Trianco EuroStar 70-90 Oil Boiler cutting in and out

Goto page 1, 2  Next
 
Post new topic   Reply to topic    DIYnot.com Forum Index > Plumbing and Central Heating
Search this topic :: View previous topic :: View next topic  
Author Message
Felmoman

from United Kingdom

Joined: 24 Oct 2009
Posts: 7
Location: United Kingdom

PostPosted: Sat Oct 24, 2009 1:46 pm Reply with quote

My Trianco EuroStar 70-90 oil boiler keeps cutting in and out. The oil burner keeps running and after approx 8 secs the igniter re-establishes the flame. It has a new nozzle and the oil pipe is clear. I have cleaned the photoresistor. The air setting is 7, could it be lack of oxygen? It has worked OK for two years at this setting. Any suggestions are most welcome.
Back to top
 Alert Moderators

If you do not want to see this advert, click here to login or if you are new click here to join free.
doitall

from United Kingdom

Joined: 08 Jan 2005
Posts: 18005
Location: Bath,
United Kingdom
Thanked: 1354 times

PostPosted: Sat Oct 24, 2009 1:50 pm Reply with quote

A good service, would sort the problem and save you a fortune on wasted oil.

You need specialist kit to set them up properly.
Back to top
The following user says thank you to doitall for this useful post:
Felmoman (24 Oct 2009)
 Alert Moderators
Felmoman

from United Kingdom

Joined: 24 Oct 2009
Posts: 7
Location: United Kingdom

PostPosted: Sat Oct 24, 2009 2:31 pm Reply with quote

doitall wrote:
A good service, would sort the problem and save you a fortune on wasted oil.

You need specialist kit to set them up properly.


Many thanks for your prompt reply. I agree, a good service may sort out the problem, my problem is that as a pensioner, I am unable to afford the high cost of a service unless I really have to. Can I hire the kit to monitor the flue gas?
Back to top
 Alert Moderators
doitall

from United Kingdom

Joined: 08 Jan 2005
Posts: 18005
Location: Bath,
United Kingdom
Thanked: 1354 times

PostPosted: Sat Oct 24, 2009 3:04 pm Reply with quote

You would more than save the expense over the winter.

It really is specialist kit, and you must know how to use it as well.

Should be well under a 100, unless it needs parts.

Ask your oil supplier, for a price.
Back to top
 Alert Moderators
Boilerman2

from United Kingdom

Joined: 10 Jun 2009
Posts: 4699
Location: Suffolk,
United Kingdom
Thanked: 852 times

PostPosted: Sat Oct 24, 2009 4:55 pm Reply with quote

Is it a Balanced Flue eurostar? (I'll bet that it is!!!)
The Flue seals on the inner flue duct are a real pain on the eurostar, Get your Engineer to remove the flue assembly and reaseal the joints icon_wink.gif
Back to top
 Alert Moderators
Felmoman

from United Kingdom

Joined: 24 Oct 2009
Posts: 7
Location: United Kingdom

PostPosted: Sat Oct 24, 2009 7:11 pm Reply with quote

Boilerman2 wrote:
Is it a Balanced Flue eurostar? (I'll bet that it is!!!)
The Flue seals on the inner flue duct are a real pain on the eurostar, Get your Engineer to remove the flue assembly and reaseal the joints icon_wink.gif

Thanks Boilerman2. Yes it is balanced flue and I like your suggestion. To test your theory all I need do is to disconnect the air input hose to the burner so that it draws air from atmosphere and not through the flue. I'll try it tomorrow. Many thanks
Back to top
 Alert Moderators
Felmoman

from United Kingdom

Joined: 24 Oct 2009
Posts: 7
Location: United Kingdom

PostPosted: Sat Oct 24, 2009 7:14 pm Reply with quote

doitall wrote:
You would more than save the expense over the winter.

It really is specialist kit, and you must know how to use it as well.

Should be well under a 100, unless it needs parts.

Ask your oil supplier, for a price.


Thanks "doitall" I'll try Boilerman2's suggestion first and if that does not work I'll do as you say and get a quote.
Back to top
 Alert Moderators
Boilerman2

from United Kingdom

Joined: 10 Jun 2009
Posts: 4699
Location: Suffolk,
United Kingdom
Thanked: 852 times

PostPosted: Sat Oct 24, 2009 7:21 pm Reply with quote

I don't remeber saying run the boiler with the snorkel tube disconnected!!!!

I will agree that this is a good way to prove that the flue seal are leaking, BUT IT IS NOT A PERMANENT REPAIR!!

With the snorkel removed the boiler will draw air from the room in which it is installed, and will need permanet ventilation which opens a whole can of worms.

The Boiler should be repair correctly so that it work with the snorkel properly fixed!

please do not twist the advice I have given! the advice about a Service by a oil Engineer is The Best possible advice icon_eek.gif icon_eek.gif icon_eek.gif
Back to top
 Alert Moderators
Felmoman

from United Kingdom

Joined: 24 Oct 2009
Posts: 7
Location: United Kingdom

PostPosted: Sat Oct 24, 2009 8:45 pm Reply with quote

Boilerman2 wrote:
I don't remeber saying run the boiler with the snorkel tube disconnected!!!!

I will agree that this is a good way to prove that the flue seal are leaking, BUT IT IS NOT A PERMANENT REPAIR!!

With the snorkel removed the boiler will draw air from the room in which it is installed, and will need permanet ventilation which opens a whole can of worms.

The Boiler should be repair correctly so that it work with the snorkel properly fixed!

please do not twist the advice I have given! the advice about a Service by a oil Engineer is The Best possible advice icon_eek.gif icon_eek.gif icon_eek.gif


Sorry for the misunderstanding but I did not intend it to be a permenent solution just a short test. I will replace the snorkel after the test and call in a Service Engineer. My boiler is in a vented boiler house and not in the house.
Back to top
 Alert Moderators
oilman

from United Kingdom

Joined: 16 Sep 2003
Posts: 7965
Location: United Kingdom
Thanked: 26 times

PostPosted: Sat Oct 24, 2009 11:16 pm Reply with quote

Boilerman2 wrote:

With the snorkel removed the boiler will draw air from the room in which it is installed, and will need permanet ventilation which opens a whole can of worms.


According to regulations, yes, but let's be practical about it. Many boilers run in houses where they get their air from inside the house, and there is no dedicated air supply and there is no measurable problem. The hole in the air shutter is considerably less than 1/2 sq in. Just disconnecting the hose is not too good if you leave the end open as exhaust will be delivered to the room. Stuff something up it.

Quote:
please do not twist the advice I have given! the advice about a Service by a oil Engineer is The Best possible advice icon_eek.gif icon_eek.gif icon_eek.gif


A service will not fix the problem, many technicians won't even be able to identify what the problem is. It will cost a good bit more than a service cost to get the flue sorted.

Bore a 4" hole through the wall, if your house is draught proofed, and fit a grill over the hole.
Back to top
 Alert Moderators
doitall

from United Kingdom

Joined: 08 Jan 2005
Posts: 18005
Location: Bath,
United Kingdom
Thanked: 1354 times

PostPosted: Sat Oct 24, 2009 11:55 pm Reply with quote

The boilers in a vented out building Oilman
Back to top
 Alert Moderators
casius66

from United Kingdom

Joined: 26 Dec 2008
Posts: 184
Location: Manchester,
United Kingdom
Thanked: 28 times

PostPosted: Sun Oct 25, 2009 10:20 am Reply with quote

The boiler needs to be working properly to be serviced, it needs to be repaired 1st then serviced, there's no getting around having to spend the money icon_wink.gif
Back to top
 Alert Moderators
cider

from United Kingdom

Joined: 25 Jul 2008
Posts: 3317
Location: Bristol,
United Kingdom
Thanked: 506 times

PostPosted: Sun Oct 25, 2009 11:18 am Reply with quote

That common conversation

Punter "Hello, could you please come and service my boiler asap please"

Me "why does it need servicing asap?"

Punter "because it it isnt working, but i think a service will fix it"

icon_rolleyes.gif
Back to top
 Alert Moderators
Felmoman

from United Kingdom

Joined: 24 Oct 2009
Posts: 7
Location: United Kingdom

PostPosted: Mon Oct 26, 2009 2:51 pm Reply with quote

casius66 wrote:
The boiler needs to be working properly to be serviced, it needs to be repaired 1st then serviced, there's no getting around having to spend the money icon_wink.gif


I have disconnected the snorkel from the flue and it is currently drawing air directly from the boiler house. So far the boiler has run without cutting in and out. I am leaving it another 24 hours in order to be really certain that we have identified the problem.

I have already spoken to the person who installed the boiler about the need to re-seal the joints in the balanced flue and if the test continues to be successful he will come and dismantle the flue and re-seal the joints.

I would like to thank everybody for their helpful advice and suggestions. Without your help I would still be at a loss as to the cause of the problem. Once again many thanks for your help.
Back to top
 Alert Moderators
Boilerman2

from United Kingdom

Joined: 10 Jun 2009
Posts: 4699
Location: Suffolk,
United Kingdom
Thanked: 852 times

PostPosted: Mon Oct 26, 2009 4:27 pm Reply with quote

It will take no more than an hour to pull out the centre flue and re-seal icon_wink.gif
Back to top
The following user says thank you to Boilerman2 for this useful post:
Felmoman (26 Oct 2009)
 Alert Moderators
Search this topic :: View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Plumbing and Central Heating All times are GMT
Goto page 1, 2  Next
Page 1 of 2

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
Trianco Eurostar Cutting out 4 1040 Tue Sep 05, 2006 9:45 am
Trianco Eurostar 70/90 Oil Boiler not working 7 500 Thu Oct 21, 2010 7:54 pm
Trianco Eurostar combi 90 oil boiler thermostat B tripping 10 600 Tue Nov 23, 2010 6:36 pm
Trianco Eurostar Combi 90 oil boiler Failing to lockout-Help 17 300 Sun Feb 06, 2011 4:50 pm
Trianco Eurostar Combi Boiler Thermostats! 3 20 Mon Oct 17, 2011 6:31 pm


 
DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
Network | Advertising | Newsletter
DIY | DIY How To | @home | DIY Wiki | DIY Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy. Copyright © 2000-2014 DIYnot Limited.