does anyone know please if it is possible to test the value of the earth rod resistance Ra I believe using a 3 lead tester on an efli robin tester because the niceic book and other literature i have seen only shows a 2 lead tester on phase and earth rod ? any suggestions
Thankyou  |
|
| Back to top |
|
|
|
If you do not want to see this advert, click here to login or if you are new click here to join free. |
 |
sparkybird

Joined: 19 Jan 2005 Posts: 1118 Location: United Kingdom Thanked: 36 times
|
Posted: Sun Apr 06, 2008 10:08 am |
|
|
yes, IIRC look in Guidance Note 3 (testing and inspection) at method 2 for Ra testing.
Someone has nicked my copy or else I'd tell you the page!
SB |
|
| Back to top |
|
|
|
 |
TONY144

Joined: 16 Feb 2006 Posts: 44 Location: Staffordshire, United Kingdom
|
Posted: Sun Apr 06, 2008 11:30 am |
|
|
| sparkybird wrote: | yes, IIRC look in Guidance Note 3 (testing and inspection) at method 2 for Ra testing.
Someone has nicked my copy or else I'd tell you the page!
SB |
thanks will look
cheers
Tony |
|
| Back to top |
|
|
|
 |
Spark123

Joined: 02 Jun 2005 Posts: 13735 Location: Cumbria, United Kingdom Thanked: 338 times
|
|
| Back to top |
|
|
|
 |
TONY144

Joined: 16 Feb 2006 Posts: 44 Location: Staffordshire, United Kingdom
|
Posted: Sun Apr 06, 2008 9:40 pm |
|
|
That will give the ze reading i believe and not the resitance value of the earth electrode but correct me if i am wrong |
|
| Back to top |
|
|
|
|
|
 |
Spark123

Joined: 02 Jun 2005 Posts: 13735 Location: Cumbria, United Kingdom Thanked: 338 times
|
Posted: Mon Apr 07, 2008 4:37 pm |
|
|
What is the Ze in a TT system?
The black (neutral) is required to power the instrument and in some instances such as DLOC for the electronics to lock the RCD. |
|
| Back to top |
|
|
|
 |
plugwash

Joined: 28 Mar 2004 Posts: 7952 Location: United Kingdom Thanked: 125 times
|
Posted: Mon Apr 07, 2008 7:18 pm |
|
|
Assuming you measure with main bonding disconnected it is the output imedanace of the suppply transformer plus the impedance of your live supply condutor plus the impedance of your electrode plus the impedance of your suppliers electode.
In practice the impedance of your rod is likely to be much higher than any of the other things mentioned above and it is normal to use the Ze measurement as a conservative estimate of the impedance of your rod.
testing earth rod resistance seperately requires a different type of tester and several temporary test electrodes but there is rarely any reason to do it. |
|
| Back to top |
|
|
|
 |
Spark123

Joined: 02 Jun 2005 Posts: 13735 Location: Cumbria, United Kingdom Thanked: 338 times
|
Posted: Mon Apr 07, 2008 7:26 pm |
|
|
Yep, what is the difference between a Ze measured with a 3 wire efli tester and a Ze measured with a 2 wire efli tester? |
|
| Back to top |
|
|
|
 |
TONY144

Joined: 16 Feb 2006 Posts: 44 Location: Staffordshire, United Kingdom
|
Posted: Mon Apr 07, 2008 8:59 pm |
|
|
| Spark123 wrote: | | Yep, what is the difference between a Ze measured with a 3 wire efli tester and a Ze measured with a 2 wire efli tester? |
Thanks lads between you all i now have the answer to my initial question. |
|