PostPosted: Tue Jul 13, 2004 2:01 pm    Post Subject:
Wiring a shed and pond
Reply with quote Thanks

I want to take a supply from the house via a 4 core armoured cable 2x live (L1 & L2), 1x neutral, 1x earth. L1 and L2 taken from house via RCB.
The cable will be run to the shed, L2 via a switch in the house, and terminated at a jct box. L1 will then be split into 2, 1 feed taken from the shed to supply a pond pump (continuous supply via RCB), the second feed via a timer to supply garden lights (3 off low power). L2 will be split into 2 supplies via MCB, one feed to supply a double socket, the other to feed 2 outside lights.
The reason for two supplies is so that I can isolate the shed and ouside lights from the house without isolating the pond and garden lights. Any problem with this arrangement? Do I need any additional protection in the feed to the pond and garden lights (currently (excuse the pun) an RCB)

icon_question.gif
Back to top
 Alert Moderators

If you don't want to see this advert, click here to login or if you are new click here to join free.
plugwash

from United Kingdom

Joined: 28 Mar 2004
Posts: 6930
Location: United Kingdom
Thanked: 15 times

PostPosted: Tue Jul 13, 2004 2:27 pm    Post Subject:
Reply with quote Thanks

seems ok

i would run from a 20A dedicated cuircuit (with rcd protection either from the rcd side of the board from a seperate rcd or by using an rcbo instead of a mcb) to a 2 module grid plus box with 20A switches for the 2 outgoing lives

http://www.tlc-direct.co.uk/Products/MKK3492.html
http://www.tlc-direct.co.uk/Products/MKK4891.html
http://www.tlc-direct.co.uk/Products/MKK3702.html
http://www.tlc-direct.co.uk/Products/MKK8891.html

at the shed end i would terminate into a 4 pole isolator http://www.tlc-direct.co.uk/Images/Products/size_3/WY921E.JPG
any sockets can be run directly off this for lights i would use fused connection units fitted with a 5A fuse

the armoured cable should be sized to be suitable for the length of the run i will advise on size when given the run lenth
Back to top
 Alert Moderators
Pymie

from United Kingdom

Joined: 13 Jul 2004
Posts: 4
Location: United Kingdom
Thanked: 0 times

PostPosted: Tue Jul 13, 2004 2:43 pm    Post Subject:
Electrics to pond and shed
Reply with quote Thanks

Thanks for advice.
Cable length is 30m to shed and then further 10m to pond. Not sure what the power requirements for pond is but probably 600W ish
Back to top
 Alert Moderators
ban-all-sheds

from United Kingdom

Joined: 27 Aug 2003
Posts: 21980
Location: London,
United Kingdom
Thanked: 78 times

PostPosted: Tue Jul 13, 2004 3:23 pm    Post Subject:
Reply with quote Thanks

Sounds like a borrowed neutral to me....

__________________
I mustn't warn people that the "experts" on the plumbing forum can't be trusted to tell the truth.
Back to top
 Alert Moderators
brown-nought

from United Kingdom

Joined: 02 Jul 2004
Posts: 211
Location: United Kingdom
Thanked: 0 times

PostPosted: Tue Jul 13, 2004 3:32 pm    Post Subject:
Re: Wiring a shed and pond
Reply with quote Thanks

Pymie wrote:
I want to take a supply from the house via a 4 core armoured cable 2x live (L1 & L2), 1x neutral, 1x earth. L1 and L2 taken from house via RCB.

The reason for two supplies is so that I can isolate the shed and ouside lights from the house without isolating the pond and garden lights. Any problem with this arrangement?
icon_question.gif


Sorry to be a pain but you cannot have a shared neutral across two different circuits.

Best option is to run two separate cables as this means there are no junction boxes etc with more than one supply to isolate.

Alternative: subject to cable sizing, fault loop imedance, earthing arrangements etc is to use the four cores for the supplies and the amour for the earth.
Back to top
 Alert Moderators
plugwash

from United Kingdom

Joined: 28 Mar 2004
Posts: 6930
Location: United Kingdom
Thanked: 15 times

PostPosted: Tue Jul 13, 2004 3:47 pm    Post Subject:
Reply with quote Thanks

but surely if they are running off a common breaker in the CU they are part of the same cuircuit
Back to top
 Alert Moderators
ban-all-sheds

from United Kingdom

Joined: 27 Aug 2003
Posts: 21980
Location: London,
United Kingdom
Thanked: 78 times

PostPosted: Tue Jul 13, 2004 3:48 pm    Post Subject:
Reply with quote Thanks

plugwash wrote:
but surely if they are running off a common breaker in the CU they are part of the same cuircuit

He's right you know.

icon_redface.gif icon_redface.gif icon_redface.gif

__________________
I mustn't warn people that the "experts" on the plumbing forum can't be trusted to tell the truth.
Back to top
 Alert Moderators
brown-nought

from United Kingdom

Joined: 02 Jul 2004
Posts: 211
Location: United Kingdom
Thanked: 0 times

PostPosted: Tue Jul 13, 2004 4:59 pm    Post Subject:
Reply with quote Thanks

Splitting hairs I know but the orginal post never said L1 & L2 were off the same supply in the house CU. It said off the same RCD (which could be a the split load CU RCD for example)

L2 is switched intended to be used as an isolator. (Isolators DP for single phases?) Its hard to isolated the neutral if its shared.
Back to top
 Alert Moderators
plugwash

from United Kingdom

Joined: 28 Mar 2004
Posts: 6930
Location: United Kingdom
Thanked: 15 times

PostPosted: Tue Jul 13, 2004 6:08 pm    Post Subject:
Reply with quote Thanks

well i presume when he says isolate evrything in the shed he means turn off functionally not isolate for maintinance

i suggested a 4 pole isolator at the shed end of teh armoured cable to provide local isolation of everything (includeing both lives) at that end
Back to top
 Alert Moderators
brown-nought

from United Kingdom

Joined: 02 Jul 2004
Posts: 211
Location: United Kingdom
Thanked: 0 times

PostPosted: Wed Jul 14, 2004 10:23 am    Post Subject:
Reply with quote Thanks

I'm going to correct what I wrote yesterday after thinking about it a bit more - I believe it was misleading/wrong.

brown-nought wrote:

L2 is switched intended to be used as an isolator. (Isolators DP for single phases?) Its hard to isolated the neutral if its shared.


Wrong - 416-01 ... isolators in TN installations do not need to isolate the neutral. Neutral isolation is only needed in TT and at the source of a single phase installation.

Burrowed neutrals - chapter 31 states final circuits need to have their own neutrals. Plugwash/Ban are right the final circuit here has its own neutral and the MCB can be used for isolation.

Obviously if you run a cable into a shed CU and then see the neutral looped out it might look odd on an inspection. However I guess if a diagram was attached and a warning notice of where to isolate was enclosed it would be ok.

Apologies for the confusion sometimes its too easy to jump into an answer without sufficent thought/verification. Wrists slapped. However I’d still personally be happier with two cables.

BN.
Back to top
 Alert Moderators
Pymie

from United Kingdom

Joined: 13 Jul 2004
Posts: 4
Location: United Kingdom
Thanked: 0 times

PostPosted: Thu Jul 15, 2004 1:12 pm    Post Subject:
Reply with quote Thanks

Thank you people.

The single cable is a convenience thing. However the supply is being fed off of a single source (the house ring main). The isolation of the shed circuit is to allow me to switch an outside light, mounted on the shed, from the house so that I can see my way to the shed at night. It will also have the benefit of isolating the shed without isolating the pump which needs to keep going 24 hrs a day apparently. For maintenance, I can isolate from the main CU.

I think from the debate, that the principle is acceptable.

Once again thanks.

icon_smile.gif
Back to top
 Alert Moderators
breezer

from United Kingdom

Joined: 03 Jan 2003
Posts: 23346
Location: Sussex,
United Kingdom
Thanked: 5 times

PostPosted: Thu Jul 15, 2004 5:25 pm    Post Subject:
Reply with quote Thanks

Pymie wrote:
the pump which needs to keep going 24 hrs a day apparently.


it does, see this

__________________
Do you like music Mr Finch?
Forum = Opinions
Back to top
 Alert Moderators
Pymie

from United Kingdom

Joined: 13 Jul 2004
Posts: 4
Location: United Kingdom
Thanked: 0 times

PostPosted: Fri Jul 16, 2004 8:03 am    Post Subject:
Pond & Shed etc etc
Reply with quote Thanks

Once again thanks.
Time to start digging trenches and shed foundations. Am I looking forward to that!
icon_rolleyes.gif
Back to top
 Alert Moderators
securespark

from United Kingdom

Joined: 11 Jan 2004
Posts: 16480
Location: Cheshire,
United Kingdom
Thanked: 14 times

PostPosted: Fri Jul 16, 2004 9:00 am    Post Subject:
Reply with quote Thanks

When you've finished can you come and help me dig up a large tree stump, and lay a driveway? Cheers.
Back to top
 Alert Moderators
Display posts from previous:   
  View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK All times are GMT
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
wiring a pond pump 4 1620 Tue Apr 22, 2008 8:40 am
pond pump 8 380 Thu Sep 27, 2007 7:18 pm
outside 240v pond pump 8 600 Sun May 20, 2007 2:07 pm
pond pump connection 6 440 Wed Oct 24, 2007 2:25 pm
Existing electrics for pond pump and filter. 15 1240 Fri Jan 04, 2008 11:58 am



DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
My DIYnot | Advertising | Newsletter
DIYnot.com | How to... | @home | Wiki | Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy.