gravity fed back boiler pushing water up flow and return


 
Post new topic   Reply to topic    DIYnot.com Forum Index > Plumbing and Central Heating
Search this topic :: View previous topic :: View next topic  
Author Message
Lotarogg

from United Kingdom

Joined: 19 Aug 2010
Posts: 20
Location: United Kingdom

PostPosted: Mon Sep 12, 2011 1:12 pm Reply with quote

Hi,

This looked easy when I started but it has turned into a bit of a nightmare.

Having gutted my house I have replumbed it all and everything is working great except the back boiler on my solid fuel stove.

Having let water into the system I light the fire. The boiler on the back hisses (like an electric kettle) then once it's built up a head of steam blows straight out the vent into the header tank for a about a minute and will keep doing this every 20mins or so. The hissing tells me there must be a fair bit of air in the boiler which I guess is being blasted out the vent when it reaches pressure. I ran it for about 2 hours over the weekend thinking that once it has blown all the air out it will start to work as normal. But it just keeps boiling.

I have the vent placed before the intake into the cylinder coil, is this right? Also the feed from the header tank enters the heating system on the return to the fire.

The hot water from the fire also trys to go up the return pipe telling me either gravity isn't working or I've done something wrong.

Any help very very gratefully received

Cheers
Back to top
 Alert Moderators

If you do not want to see this advert, click here to login or if you are new click here to join free.
Nige F

from United Kingdom

Joined: 28 Jun 2005
Posts: 16211
Location: United Kingdom
Thanked: 808 times

PostPosted: Mon Sep 12, 2011 1:45 pm Reply with quote

Lotarogg wrote:
Hi,

either gravity isn't working or I've done something wrong.


Cheers
Both icon_eek.gif Have you used 28mm pipe for the gravity primaries to the cylinder
Back to top
The following user says thank you to Nige F for this useful post:
Lotarogg (13 Sep 2011)
 Alert Moderators
spraggo

from United Kingdom

Joined: 06 Sep 2010
Posts: 916
Location: Avon,
United Kingdom
Thanked: 149 times

PostPosted: Mon Sep 12, 2011 2:09 pm Reply with quote

You either have an airlock in the flow or return from boiler to cylinder (have you checked that these are rising to the cylinder with no dips), or the feed pipe between the header tank and the boiler is blocked. Assuming that you have water in the header tank.
Back to top
The following user says thank you to spraggo for this useful post:
Lotarogg (13 Sep 2011)
 Alert Moderators
Space cat

from United Kingdom

Joined: 09 Sep 2007
Posts: 3862
Location: Newcastle upon Tyne,
United Kingdom
Thanked: 74 times

PostPosted: Mon Sep 12, 2011 2:46 pm Reply with quote

Lotarogg wrote:
The hot water from the fire also trys to go up the return pipe


This might be a stupid question but have you connected the boiler the right way round? icon_question.gif icon_question.gif icon_question.gif

and also wrote:
I have the vent placed before the intake into the cylinder coil, is this right?


The vent must attach to the highest point in the circuit. You should have a clear path running upwards from the TOP of the boiler all the way to the vent. This pipe will also branch off to the top of the cylinder coil but it must run DOWN from the branch point to the cylinder. Look at it a different way; there must be a clear path running upwards from the TOP of the cylinder to the vent.
Back to top
The following 2 users say thank you to Space cat for this useful post:
Lotarogg (13 Sep 2011), Nige F (12 Sep 2011)
 Alert Moderators
Lotarogg

from United Kingdom

Joined: 19 Aug 2010
Posts: 20
Location: United Kingdom

PostPosted: Mon Sep 12, 2011 5:54 pm Reply with quote

Thanks very much all. Looks like I need to make some changes. For 3 metres from the boiler I have 28mm copper then reduce to 22mm pex at the same point for both flow and return. The flow from the boiler has a couple of 90 corners but is always going up so no dips. The flow meets the vent pipe then a 90 corner up to (400mm) the intake for the coil Ė so I guess thatís the first change to place the vent going vertically up from the coil intake.

The boiler connects: Return: From bottom of cylinder to bottom of boiler. Flow: from top of boiler to top of cylinder.

Is it vital that 28mm be maintained throughout boiler < > cylinder cycle? I have 22mm intakes on the cylinder.

Cheers
Back to top
 Alert Moderators
Space cat

from United Kingdom

Joined: 09 Sep 2007
Posts: 3862
Location: Newcastle upon Tyne,
United Kingdom
Thanked: 74 times

PostPosted: Mon Sep 12, 2011 6:23 pm Reply with quote

Quote:
so I guess thatís the first change to place the vent going vertically up from the coil intake.


That's the solution. If I read your post correctly, you currently have a giant airlock in the cylinder coil. icon_sad.gif icon_sad.gif icon_sad.gif

Quote:
Is it vital that 28mm be maintained throughout boiler < > cylinder cycle? I have 22mm intakes on the cylinder.


You obviously have to step down at some point. What lengths of 22mm do you have in there?
Back to top
 Alert Moderators
Nige F

from United Kingdom

Joined: 28 Jun 2005
Posts: 16211
Location: United Kingdom
Thanked: 808 times

PostPosted: Mon Sep 12, 2011 6:42 pm Reply with quote

Lotarogg wrote:
l Ė so I guess thatís the first change to place the vent going vertically up from the coil intake.

.

Is it vital that 28mm be maintained throughout boiler < > cylinder cycle? I have 22mm intakes on the cylinder.

Cheers
sounds like you have a cylinder for pumped circulation - with those 22mm intakes - you might get it to work after altering the vent icon_wink.gif
Back to top
 Alert Moderators
Lotarogg

from United Kingdom

Joined: 19 Aug 2010
Posts: 20
Location: United Kingdom

PostPosted: Tue Sep 13, 2011 11:21 am Reply with quote

@spacecat - have got about a meter of 22mm pex going to and from the cylinder coil.

Will make the changes and report back.

Thanks again
Back to top
 Alert Moderators
peaps

from United Kingdom

Joined: 22 Aug 2011
Posts: 1311
Location: Derbyshire,
United Kingdom
Thanked: 54 times

PostPosted: Tue Sep 13, 2011 12:18 pm Reply with quote

I have a multifuel system that I have just fitted. It is set up as a gravity/pumped y system with a three port diverter and had the same problem. The solution was to add a bleed valve on the 28mm flow at the highest point in the pipe work going into the tank. Bled out all the air and bobs your uncle. In older AGA systems the vent was connected to the return but I was advised to connect it to the flow pipe just below the diverter. You may find that if you don't pump the system it will vent when the tank get too hot so making sure you have a heat sink is important.

I just have a problem with the wiring and turm turn the diverter over manual for now.

Is it a stright gravity fed system?
Back to top
 Alert Moderators
Lotarogg

from United Kingdom

Joined: 19 Aug 2010
Posts: 20
Location: United Kingdom

PostPosted: Wed Nov 09, 2011 3:23 pm Reply with quote

sorry for delay in posting as have been on hols then other jobs on the house took priority.

Have done the suggestion of making the vent to the header tanker on the return pipe the last outlet in the system. I took a hose pipe and ran mains pressure through the flow and out the return to take out any air locks. fired up the stove and gravity is at last doing its thing icon_smile.gif

@peaps the only heat sink I use is run the hot want to draw cold down into the system, is there a better way?

Finally have to connect the rads up. I'm thinking flow to be taken about a foot higher from where the flow from the stove enters the cyclinder - ie the last outlet on the vent pipe before it vents into the header tank? I will put a pump there triggered by a temp sensor on the flow pipe from the stove. The returns will come in through one way valves into the return to the stove.

Thanks for all help and suggestions
Back to top
 Alert Moderators
Search this topic :: View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Plumbing and Central Heating All times are GMT
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
Gas boiler pushing hot water to taps but not bath? 4 60 Sat Sep 17, 2011 5:02 am
Pushing the limits of my boiler? 3 280 Thu Aug 14, 2008 12:34 pm
Biasi 24S - pushing flue through conservatory roof? 2 240 Tue Jan 06, 2009 10:09 pm
Not pushing a push fit fitting far enough in 4 200 Sun Jun 15, 2014 4:51 pm
Hot water thermostat needs fitting, gravity fed back boiler. 6 1060 Sun Feb 26, 2006 2:31 pm


 
DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
Network | Advertising | Newsletter
DIY | DIY How To | @home | DIY Wiki | DIY Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy. Copyright © 2000-2014 DIYnot Limited.