Pumping over problem

Goto page 1, 2  Next
 
Post new topic   Reply to topic    DIYnot.com Forum Index > Plumbing and Central Heating
Search this topic :: View previous topic :: View next topic  
Author Message
beermatt3

from United Kingdom

Joined: 05 Jul 2005
Posts: 44
Location: Sussex,
United Kingdom

PostPosted: Fri Dec 09, 2005 6:52 pm Reply with quote

I have been called in to a job to look at a heating system that has a serious pumping over problem. It is a two story house with boiler on ground floor, pump and three way valve in airing cupboard on first floor. The cold feed and vent tee into the common flow in airing cupboard. (seperatly both 22mm)

The system has been flushed and shows no signs of any blockages, but as soon as the pump goes on in either heating or hot water it shoots out the 22mm vent pipe even when cold.

I reckon I have been called in to sort a problem that never has been right since installation as the water in expansion tank was very brown.

Any suggestions, I no it's the weekend but I would be gratefull for any comments.

Will making the expansion pipe higher make any difference?
Back to top
 Alert Moderators

If you do not want to see this advert, click here to login or if you are new click here to join free.
ollski

from United Kingdom

Joined: 08 Oct 2003
Posts: 4906
Location: Birmingham,
United Kingdom
Thanked: 55 times

PostPosted: Fri Dec 09, 2005 6:56 pm Reply with quote

What speed is the pump on?, is the open vent the next connection after the pump?
Back to top
 Alert Moderators
andsam

from United Kingdom

Joined: 13 Nov 2005
Posts: 931
Location: Yorkshire,
United Kingdom
Thanked: 115 times

PostPosted: Fri Dec 09, 2005 7:07 pm Reply with quote

As Ollski says tell us more about the pipework config.
1 Where the open vent is
2 Where cold feed is
3 Are they positioned before the pump.
3 How far are these apart
4 How high does the open vent go above the header tank.
Back to top
 Alert Moderators
beermatt3

from United Kingdom

Joined: 05 Jul 2005
Posts: 44
Location: Sussex,
United Kingdom

PostPosted: Fri Dec 09, 2005 7:20 pm Reply with quote

1 Where the open vent is
2 Where cold feed is
3 Are they positioned before the pump.
3 How far are these apart
4 How high does the open vent go above the header tank.

Thanks for quick response.

The cold feed and open vent are positioned on a piece of verital pipe about 2" below before the the pump and about 2" apart.

The vent pipe goes about 4" above the header tank.

I hope this is of use!
Back to top
 Alert Moderators
beermatt3

from United Kingdom

Joined: 05 Jul 2005
Posts: 44
Location: Sussex,
United Kingdom

PostPosted: Fri Dec 09, 2005 7:23 pm Reply with quote

It doesn't make any difference what speed the pump is on, even on 1 it still pumps over.

What a nightmare, who would be a plumber!
Back to top
 Alert Moderators
PIPERPETE

from United Kingdom

Joined: 27 Nov 2005
Posts: 28
Location: United Kingdom

PostPosted: Fri Dec 09, 2005 7:25 pm Reply with quote

If youre having pump back then the expansion pipe is fitted after the pump and not before, also the motorised valve could be closed, i suspect a wiring problem that the motorised valve has not been wired to switch the boiler and pump off, another prblem could be is it an old house? if it is then at some time the system would have been on gravity central heating and gravity hot water and there could be a non return valve jammed in teh flow pipe somewhere. Thinsk about it, if you are confused then draw a diagram on paper then have a cup of tea, trust your instincts
Back to top
 Alert Moderators
beermatt3

from United Kingdom

Joined: 05 Jul 2005
Posts: 44
Location: Sussex,
United Kingdom

PostPosted: Fri Dec 09, 2005 7:30 pm Reply with quote

The pump and motorised valve are new, so I don't reckon they could be at fault. All the rads and cylinder get hot so can't be a circulation problem.

Most odd.
Back to top
 Alert Moderators
ollski

from United Kingdom

Joined: 08 Oct 2003
Posts: 4906
Location: Birmingham,
United Kingdom
Thanked: 55 times

PostPosted: Fri Dec 09, 2005 8:11 pm Reply with quote

beermatt3 wrote:
The pump and motorised valve are new, so I don't reckon they could be at fault. All the rads and cylinder get hot so can't be a circulation problem.

Most odd.


When you say the pump is new are you sure it is fitted the right way round icon_question.gif
Back to top
 Alert Moderators
beermatt3

from United Kingdom

Joined: 05 Jul 2005
Posts: 44
Location: Sussex,
United Kingdom

PostPosted: Fri Dec 09, 2005 8:45 pm Reply with quote

Yep the pump is the right way around.
Back to top
 Alert Moderators
ollski

from United Kingdom

Joined: 08 Oct 2003
Posts: 4906
Location: Birmingham,
United Kingdom
Thanked: 55 times

PostPosted: Fri Dec 09, 2005 9:23 pm Reply with quote

Try extending the vent pipe, should be 18" above the tank, or combine the cold feed and vent (min.22mm).
Back to top
 Alert Moderators
kaboom

from Russian Federation

Joined: 14 Jan 2005
Posts: 97
Location: Russian Federation

PostPosted: Fri Dec 09, 2005 10:46 pm Reply with quote

What timing! I flushed one today that had ground to a halt due to very serious sludge. Got it all clean, 3 port ok, fitted shiny new pump and the b*****r pumps over a little on 2. On 1 it won't circulate. The set up is boiler on ground floor and the rest in airing cupboard. Its what I call an 'H' set up, with the feed coming up from the bottom right and turns left (vent is straight up) turns left again (with feed coming down from top left) into pump which faces down. The header tank is sitting on the loft floor and the vent only goes 300mm above it at highest point. Think I'll try raising the header off the loft floor and extend the vent a bit higher too. Any other ideas (other than sealed system) chaps? 14 rad system all bar 1 on trv's, no room stat and manual bypass (which I don't really want to cheat with).
Back to top
 Alert Moderators
Softus

from United Kingdom

Joined: 21 Oct 2004
Posts: 19558
Location: United Kingdom
Thanked: 9 times

PostPosted: Fri Dec 09, 2005 10:58 pm Reply with quote

beermatt3 wrote:
The system has been flushed and shows no signs of any blockages...

...the water in expansion tank was very brown.

These two statements conflict. If the system was clean then the water would not be brown.

Water running out of the vent is not the way it's designed to be, so it's a symptom of problem, rather than a problem per se.

One common point of a blockage is at the junction of the cold feed into the pumped circuit. This can be exacerbated by incorrect installation - in the direction of flow, the sequence should be vent, cold feed, pump. If the vent is after the cold vent then there's a risk of pulling in air, and if the vent is after the pump then there's a risk of "pumping over".

The chances are that you're at the beginning of a medium length road leading from an unhealthy system to a healthy one. You may wish to consider the virtues of leaving the work until the spring, but you can mitigate the problem in the meantime.

However, if your system is pumping over, then you may get away with just cleaning it for now. I would do this by draining the water out of the system (with the boiler and pump turned off) until the F&E cistern is empty, then drain the same amount again, then add a cleaner to the cistern and re-fill. You'll need to shut off the cold feed to the F&E while doing this - tying up the ball valve will do if you have no service valve ro stop cock.

Run the system for a couple of weeks in this state - ensure that each radiator gets nice and hot for some of that time. When you drain down after all of this (do it HOT) then the water should contain much of the muck that's blocking your system. You can then add an inhibitor, and refill, and wait until the spring.

BTW, the forum contains information about about blockages, and sludge, and draining, and inhibitors, and pumping over, and blockages, and sludge....
Back to top
 Alert Moderators
ollski

from United Kingdom

Joined: 08 Oct 2003
Posts: 4906
Location: Birmingham,
United Kingdom
Thanked: 55 times

PostPosted: Fri Dec 09, 2005 11:36 pm Reply with quote

Softus wrote:
However, if your system is pumping over, then you may get away with just cleaning it for now. I would do this by draining the water out of the system (with the boiler and pump turned off) until the F&E cistern is empty, then drain the same amount again, then add a cleaner to the cistern and re-fill. You'll need to shut off the cold feed to the F&E while doing this - tying up the ball valve will do if you have no service valve ro stop cock.


I think personally if I suspected the cold feed to be virtually blocked that I would isolate a rad, drain a couple of litres out of it and inject the cleaner into the rad via the bleed plug....just in case.
Back to top
 Alert Moderators
beermatt3

from United Kingdom

Joined: 05 Jul 2005
Posts: 44
Location: Sussex,
United Kingdom

PostPosted: Fri Dec 09, 2005 11:45 pm Reply with quote

Thanks everyone, I've got plenty of things to check and try on Monday. When I say the water was brown it is in the past tense, obioulsy it's not brown after being flushed.

Anyway Cheers
Back to top
 Alert Moderators
Softus

from United Kingdom

Joined: 21 Oct 2004
Posts: 19558
Location: United Kingdom
Thanked: 9 times

PostPosted: Fri Dec 09, 2005 11:46 pm Reply with quote

ollski, IMO, if the blockage is in the usual place then the cleaner is unlikely to shift it.
Back to top
 Alert Moderators
Search this topic :: View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Plumbing and Central Heating All times are GMT
Goto page 1, 2  Next
Page 1 of 2

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
Shower pump problem - pump stops pumping water 5 80 Tue Mar 20, 2012 8:51 pm
problem with pumping over on my central heating system 4 440 Thu Sep 02, 2010 5:35 pm
Pumping over problem 5 140 Tue Nov 16, 2010 1:09 pm
Pumping over/overflowing problem, Y-plan system 3 100 Mon Jan 03, 2011 6:18 pm
Pumping over problem 4 860 Thu Nov 22, 2007 9:35 pm


 
DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
Network | Advertising | Newsletter
DIY | DIY How To | @home | DIY Wiki | DIY Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy. Copyright © 2000-2014 DIYnot Limited.