Guys
Yes its that same ol topic once again...RCD tripping
The owner of the house tells me the 30 ma rcd started tripping daily ever since a storm 2 weeks ago and Western Power came out to repair a damaged overhead line feeding the premises
The combined insulation reading of the house with vereything connected is 0.2Megohms...Not good I know but too high to knock the trip off
Impedance is 35 ohms .I found that the RCD is tripping out at 20 milliamps
Ok so I changed the RCD and put a new Wylex one in
I tested this before installation in my own home and all ok
Damn when I got down to the property even this started tripping at 20 milliamps although it did "settle down and behave accordingly
I am wondering if anyone has any experience of the supply affecting RCD's cuz it seems strange that all this started after Western Power had done their stuff
I can understand that the above insulation test readings may not be helping but the original RCD had been put in about 10 years ago with minimal tripping and it seems a coincidence that all this has come about since the repair to the overhead supply
Cheers
Yes its that same ol topic once again...RCD tripping
The owner of the house tells me the 30 ma rcd started tripping daily ever since a storm 2 weeks ago and Western Power came out to repair a damaged overhead line feeding the premises
The combined insulation reading of the house with vereything connected is 0.2Megohms...Not good I know but too high to knock the trip off
Impedance is 35 ohms .I found that the RCD is tripping out at 20 milliamps
Ok so I changed the RCD and put a new Wylex one in
I tested this before installation in my own home and all ok
Damn when I got down to the property even this started tripping at 20 milliamps although it did "settle down and behave accordingly
I am wondering if anyone has any experience of the supply affecting RCD's cuz it seems strange that all this started after Western Power had done their stuff
I can understand that the above insulation test readings may not be helping but the original RCD had been put in about 10 years ago with minimal tripping and it seems a coincidence that all this has come about since the repair to the overhead supply
Cheers