cable size for cooker
This topic originated from the How to page called Choosing the correct size cable
Click here to return to the page called Choosing the correct size cable.
  View previous topic :: View next topic
Author Message
country boy
from United Kingdom
Thanked: 0 times
PostPosted: Mon Oct 08, 2007 8:27 pm    Post Subject:
Reply with quote Thanks
We are moving to an all electric flat our new (Belling)cooker is rated at 9400 watts.
what size cable will this need?
Back to top
 Alert Moderators
If you don't want to see this advert, click here to login or if you are new click here to join free.
securespark
from United Kingdom
Thanked: 14 times
PostPosted: Mon Oct 08, 2007 8:55 pm    Post Subject:
Depends.
Whether you want to design the circuit to take flc or use diversity. Upon the cable length, route and other environmental factors.
__________________
As George Michael once said, "..if you're gonna do it, do it right, right?"
Back to top
 Alert Moderators
country boy
from United Kingdom
Thanked: 0 times
PostPosted: Mon Oct 08, 2007 9:03 pm    Post Subject:
Re: cable size for cooker
I should have said the cable in question is the one from the back of the cooker to the outlet in the wall.
Back to top
 Alert Moderators
loosenup
from United Kingdom
Thanked: 0 times
PostPosted: Mon Oct 08, 2007 9:55 pm    Post Subject:
Without seeing the circuit I would say that you need to have the circuit checked by a sparks .. only then can safe advise be given . there are so many factors to take into consideration when connecting a high power cooker to an existing circuit.. even to calculate diversity .
If you connect it with too small a cable then you will overload the cable to the fuseboard .. with a result of the very least the mcb tripping when you turn the main oven on. if you do not have an mcb in the CU then the results could be far worse .
Get a sparks in .
Safety first .
Phill
Back to top
 Alert Moderators
securespark
from United Kingdom
Thanked: 14 times
PostPosted: Mon Oct 08, 2007 10:21 pm    Post Subject:
Overloading the cable does not necessarily mean the CPD will operate...
__________________
Back to top
 Alert Moderators
loosenup
from United Kingdom
Thanked: 0 times
PostPosted: Tue Oct 09, 2007 3:26 pm    Post Subject:
true
Back to top
 Alert Moderators
SparkyMike
from United Kingdom
Thanked: 0 times
PostPosted: Thu Nov 08, 2007 12:19 pm    Post Subject:
cooker circuit
The rule of thumb for cooker circuits is:
32A MCB or 30A fuse
6mm flat Twin+Earth cable
Applying diversity:
9400w
9400/230 = 41Amps maximum
Formula: 10A + 30% of rest + 5A for any socket outlet
10 + 0.3 * 31 + 5 = 24.3A
We only need to cater for 24.3Amps or only 19.3Amps if no socket outlet.
If its a short run from the cooker to the consumer unit then you could get away with 4mm cable.
I would use 6mm cable just incase you get a bigger cooker in the future or the cable run is long.
Also if the cooker switch has a build in 13A socket and the flat is on the ground floor then ideally it should be protected by a 30mA RCD as well.
some old cookers will nuisence trip some RCDs due to there higher leakage currents. This is normal and nothing to worry about.
Back to top
 Alert Moderators
plugwash
from United Kingdom
Thanked: 16 times
PostPosted: Thu Nov 08, 2007 12:22 pm    Post Subject:
Before we give advice we need to know the following
1: what is the rating of the fuse/mcb protecting the circuit
2: what is the size of the existing cable in the circuit.
Back to top
 Alert Moderators
Display posts from previous:
Page 1 of 1
Jump to:
New cooker cable size 2 5240 Sat Dec 16, 2006 11:19 am