i would like to clarify the wring on my new shower before i switch on, i will get an electrician in to check everything.
i have an triton aquatronic 2 7.5kw shower fitted. i've ran 6mm to a 45amp switch outside the bathroom door and ran 6mm back to the consumer unit. all wiring is run in uninsulated wall cavities and above the insulation, on top of the joists in the loft. the water feed is taken off the cold water tank feed, which is fed directly from the mains. at the consumer unit i have a 40 amp mcb. my current consumer unit is rated at 100 amps i can either fit the mcb in the unit as i have spare places or i could fit a 2 way seperate enclosure.
which is better? or is it something else altogether
thanks in advance
i have an triton aquatronic 2 7.5kw shower fitted. i've ran 6mm to a 45amp switch outside the bathroom door and ran 6mm back to the consumer unit. all wiring is run in uninsulated wall cavities and above the insulation, on top of the joists in the loft. the water feed is taken off the cold water tank feed, which is fed directly from the mains. at the consumer unit i have a 40 amp mcb. my current consumer unit is rated at 100 amps i can either fit the mcb in the unit as i have spare places or i could fit a 2 way seperate enclosure.