If you are referring to my question, it did not relate to VD (which, quite honestly, I find it difficult to get excited about) but, rather, EFLI - in particular confirming that Zs is low enough to provide the required disconnection times.Your question is very valid as I know my boss never calculated volt drop it was me as the site electrician who would suggest maybe he should use thicker cable and until the loop impedance meter was used really we had only a guess at the result.
If an electrician measures Zs on an unloaded circuit (with conductors at ambient temperature) and finds that it is 'just low enough' to achieve the required disconnection times, then if that circuit becomes heavily loaded (hence much higher conductor temperatures), then the Zs may well rise to a level which is no longer low enough to satisfy the ADS requirements. What are your views about this?
Kind Regards, John