After much deliberation we are having two single ovens in our kitchen with an induction hob above.
I am looking for advice on wiring.
Both cable runs go through an open void under the house so not insulated etc. The runs for both cookers and hob is about 9 meters.
The oven manufactor says min 16A for each oven and the hob 63A (five ring induction so takes alot of power)
My question what size cables are required?
I only have two spare spaces on my fuseboard so was thinking of running a 6mm cable to run both ovens and 10mm for the cooker.
Is this sufficient?