Continuity Assistance - Lighting Circuit with readings!

Goto page Previous  1, 2
 
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK
Search this topic :: View previous topic :: View next topic  
Author Message
holmslaw

from Vanuatu

Joined: 12 Dec 2006
Posts: 5844
Location: Vanuatu
Thanked: 400 times

PostPosted: Tue Mar 13, 2012 11:52 am Reply with quote

..


Last edited by holmslaw on Thu Apr 12, 2012 8:14 am, edited 1 time in total
Back to top
The following user says thank you to holmslaw for this useful post:
dizz (13 Mar 2012)
 Alert Moderators

If you do not want to see this advert, click here to login or if you are new click here to join free.
riveralt

from United Kingdom

Joined: 04 Jan 2004
Posts: 3768
Location: United Kingdom
Thanked: 565 times

PostPosted: Tue Mar 13, 2012 1:45 pm Reply with quote

dizz wrote:
Now I'm getting a bit hacked off - Continuity on the circuits, and finnaly started to attck the ring. Cross connect CPC and neutral at the CU and took a reading of 0.85 ohms. Checking for bridges, so cross connect both phase and neutral at CU, and go round the sockets, 0.21, 0.24, 1.74, 0.22, 1.55, ... and on one double socket I get a reading of 0.22, and on the same socket, over 1 ohm. Click the switches and the reading changes a bit, sometimes I can get it down to just over 0.2 ... it's all looking a bit problematic.

We have had this discussion before.....
If you are going to conduct tests do them properly in the proper order.
What where you end to end readings? r1 r2 rn.

Do the cross connect (figure of eight) readings equate to 1/4 r1+r2?
What radials do you have running off the ring final circuit - the end of which can give you higher readings.
Back to top
 Alert Moderators
dizz

from United Kingdom

Joined: 19 Jun 2009
Posts: 274
Location: United Kingdom
Thanked: 7 times

PostPosted: Tue Mar 13, 2012 2:39 pm Reply with quote

Hi Riveralt - R1+R2 was 0.85 ohms as stated, now I'm moving on by cross connecting L1/N2 and L2/N1 at the CU, which is about 0.21, a quarter of the 0.85 I was getting!

HOWEVER, the pertinent "discussion" we had before though was when you said "BTW new switches are sometimes sticky and a few seconds flicking them on and off sometimes clears the cobwebs".

After doing what Holmslaw suggested by connecting the probes together and "wiggling" the wires, it revealed nothing, the reading was as solid as a rock - so I thought I'd flick the switches a number of times (and I mean a number - it took about 40-50 switches to "clear the cobwebs"), and now I get readings between 0.19 and 0.23 on every socket.

I guess that the manufacturing process might mean that some sort of coating gets on the metal which adds resistance, and the constant flicking of the switches wears that away??!!, until you get a perfect connection??!!

PS - only have two "small" spurs from the ring, which increased the reading to 0.25/0.26

ADDED - Sorry meant R1 + R2 = 0.85/4 - no haven't done r1, r2, rn separately!! oops
Back to top
 Alert Moderators
RF Lighting

from United Kingdom

Joined: 31 Mar 2006
Posts: 17355
Location: Leeds,
United Kingdom
Thanked: 917 times

PostPosted: Tue Mar 13, 2012 8:31 pm Reply with quote

riveralt wrote:
We have had this discussion before.....
If you are going to conduct tests do them properly in the proper order.
Back to top
 Alert Moderators
17thman

from United Kingdom

Joined: 29 Jun 2008
Posts: 831
Location: West Midlands,
United Kingdom
Thanked: 45 times

PostPosted: Fri Mar 16, 2012 10:32 pm Reply with quote

dizz wrote:
Hi Riveralt - R1+R2 was 0.85 ohms as stated, now I'm moving on by cross connecting L1/N2 and L2/N1 at the CU, which is about 0.21, a quarter of the 0.85 I was getting!


R1 +R2 is the resistance of the line conductor(s) and cpc(s). if you have .85 ohms as a R1 + R2 on a ring final socket circuit then you really need to check your supply type as its its sqeeky bum time if you are measuring at non operational temperatures.

Secondly, if you are cross linking Line and Neutral and comnparing it with R1 + R2 without knowing r1 r2 and rn, what is it worth.

consider not correctly crossing L and E then the measurements wiill differ depending on where in the circuit you measure.
Back to top
 Alert Moderators
dizz

from United Kingdom

Joined: 19 Jun 2009
Posts: 274
Location: United Kingdom
Thanked: 7 times

PostPosted: Mon Mar 19, 2012 8:39 am Reply with quote

Thanks 17thman - I was quoting R1 and R2 loosely - from my post, that was the reading of the L2-N1 reading from cross connect of L1-N2 at the board, so R1+R2 should be 1/4 of 0.85 ohms, so when I do the external loop I hope that it won't be "sqeeky bum time".

Regarding the Zs - I plan to measure the Zs for the ring and radial, as I have a plug, but for the other circuits I plan to just add the R1+R2 to the Ze - is that acceptable, and normal practice?
Back to top
 Alert Moderators
kevindgas

from United Kingdom

Joined: 28 Mar 2006
Posts: 5691
Location: Southampton,
United Kingdom
Thanked: 467 times

PostPosted: Mon Mar 19, 2012 8:49 am Reply with quote

@dizz, yes i've had a few issues with those double sockets and now don't buy them. buy from TLC now as although still cheap switches are slightly better quality and their cable is cheaper too!
Back to top
 Alert Moderators
Search this topic :: View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK All times are GMT
Goto page Previous  1, 2
Page 2 of 2

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
Kitchen Wiring Assistance 79 1480 Thu Mar 15, 2012 9:03 pm
Assistance please! manrose extractor fan stuck on 3 80 Sat Oct 20, 2012 7:42 am
Electric shower fault diagnosis assistance please 9 380 Sun Sep 08, 2013 8:37 am
diversity assistance 2 340 Thu Dec 09, 2004 6:21 pm
Dimmer switches - wiring assistance appreciated please 8 140 Mon Sep 12, 2011 7:31 pm


 
DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
Network | Advertising | Newsletter
DIY | DIY How To | @home | DIY Wiki | DIY Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy. Copyright © 2000-2014 DIYnot Limited.