I want to run an outside light from a spur coming of an electrical socket. Can I do this and what cable would I need for the spur? |
|
| Back to top |
|
|
|
If you do not want to see this advert, click here to login or if you are new click here to join free. |
 |
festa

Joined: 06 Feb 2006 Posts: 212 Location: Cheshire, United Kingdom
|
Posted: Mon Jun 18, 2007 5:57 pm |
|
|
Yes you can do this as long as your new extension doesn't put too much on to the circuits Earth fault loop.
If the ring is run in 2.5mm twin and earth then your spur should be in the same size cable to a suitable FCU,from there,depending on the power the new light is pulling you can run a smaller cable as long as the fuse in the FCU protects it i.e...
If your new light is 1000w then 2.5mm should be run to the FCU, from the FCU you can run either 1mm or 1.5mm cable ( for ease of terminating in new light fitting) to the new fitting and a suitable 5amp fuse placed in the FCU. |
|
| Back to top |
|
|
|
 |
hadsatron

Joined: 18 Jun 2007 Posts: 2 Location: United Kingdom
|
Posted: Mon Jun 18, 2007 7:36 pm |
|
|
Thanks for that. What sort of FCU would you reccommend and where should I locate it. I was planning to run the spur from a socket that is on the inside of the outside wall where the light is to be placed. Should I run the spur to the FCU on the inside and then run the cable from the FCU outside to the light? |
|
| Back to top |
|
|
|
 |
JohnD

Joined: 15 Nov 2005 Posts: 34338 Location: Hampshire, United Kingdom Thanked: 1087 times
|
Posted: Mon Jun 18, 2007 7:46 pm |
|
|
have the FCU inside the house.
It will then be out of the rain and you will not need to buy an expensive weatherproof one. Fit a 3A fuse cartidge.
Put the FCU next to, or above, the socket that it spurs from. make a neat permanent label saying "outside lights spur, 3A"
Last edited by JohnD on Mon Jun 18, 2007 7:47 pm, edited 1 time in total |
|
| Back to top |
|
|
|
 |
securespark

Joined: 11 Jan 2004 Posts: 22509 Location: Cheshire, United Kingdom Thanked: 305 times
|
Posted: Mon Jun 18, 2007 7:47 pm |
|
|
| festa wrote: | | 1000w.........5amp fuse |
When I had a security lighting circuit running 1000W off a type 1 5A breaker, it kept tripping.poo poo farts |
|
| Back to top |
|
|
|
|
|
 |
securespark

Joined: 11 Jan 2004 Posts: 22509 Location: Cheshire, United Kingdom Thanked: 305 times
|
Posted: Mon Jun 18, 2007 7:48 pm |
|
|
| securespark wrote: | | festa wrote: | | 1000w.........5amp fuse |
When I had a security lighting circuit running 1000W off a type 1 5A breaker, it kept tripping.poo poo farts |
I must apologise....my 7 yo has just hijacked this post and written a load of juvenile toilet words.... something I'd never do...
What I meant to say was....
When I had a security lighting circuit running 1000W off a type 1 5A breaker, it kept tripping. I had to downgrade the load to 6/800W. |
|
| Back to top |
|
|
|
 |
bpowell555

Joined: 19 May 2005 Posts: 360 Location: Sussex, United Kingdom
|
Posted: Sun Sep 16, 2007 12:46 pm |
|
|
I was thinking of doing this but the light site is round the corner from the socket. Can I run the cable round outside at the top of the wall or do I need to chase it all the way up the inside and along the top of the wall to the middle of the patio doors and out? For the outside option I was wondering if I could run the cable 1.5m up the wall then inside again for the switch and then up from there?
Cheers! |
|
| Back to top |
|
|
|
 |
Tim 77

Joined: 13 Feb 2007 Posts: 565 Location: Nottingham, United Kingdom
|
Posted: Sun Sep 16, 2007 12:57 pm |
|
|
| securespark wrote: | | .poo poo farts |
Toilet talk, I get it all the time from my 4 year old son!  |
|
| Back to top |
|
|
|
 |
bpowell555

Joined: 19 May 2005 Posts: 360 Location: Sussex, United Kingdom
|
|
| Back to top |
|
|
|
|
|
 |
|
|