Joined: 18 Oct 2007 Posts: 3166 Location: Sussex, United Kingdom Thanked: 70 times
Posted: Thu Oct 29, 2009 6:03 pm Post Subject:
Re: Wiring from Digistat to Honeywell
As the exisiting stat does not have a neutral wire, you will need to run a new cable to the receiver, which can be near the HW cylinder/motorized valve. You should use 3 core cable (not twin and earth), e.g brown, blue and yellow.
Receiver end
Connect Brown to L
Connect L to A
Connect 3rd colour to B
Connect Blue to N
At the other end
Connect Brown to a permanent Live
Connect Blue to permanent Neutral
If you have a three port valve: Connect 3rd colour to white valve wire (remove the existing wire - this goes to 3 on your old thermostat)
If you have two 2-port valves: Connect 3rd colour to brown wire of CH valve and remove the existing wire which goes to 3 on old thermostat.
At the Sunvic, remove the wire from terminal 4 (CH ON) - this goes to 1 on your old thermostat.
The Sunvic 207 XL is a two channel timer, but the CH channel is now redundant as the CM927 will be in charge.
Hint
Before fixing the receiver in place, it is a good idea to check that the two parts of the CM927 communicate properly from their proposed locations.
Connect a long lead with a 3 pin plug on one end to the L and N terminals of the receiver and plug in. You can now do the communication test in the installation manual and try different receiver locations until you find the best one.
Joined: 03 Apr 2004 Posts: 105 Location: United Kingdom Thanked: 0 times
Posted: Thu Oct 29, 2009 6:56 pm Post Subject:
Its not possible for me to start re-wiring, because its all inaccesable.
Currently I have two cables both have a red and black, the two reds are connected to the current stat the blacks connected together.
I do know which cable comes from the white valve port cable.
I wanted an RF stat that I could easily swap for my current one. Withe the messing about I may as well just drop my current cable down the cavity and locate in the lounge, lot easier and I know what I am doing.
Joined: 03 Apr 2004 Posts: 105 Location: United Kingdom Thanked: 0 times
Posted: Fri Oct 30, 2009 2:50 pm Post Subject:
Thanks Dave
Much appreciated I am up and running, the only thing is when I wired it all up everything was doing what it should but the boiler was not firing up, so I reconnected the programmer and the negatives and it worked !
I have never used the programmer it always stays on "on" for heating and water so I am happy to leave it as it is.
I will at some point in the near future have to get the boiler changed as its on its last legs. The biggest problem I have is whoever lived here before boxed everything in (even the programmer was plastered into the wall). so nothing is accessible if the pump packed up I would have to rip a wall down to get to it. !