roofers installed vented soffit - building regs no likey


 
Post new topic   Reply to topic    DIYnot.com Forum Index > Roofing and Guttering
Search this topic :: View previous topic :: View next topic  
Author Message
davebwithane

from United Kingdom

Joined: 14 Jan 2008
Posts: 71
Location: Sussex,
United Kingdom

PostPosted: Wed Feb 29, 2012 1:17 pm Reply with quote

Hello
Just had building regs round to look at my re-tiled, re-soffited and re-fascia'd roof.
The soffit and fascia has been installed and the soffit is vented. Building regs say this is incorrect and it should not have been vented.
Now what do I do ? Big job to get it removed. Is there something I can put over the vents ?
Thanks
Dave
Back to top
 Alert Moderators

If you do not want to see this advert, click here to login or if you are new click here to join free.
freddymercurystwin

from United Kingdom

Joined: 21 Jan 2007
Posts: 13143
Location: Devon,
United Kingdom
Thanked: 1367 times

PostPosted: Wed Feb 29, 2012 1:52 pm Reply with quote

Can you explain a bit more about the roof construction, why BC are involved and why they have said the venting is incorrect. What underlay was used breathable or felt?

You saying they won't approve it with the vents insitu?
Back to top
 Alert Moderators
davebwithane

from United Kingdom

Joined: 14 Jan 2008
Posts: 71
Location: Sussex,
United Kingdom

PostPosted: Wed Feb 29, 2012 2:09 pm Reply with quote

Thanks.

Had the roofed stripped, celutex put in between the rafters, breathable felt over then re-tiled.

They said the airflow is incorrect with vented soffits insitu and they need to be taken out before approval is given. No vents required at all due to breathable felt.

Regs involved 'cos the entire roof covering is being overhauled.
Back to top
 Alert Moderators
freddymercurystwin

from United Kingdom

Joined: 21 Jan 2007
Posts: 13143
Location: Devon,
United Kingdom
Thanked: 1367 times

PostPosted: Wed Feb 29, 2012 3:07 pm Reply with quote

You do mean rafters and not joists?

If so then the loft has been converted presumably? If so are you saying the Celotex runs all the way down the rafters to the eaves and effectively the ventilation is able to get beneath the Celotex? The Celotex needs to meet the wall insulation to make an 'insulation bubble' around the living area.

There are certain circumstances where additional venting above the insulation is required when using a breathable membrane but these can largely be designed out so we assume the roofers have made a booboo!
Back to top
 Alert Moderators
davebwithane

from United Kingdom

Joined: 14 Jan 2008
Posts: 71
Location: Sussex,
United Kingdom

PostPosted: Wed Feb 29, 2012 3:30 pm Reply with quote

Thanks. Yes I meant rafters. The main reason for putting the celotex in between the rafters was because of draughts in the house and to make it more useable up there.

Just spoke to principal building regs guy - solution is to cover over soffit vents with plastic strip and not to ventilate the roof. The air pressure build up within the roof space will then be enough to send moist air through the breathable membrane. That's the theory anyway.
Back to top
 Alert Moderators
freddymercurystwin

from United Kingdom

Joined: 21 Jan 2007
Posts: 13143
Location: Devon,
United Kingdom
Thanked: 1367 times

PostPosted: Wed Feb 29, 2012 3:49 pm Reply with quote

Ahh OK hope you didn't pay for those vents then! icon_question.gif icon_wink.gif
Back to top
The following user says thank you to freddymercurystwin for this useful post:
davebwithane (29 Feb 2012)
 Alert Moderators
davebwithane

from United Kingdom

Joined: 14 Jan 2008
Posts: 71
Location: Sussex,
United Kingdom

PostPosted: Wed Feb 29, 2012 3:54 pm Reply with quote

yes unfortunately I did icon_sad.gif
Back to top
 Alert Moderators
davebwithane

from United Kingdom

Joined: 14 Jan 2008
Posts: 71
Location: Sussex,
United Kingdom

PostPosted: Wed Feb 29, 2012 6:46 pm Reply with quote

so does it sound right to you guys - no ventilation ? So the moisture is supposed to go through celotex and then the felt membrane only by the build up of pressure it creates up there itself and that's the only way it gets out ? doesn't sound right to me, but that's why I'm on here ..
thanks again.
Back to top
 Alert Moderators
noseall

from United Kingdom

Joined: 02 Feb 2006
Posts: 19846
Location: Staffordshire,
United Kingdom
Thanked: 1175 times

PostPosted: Wed Feb 29, 2012 7:29 pm Reply with quote

davebwithane wrote:
. The air pressure build up within the roof space will then be enough to send moist air through the breathable membrane. That's the theory anyway.
Sounds like blarney to me. icon_confused.gif
Back to top
 Alert Moderators
davebwithane

from United Kingdom

Joined: 14 Jan 2008
Posts: 71
Location: Sussex,
United Kingdom

PostPosted: Wed Feb 29, 2012 8:21 pm Reply with quote

just been reading the housebuilders bible (not that I am buiding a house). But the whole theory behind roof ventilation seems to be just that. There doesn't seem to be any hard and fast rules to stop condensation building up. I'm trying to workout if the warm roof space I now (or will have once soffit vents are sealed up) is going to cause condensation build up or not. Maybe the permeable membrane is enough for airflow, who knows ?
Back to top
 Alert Moderators
davebwithane

from United Kingdom

Joined: 14 Jan 2008
Posts: 71
Location: Sussex,
United Kingdom

PostPosted: Wed Feb 29, 2012 8:52 pm Reply with quote

interesting ..

http://www.thenbs.com/topics/ConstructionProducts/articles/ventedUnventedRoofConstruction.asp

"The enclosed void of a warm pitched roof does not require to be ventilated"

http://www.planningportal.gov.uk/permission/commonprojects/roof/

"Not all roofs need to be ventilated. Ventilation is not required to a warm roof system, which is where the insulation is placed above the joists or rafters."
Back to top
 Alert Moderators
freddymercurystwin

from United Kingdom

Joined: 21 Jan 2007
Posts: 13143
Location: Devon,
United Kingdom
Thanked: 1367 times

PostPosted: Wed Feb 29, 2012 10:12 pm Reply with quote

noseall wrote:
davebwithane wrote:
. The air pressure build up within the roof space will then be enough to send moist air through the breathable membrane. That's the theory anyway.
Sounds like blarney to me. icon_confused.gif

No, effectively this a loft conversion in terms of the insulation bubble noseall. Either vent the gap or fit a breathable membrane (albeit following the strict fitting guidance as breathable membranes do sometimes need additional ventilation). That's the theory anyway.
Back to top
 Alert Moderators
Nige F

from United Kingdom

Joined: 28 Jun 2005
Posts: 16176
Location: United Kingdom
Thanked: 804 times

PostPosted: Thu Mar 01, 2012 9:09 am Reply with quote

davebwithane wrote:
t. Maybe the permeable membrane is enough for airflow, who knows ?
Not for me , it`s not : BUT I`m only an old school plumber with general building experience . I know what I would do - cover the vents until it`s all signed off - then ...... icon_wink.gif The devil is in the detail with roof insulation , you have to work out exactly where and how much the air is going to flow : FMT and Nose have that experience . At my last house ( chalet bungalow) an existing extension had all the work under Sussex ( Wealden ) BC signed off and I found the air from the continuous soffit vents was going under the floor of the bedroom/ ceiling of living room - instead of round the "bubble"
Back to top
 Alert Moderators
freddymercurystwin

from United Kingdom

Joined: 21 Jan 2007
Posts: 13143
Location: Devon,
United Kingdom
Thanked: 1367 times

PostPosted: Thu Mar 01, 2012 9:37 am Reply with quote

Nige F wrote:
davebwithane wrote:
t. Maybe the permeable membrane is enough for airflow, who knows ?
Not for me , it`s not : BUT I`m only an old school plumber with general building experience . I know what I would do - cover the vents until it`s all signed off - then ...... icon_wink.gif The devil is in the detail with roof insulation , you have to work out exactly where and how much the air is going to flow : FMT and Nose have that experience . At my last house ( chalet bungalow) an existing extension had all the work under Sussex ( Wealden ) BC signed off and I found the air from the continuous soffit vents was going under the floor of the bedroom/ ceiling of living room - instead of round the "bubble"

I'm guessing the vents allowed airflow directly into the loft otherwise I don't see why BC would have condemned them but who knows! As you say if the vents were allowing airflow into the gap between the ins and U/S of the tiles that'd only be a good thing.
Back to top
 Alert Moderators
paulandfrodo

from United Kingdom

Joined: 06 Apr 2008
Posts: 146
Location: Hampshire,
United Kingdom
Thanked: 6 times

PostPosted: Sat Mar 10, 2012 8:13 pm Reply with quote

I thought the construction was celotex between and OVER the roof joists. This would be up to the required amount to achieve app. U values.

You then have an air gap between the celotex and breathable membrane, then tiles. Can't remember if it's 25mm or 50mm gap - sorry, it sat. night and I've had wine !

You have a vented soffit and vented ridge (marley do various systems).

Thus moisture is taken up and out. Ensure you drill app holes through any noggins used with rafters - esp. where velux windows are.
Back to top
 Alert Moderators
Search this topic :: View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Roofing and Guttering All times are GMT
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
Are vented soffits necessary in 1930 end of terrace? 3 200 Mon Dec 13, 2010 2:44 am
Vented pantiles ? 4 80 Mon Dec 02, 2013 7:43 pm
1930s Roof Joists and Building Regs 5 100 Tue Sep 20, 2011 8:54 pm
Gutters, downpipes and Building regs 3 160 Thu Dec 22, 2011 2:11 pm
Full plans building regs - where do I stand with roof calcs? 3 520 Mon Feb 15, 2010 9:25 pm


 
DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
Network | Advertising | Newsletter
DIY | DIY How To | @home | DIY Wiki | DIY Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy. Copyright © 2000-2014 DIYnot Limited.