Hi

I would like some help please choosing between 2 boilers, Baxi Neta-Tec 28 HE and the 33 HE.

Max flowrate is 13.5 LPM for the 33 and 11.5 LPM for the 28. The difference between the two models is only 70 but I will only spend it if I will actually achieve the flow at the showerhead. It's going in to a 2-bed mid-terrace and either model is fine is terms of KW for the CH.

I currently get 14.5 LPM out of the filling loop directly underneath my existing boiler which is a 24KW which gives 9.5 LPM at the shower. Will I get 13.5 LPM if I install the 33 model?

The bath/shower is located around 2 metres from the boiler.

By the way I'm going for the Baxi as it's got a 5year warranty and has a high 13.5 LPM for low price. Of course if it turns out that I will
never achieve 13.5 LPM I will either get the 28 model or switch completey to a glow worm Flexicom which is also doing a 5-yr warranty until the end of the year.

Thanks!

Info here:

http://www.boilers2go.co.uk/Baxi-Neta-Tec-33-HE-Gas-Combination-Boiler.html

http://www.boilers2go.co.uk/Baxi-Neta-Tec-28-HE-Gas-Combination-Boiler.html

Technical specs here: http://www.baxi.co.uk/docs/baxi-think-guide-final-SPS.pdf
Back to top
 Alert Moderators

If you do not want to see this advert, click here to login or if you are new click here to join free.
manofgas

from United Kingdom

Joined: 22 Jul 2010
Posts: 12
Location: United Kingdom
Thanked: 3 times

PostPosted: Sun Dec 04, 2011 7:23 pm Reply with quote

if you are obtaining 14.5lpm below the boiler you should in theory obtain 13.5 lpm raised through 35 degrees from the boiler to the hot outlets.
However you would have to ensure that you have a sufficiency good and consistent inlet pressure from your cold water mains.
In addition you would have to ensure that your supply pipework is correctly sized and installed correctly, ensure that your shower head can pass the volume of water required .

IF YOU HAVE 14.5 LPM ON THE INLET THE BOILER SHOULD PASS THE MAX 13,5LPM IF THE CORRECT SIZE OF RESTRICTORS HAVE BEEN FITTED (IF THERE ARE ANY).
Back to top
 Alert Moderators
powerbooksub

from United Kingdom

Joined: 03 Jul 2011
Posts: 40
Location: Surrey,
United Kingdom

PostPosted: Sun Dec 04, 2011 7:48 pm Reply with quote

Thanks.

I think I therefore get the larger boiler.
Back to top
 Alert Moderators
Dan_Robinson

from United Kingdom

Joined: 01 Jul 2007
Posts: 24065
Location: Hertfordshire,
United Kingdom
Thanked: 3465 times

PostPosted: Sun Dec 04, 2011 7:53 pm Reply with quote

Of course if you haver slightly less l/min, it will be raise to a higher temperature - which has its own benefits.
Back to top
 Alert Moderators
powerbooksub

from United Kingdom

Joined: 03 Jul 2011
Posts: 40
Location: Surrey,
United Kingdom

PostPosted: Sun Dec 04, 2011 8:08 pm Reply with quote

good point, thanks
Back to top
 Alert Moderators
dreadnoughtheating

from United Kingdom

Joined: 31 May 2009
Posts: 1739
Location: Norfolk,
United Kingdom
Thanked: 236 times

PostPosted: Sun Dec 04, 2011 8:37 pm Reply with quote

PBS, 35 degrees temp rise is the standard quoted by most manufacturers.

I would ask you to note that if we have another cold spell like last year, an incoming cold water temp of 2-3 degrees will generate an output temp of say 38 degrees at the quoted flow rate. That is blood temp (give or take).

A comfortable shower temp would be way above that temp, so please do not expect 13.5 l/min all year round at the shower head if you enjoy a hot one.

Combi's are not the answer to every hot-water/heating 'upgrade'

DH
Back to top
 Alert Moderators
Dan_Robinson

from United Kingdom

Joined: 01 Jul 2007
Posts: 24065
Location: Hertfordshire,
United Kingdom
Thanked: 3465 times

PostPosted: Sun Dec 04, 2011 8:39 pm Reply with quote

Very true.
Back to top
 Alert Moderators
mysteryman

from United Kingdom

Joined: 05 Jun 2010
Posts: 1664
Location: Shropshire,
United Kingdom
Thanked: 233 times

PostPosted: Sun Dec 04, 2011 9:26 pm Reply with quote

Make sure the water main can push the water through the boiler against the back pressure of the shower. If it can't, there's no point in having the extra power.
Back to top
 Alert Moderators
DP

from United Kingdom

Joined: 10 Dec 2003
Posts: 6228
Location: Glasgow,
United Kingdom
Thanked: 627 times

PostPosted: Sun Dec 04, 2011 10:07 pm Reply with quote

If you are getting 14.5l of water at the filling loop, what do you think will happen to the flow rate when cold tap is run AS WELL as hot water delivered by the boiler. What if someone flushes the WC, you certainly will not get delivered hot water as per the data badge nor adequate cold water..
Back to top
 Alert Moderators
Search this topic :: View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Plumbing and Central Heating All times are GMT
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
Ariston Microgenus - faulty, cut losses and go for new? 3 60 Sun Apr 01, 2012 7:24 pm
Thermal stores and standing losses 3 320 Fri Jun 03, 2011 8:16 am
UF optimum flowrate. 2 300 Sun Nov 19, 2006 6:29 pm
Hot water flowrate upstairs is zero? 5 440 Tue Jun 15, 2004 12:36 pm
Thermostatic Shower Valve Uneven Flowrate 7 700 Tue Nov 21, 2006 6:48 pm


 
DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
Network | Advertising | Newsletter
DIY | DIY How To | @home | DIY Wiki | DIY Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy. Copyright © 2000-2014 DIYnot Limited.