Worcester 24i RSF-L Combi boiler problem


 
Post new topic   Reply to topic    DIYnot.com Forum Index > Plumbing and Central Heating
  View previous topic :: View next topic  
Author Message
CRANEPB

from United Kingdom

Joined: 11 Feb 2004
Posts: 12
Location: United Kingdom
Thanked: 0 times

PostPosted: Wed Oct 08, 2008 10:18 am    Post Subject:
Worcester 24i RSF-L Combi boiler problem
Reply with quote Thanks

Worcester 24i RSF-L Combi boiler problem:
When I turn the hot water tap on the boiler fires up and hot water is dispensed from the tap. However after a minute or two the water goes cold. Is this a diverter valve problem? The boiler also makes a noise after I have turned the tap off that sounds like it is trying to fire up / reset or something, but it can't make its mind up. The heating function of the boiler works fine. Can anyone please advise.

Thank you.
Back to top
 Alert Moderators

If you don't want to see this advert, click here to login or if you are new click here to join free.
Agile

from United Kingdom

Joined: 26 Jun 2004
Posts: 24311
Location: London,
United Kingdom
Thanked: 193 times

PostPosted: Wed Oct 08, 2008 10:22 am    Post Subject:
Reply with quote Thanks

It sounds as if the heat exchanger may be scaled up and causing overheat protection to be activated.

What happens if you leave it running after it goes cold?

It could also be a PCB fault or another component. Some people find these faults difficult to identify.

Tony

__________________
ARGI Registered Engineer
Back to top
 Alert Moderators
CRANEPB

from United Kingdom

Joined: 11 Feb 2004
Posts: 12
Location: United Kingdom
Thanked: 0 times

PostPosted: Wed Oct 08, 2008 1:54 pm    Post Subject:
Reply with quote Thanks

Thanks for the reply. We do live in a hard water area so a scaled up heat exchanger could be the problem. If this is the problem what would be the remedy? I will try running it after it goes cold tonight to see if it heats up again.
Back to top
 Alert Moderators
Agile

from United Kingdom

Joined: 26 Jun 2004
Posts: 24311
Location: London,
United Kingdom
Thanked: 193 times

PostPosted: Wed Oct 08, 2008 9:59 pm    Post Subject:
Reply with quote Thanks

We would use a power flushing pump and sulphamic acid to descale it.

Unfortunately only a very few gas engineers would do this messy and time consuming procedure. We would charge £180 !

Others would change the HE at a cost of perhaps £150 plus labour ( at £120 ? ).

Tony

__________________
ARGI Registered Engineer
Back to top
 Alert Moderators
CRANEPB

from United Kingdom

Joined: 11 Feb 2004
Posts: 12
Location: United Kingdom
Thanked: 0 times

PostPosted: Thu Oct 09, 2008 10:39 am    Post Subject:
Reply with quote Thanks

Was unable to repeat the problem last night and the system worked fine. Obviously a problem is evident and I will have to monitor it.

Best Regards.
Back to top
 Alert Moderators
magicmanalex

from United Kingdom

Joined: 24 Oct 2009
Posts: 5
Location: Tyne and Wear,
United Kingdom
Thanked: 0 times

PostPosted: Sat Oct 24, 2009 11:56 am    Post Subject:
Reply with quote Thanks

Hi there,

Was just wondering if you managed to diagnose this fault as I'm having the same problem with the same model boiler.

I had a plumber come out and look at it. He thought it may have been the air pressure switch and swapped it out for a new one, but the problem was still there.

It also makes a very rapid clicking noise, like there's a solenoid valve open and closing very quickly.

Thanks in advance.

Alex
Back to top
 Alert Moderators
bengasman

from United Kingdom

Joined: 28 Jan 2005
Posts: 10130
Location: London,
United Kingdom
Thanked: 189 times

PostPosted: Sat Oct 24, 2009 1:06 pm    Post Subject:
Reply with quote Thanks

How often do you have to re-pressurise the system?
What is the pressure cold and hot?
What setting do you keep the boiler stat on?

__________________
Don't feed the troll.
Back to top
 Alert Moderators
magicmanalex

from United Kingdom

Joined: 24 Oct 2009
Posts: 5
Location: Tyne and Wear,
United Kingdom
Thanked: 0 times

PostPosted: Sun Oct 25, 2009 1:17 pm    Post Subject:
Reply with quote Thanks

Thanks for the quick response.

When the boiler's on, the pressure sits at about 1.3 bar, when it's off, it's normally at about 0.9 - 1.0 bar.

I don't have to pressurise it that often - the last time I did was a couple of months ago when I put back a radiator I had removed when getting the wall re-plastered.

This fault has existed before the radiator was removed though.

At the moment, the CH is set to hot, but this issue occurs no matter what the setting.
Back to top
 Alert Moderators
holty

from United Kingdom

Joined: 14 Jan 2006
Posts: 1343
Location: Cornwall,
United Kingdom
Thanked: 21 times

PostPosted: Sun Oct 25, 2009 1:39 pm    Post Subject:
Reply with quote Thanks

not uncommon for pcb issues on these.the rapid clicking does sound like the gas valve solenoid.a decent rgi would find the problem, and not just change pointless parts till it works.
Back to top
The following user says thank you to holty for this useful post:
magicmanalex (25 Oct)
 Alert Moderators
bengasman

from United Kingdom

Joined: 28 Jan 2005
Posts: 10130
Location: London,
United Kingdom
Thanked: 189 times

PostPosted: Sun Oct 25, 2009 1:43 pm    Post Subject:
Reply with quote Thanks

Without being able to measure things, I would guess limescale to be the culprit; do you have hard water?

__________________
Don't feed the troll.
Back to top
The following user says thank you to bengasman for this useful post:
magicmanalex (25 Oct)
 Alert Moderators
magicmanalex

from United Kingdom

Joined: 24 Oct 2009
Posts: 5
Location: Tyne and Wear,
United Kingdom
Thanked: 0 times

PostPosted: Sun Oct 25, 2009 1:51 pm    Post Subject:
Reply with quote Thanks

According to Northumbrian Water's website, the water is 'SLIGHTLY HARD'.

The measurement comes in at: 54 (Hardness in mg/l as calcium).

If limescale build-up is the problem, what's the recommended solution?
Back to top
 Alert Moderators
bengasman

from United Kingdom

Joined: 28 Jan 2005
Posts: 10130
Location: London,
United Kingdom
Thanked: 189 times

PostPosted: Sun Oct 25, 2009 1:54 pm    Post Subject:
Reply with quote Thanks

magicmanalex wrote:


If limescale build-up is the problem, what's the recommended solution?

Fixed price repair.

__________________
Don't feed the troll.
Back to top
 Alert Moderators
magicmanalex

from United Kingdom

Joined: 24 Oct 2009
Posts: 5
Location: Tyne and Wear,
United Kingdom
Thanked: 0 times

PostPosted: Sun Oct 25, 2009 2:04 pm    Post Subject:
Reply with quote Thanks

Oh yes, sorry - somebody did mention a powerflush/acidic descale above. I forgot.

I don't know much about boilers, but would the engineer be able to check for limescale before proceeding with a power flush?

I'd hate to have to fork out something like 180 pounds for it to be flushed only to find out it's just the same and I then have to pay for a new PCB.
Back to top
 Alert Moderators
bengasman

from United Kingdom

Joined: 28 Jan 2005
Posts: 10130
Location: London,
United Kingdom
Thanked: 189 times

PostPosted: Sun Oct 25, 2009 2:29 pm    Post Subject:
Reply with quote Thanks

magicmanalex wrote:
...but would the engineer be able to check for limescale before proceeding with a power flush?

I'd hate to have to fork out something like 180 pounds for it to be flushed only to find out it's just the same and I then have to pay for a new PCB.

That is why I mentioned a fixed price repair.

__________________
Don't feed the troll.
Back to top
 Alert Moderators
magicmanalex

from United Kingdom

Joined: 24 Oct 2009
Posts: 5
Location: Tyne and Wear,
United Kingdom
Thanked: 0 times

PostPosted: Wed Oct 28, 2009 5:34 pm    Post Subject:
Reply with quote Thanks

OK, so I took your advice and went for a fixed-price repair.

Called British Gas this morning who said £167.42 all-in, guaranteed for 12 months (existing customer). I was expecting them to say at least a couple of days. They were out within about 6 hours.

Turned out to be the PCB (£120 part online). The engineer didn't have one, but sent a text to all of the engineers in the local area to see if they had one available. No luck so he said he'd have to come back tomorrow. His line manager then called and authorised him to go and purchase one from a nearby seller (apparently BG have a 70% same-day fix target that they need to reach).

An hour later, here I am typing this in a really warm living room with a really quiet boiler. One happy chappy. icon_smile.gif

Just wanted to thank everyone here for their input. It was greatly appreciated.
Back to top
 Alert Moderators
Display posts from previous:   
  View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Plumbing and Central Heating All times are GMT
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
Worcester Combi Boiler Problem 4 520 Tue Nov 29, 2005 9:29 pm
I have a problem with my Worcester 240 Combi RSF boiler 13 320 Fri Nov 21, 2008 1:40 am
Worcester Bosch 28CDi combi boiler hot water flow problem. 5 1020 Thu Mar 26, 2009 6:05 pm
Worcester boiler combi problem 3 240 Sat Aug 30, 2008 3:50 pm
24i Junior Worcester Combi Boiler - problem no hot water... 10 1620 Tue May 01, 2007 8:11 am



DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
My DIYnot | Advertising | Newsletter
DIYnot.com | How to... | @home | Wiki | Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy.