Without seeing the circuit I would say that you need to have the circuit checked by a sparks .. only then can safe advise be given . there are so many factors to take into consideration when connecting a high power cooker to an existing circuit.. even to calculate diversity .
If you connect it with too small a cable then you will overload the cable to the fuseboard .. with a result of the very least the mcb tripping when you turn the main oven on. if you do not have an mcb in the CU then the results could be far worse .
Get a sparks in .
Safety first .
Phill
Joined: 08 Nov 2007 Posts: 1 Location: Hampshire, United Kingdom Thanked: 0 times
Posted: Thu Nov 08, 2007 12:19 pm Post Subject:
cooker circuit
The rule of thumb for cooker circuits is:
32A MCB or 30A fuse
6mm flat Twin+Earth cable
Applying diversity:
9400w
9400/230 = 41Amps maximum
Formula: 10A + 30% of rest + 5A for any socket outlet
10 + 0.3 * 31 + 5 = 24.3A
We only need to cater for 24.3Amps or only 19.3Amps if no socket outlet.
If its a short run from the cooker to the consumer unit then you could get away with 4mm cable.
I would use 6mm cable just incase you get a bigger cooker in the future or the cable run is long.
Also if the cooker switch has a build in 13A socket and the flat is on the ground floor then ideally it should be protected by a 30mA RCD as well.
some old cookers will nuisence trip some RCDs due to there higher leakage currents. This is normal and nothing to worry about.