Have proble with worsecter 28i, It goes to overheat and then lock out two or three times a day after using hot water so we have to push the over heatstat knob on the top of boiler to start working again. any help appreciated.
 
Sponsored Links
I expect its sludged up as usual when its been fitted without cleaning the system!

Tony
 
Thanks Tony for you kwik response I did guess that but I was not sure do you think if I do power flash the system it will cure the problem or may I take out the secondry heat exchanger to clean it seperately or take it to adlink and get a reconstructed one.
 
Sponsored Links
You can power flush the system, or just concentrate on the boiler. You will never remove ALL the sludge from a system so the problem may recur, though the interval may be acceptable.

You will have some difficulty removing a secondary heat exchanger from a 28i.
 