basically just a junction box).
Quite so. We didn't even know that there was a 'distributor' (with voltage and current ratings) until a picture of it popped up - I don't think I can blame myself for having been confused
The 60w transformer looks to be one that needs to be in an enclosure of some nature. You can get them which don't need an external enclosure such as here: http://www.tlc-direct.co.uk/Products/TLET60.html
As for the cable, mains two core cable (min 0.75mm) will do. I wouldn't bother with car wire.
As another option, you may use the transformer you have to run two lights and buy another one to run the other two.
Methinks therein lies a can of worms The 'voltage drop 'limit " to which you refer (per 6.4 of 'informative' Appendix 4 of the regs) is to be measured from 'the origin of the installation' and is expressed as a percentage of 'the nominal voltage of the installation' (aka 230V)
You can apply a % to anything. It may or not make sense to use 3% as the limit for an ELV lighting circuit - I don't know, which is why I put the word in quotes. (That's the problem with persistently misusing quotes - you forget what they actually signify.)
But if you don't ignore that 3% it can get eaten up quite quickly with incandescent ELV lighting.
As a generalisation, indeed one can. However, I thought you were referring to Appendix 4 of the regs, and 6.4 thereof indicates that the 3% figure referred to in Table 4Ab means "3% of the nominal voltage of the installation" (i.e. 3% of 230V, aka 6.9V)!
It may or not make sense to use 3% as the limit for an ELV lighting circuit - I don't know, which is why I put the word in quotes. (That's the problem with persistently misusing quotes - you forget what they actually signify.)
I'm probably the world's greatest culprit as regards use of quotes! On this occasion, I thought you put 'limit' in quotes because it is essentially a recommendation in an 'informative' Appendix, rather than the 'regulation' which so many think it is!
As for what 'makes sense' or is appropriate for ELV lighting, it's fairly complicated. If we wish to remain consistent with the usual practice with LV lighting, I suppose that we should think in terms of the 'equivalent LV voltage drop' (** see below) expressed as a percentage of the nominal LV supply voltage - and, if we did that, I imagine that it would probably still be appropriate to apply the 3% 'limit'.
** I suppose the 'equivalent LV voltage drop' would be calculated as the actual VD in the LV wiring PLUS (the VD in the ELV wiring multiplied by the LV/ELV ratio of the transformer or PSU)
most of them transformers limit the output length to the lamp at less than two metres,for EMC reasons, hence I assume one reason why the wickes fittings are prewired with plugs to allow the distribution box to star wire them
If you need to find a tradesperson to get your job done, please try our local search below,
or if you are doing it yourself you can find suppliers local to you.
Select the supplier or trade you require, enter your location to begin your search.
Please select a service and enter a location to continue...
Are you a trade or supplier? You can create your listing free at DIYnot Local