Hello

I have a 'Baxi Duo-tec Combi 28 HE A' condensing combination boiler.

It is just over 1 year old and was already installed into our new-build property by the developers prior to us moving in.

It has been working fine up until today, when I noticed that the radiators were stone cold. They have all been bled recently, and have been working fine yesterday, getting very hot within minutes of turning on the heating.

The hot water still comes through the tap on demand and you can hear the boiler fire up when the tap is turned on.

The wireless thermostat is also working fine, and I have set the heating to its maximum temperature, which displays a flame symbol on the thermostat and you can then hire the boiler fire up and the green light come on to indicate the central heating is in operation. The boiler is warm to the touch and you can hear it doing its thing.

The radiators are still stone cold. No error messages are displayed, it still makes all its normal noises, radiators have been re-bled, radiator thermostats have all been set to maximum, boiler has been reset multiple times, as has the wireless thermostat, but no still hot water going to the radiators.

Fortunately we're approaching April so heating is hopefully going to be less of an issue provided the hot water still works, but I would love to know what is causing this fault. Pump problem of some sort perhaps? Despite the boiler being a year old?

Any ideas?

Thanks in advance for your help.
Back to top
 Alert Moderators

If you do not want to see this advert, click here to login or if you are new click here to join free.
gas112

from Unknown or unspecified country

Joined: 27 Oct 2009
Posts: 8254
Location: Unknown or unspecified country
Thanked: 1904 times

PostPosted: Mon Mar 25, 2013 7:22 pm Reply with quote

sure no one has touched the isolating valves under the boiler and turned one off by mistake,
Back to top
The following user says thank you to gas112 for this useful post:
EMT999 (25 Mar 2013)
 Alert Moderators
EMT999

from United Kingdom

Joined: 25 Mar 2013
Posts: 2
Location: Hampshire,
United Kingdom

PostPosted: Mon Mar 25, 2013 7:24 pm Reply with quote

gas112 wrote:
sure no one has touched the isolating valves under the boiler and turned one off by mistake,

Very sure!
Back to top
 Alert Moderators
MANDATE

from United Kingdom

Joined: 06 Mar 2003
Posts: 2290
Location: Manchester,
United Kingdom
Thanked: 129 times

PostPosted: Mon Mar 25, 2013 7:42 pm Reply with quote

My understanding is that there are two circuits the water can take and the movement of a diverter valve dictates which one is in operation.
The pump is used for both circuits.
The diverter valve also triggers one of two micro switches (HW or CH) depending on the valves position.
I'd be looking at:
(a) The wire less stat could be faulty.
To fit a room stat normally involves removing a wire 'link' so replacing the 'link' temporarily would help
(b) Diverter valve may be stuck. Should I would think be able to prove if it goes to CH position and trigger the CH micro switch
(c) CH micro switch may not be triggered fully to make contact or contacts get burned /dirty so contact not made. Continuity of switch could be checked.
These are just my ideas based on a different combi
Back to top
 Alert Moderators
Baxmax

from Turks and Caicos Islands

Joined: 18 Feb 2006
Posts: 789
Location: Turks and Caicos Islands
Thanked: 33 times

PostPosted: Mon Mar 25, 2013 8:48 pm Reply with quote

These are just my ideas based on a different combi

Read more: http://www.diynot.com/forums/plumbing/baxi-combi-boiler-hot-water-but-no-central-heating.359731/#ixzz2OaRCgIUa

Yes they are MANDATE
Back to top
 Alert Moderators
Search this topic :: View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Plumbing and Central Heating All times are GMT
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
Baxi Combi 80e Central heating problem water not circulating 4 760 Mon Sep 28, 2009 11:45 am
Baxi 80 eco combi hot water no central heating 6 240 Fri Dec 31, 2010 10:35 am
Baxi combi boiler central heating problem 14 1520 Mon Sep 05, 2005 5:39 pm
baxi combi instant 105e central heating boiler 5 840 Tue Sep 08, 2009 11:28 am
Baxi Combi 105e No central heating 8 821 Sat Oct 02, 2004 5:03 pm


 
DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
Network | Advertising | Newsletter
DIY | DIY How To | @home | DIY Wiki | DIY Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy. Copyright © 2000-2014 DIYnot Limited.