Correct colour code for switched-live

Goto page 1, 2  Next
 
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK
Search this topic :: View previous topic :: View next topic  
Author Message
rowanbradley

from United Kingdom

Joined: 30 Dec 2009
Posts: 3
Location: Suffolk,
United Kingdom

PostPosted: Wed Dec 30, 2009 11:26 pm Reply with quote

I'm wiring in a new outdoor photo-electric/time switch for my driveway light. The switch has three terminals, live, switched-live and neutral. Can anyone recommend the correct colour code for these three wires (and in particular for the switched-live wire)? The switch needs to have a single, round cable going to it, since it has to seal into a gland, and I need to buy a suitable cable.

If I can't get a suitable cable, is it allowed by the regulations to use a standard brown/blue/green-yellow cable and sleeve the ends to show the correct colours? Note that this will incolve sleeving the green-yellow cable to be something else - live or neutral.

If the above is not permitted, I guess the next alternative is to use 4-way cable, and just not use the earth wire (I can connect it to earth at the other end). If I do this, is it permissible to sleeve the other wires where they are not the correct colour?

Many thanks - Rowan
Back to top
 Alert Moderators

If you do not want to see this advert, click here to login or if you are new click here to join free.
Taylortwocities

from United Kingdom

Joined: 27 Jul 2006
Posts: 12490
Location: Oxfordshire,
United Kingdom
Thanked: 1028 times

PostPosted: Wed Dec 30, 2009 11:33 pm Reply with quote

The earth must be used and connected to earth at teh source end, even if the device it is feeding does not have an earth connection (eg for a double insulated device).

This conductor is a very important safety feature and will be required when you test the Earth Fault Loop Impedance before the circuit goes into service.

So you'll need 3 core and earth cable. Or 4-core flex. But see edit below.

Usually:
Brown is permanent live
Grey, sleeved with blue = neutral
Black, sleeved with brown = switched live.

Edit:
1. If this cable is being run outside you will probably need steel wired armoured cable. you cannot and must not drape PVC flex around your garden.
2. Are you aware that this work is notifiable under building regs Part P.
Please check the WIKI for information.


Last edited by Taylortwocities on Wed Dec 30, 2009 11:39 pm, edited 2 times in total
Back to top
 Alert Moderators
conny

from United Kingdom

Joined: 30 Jun 2008
Posts: 9488
Location: Liverpool,
United Kingdom
Thanked: 115 times

PostPosted: Wed Dec 30, 2009 11:35 pm Reply with quote

3 core +earth.

Brown- permanent live.
Blue - neutral,
yellow- switched live.
Earth - earth.

You cannot use the earth for anything other than earth under any circumstances

Damm again!

(TTC you a professional typist or summat? icon_lol.gif icon_lol.gif )
Back to top
 Alert Moderators
Taylortwocities

from United Kingdom

Joined: 27 Jul 2006
Posts: 12490
Location: Oxfordshire,
United Kingdom
Thanked: 1028 times

PostPosted: Wed Dec 30, 2009 11:38 pm Reply with quote

Yup, Pitmans trained 350,000 words per minute.


By the way, where do you get cable with brown, blue and yellow conductors icon_wink.gif
Back to top
 Alert Moderators
ColJack

from United Kingdom

Joined: 16 Feb 2007
Posts: 11773
Location: West Midlands,
United Kingdom
Thanked: 408 times

PostPosted: Wed Dec 30, 2009 11:43 pm Reply with quote

conny wrote:
3 core +earth.

Brown- permanent live.
Blue - neutral,
yellow- switched live.
Earth - earth.

You cannot use the earth for anything other than earth under any circumstances

Damm again!

(TTC you a professional typist or summat? icon_lol.gif icon_lol.gif )


you wanna try that answer again in one colour code or the other?
Back to top
 Alert Moderators
conny

from United Kingdom

Joined: 30 Jun 2008
Posts: 9488
Location: Liverpool,
United Kingdom
Thanked: 115 times

PostPosted: Thu Dec 31, 2009 12:31 am Reply with quote

Typing too quickly and got mixed up.
Please accept my apologies. icon_lol.gif

Quote:
350,000 words per minute


Not as fast as I thought then. icon_wink.gif
Back to top
 Alert Moderators
ericmark

from United Kingdom

Joined: 27 Jan 2008
Posts: 7686
Location: Flintshire,
United Kingdom
Thanked: 652 times

PostPosted: Thu Dec 31, 2009 1:41 am Reply with quote

In a single phase installation are Line (Phase) wires should be Brown and all Neutral wires should be Blue if colour system is used. With green and yellow for earth.

It is common to use cable coloured with the three phase colours of Brown, Black, and Grey and to sleeve the cables with brown or blue to identify however since the cable is not designed for what it is used for there are no colour codes.

For DC installations Brown and Grey are Phase colours so to used the remaining colour as neutral would make sense plus in past black was used for neutral so industrial electricians will tend to used black as the neutral so that all systems are the same.

However on split phase systems blue is often used as L2 even though L2 should be black so there will never be agreement in what colour to use. So long as the green/yellow and Cream is always used as earth any other colour can be sleeved with colours or numbers.

To say either Grey or Black should be used as Neutral or Switched line without explaining that there is no convention is dangerous as people can make the mistake of thinking this is a convention and make mistakes as a result.
Back to top
 Alert Moderators
TicklyT

from United Kingdom

Joined: 30 Jul 2006
Posts: 3480
Location: Hampshire,
United Kingdom
Thanked: 336 times

PostPosted: Thu Dec 31, 2009 7:00 am Reply with quote

ericmark wrote:
...For DC installations Brown and Grey are Phase colours ....


Does DC have a 'phase'? icon_confused.gif

DC distribution in some industries is identified as Grey = positive, which is usually maintained at about earth potential, and Blue = Negative, the live conductor. That replaced an earlier convention where Black was the live and Red was earthed.

OP - Use whatever makes sense to you, Identify the conductors with blue or brown sleeving and make a note for future reference, or use by others. A note on the inside of a cover can save a lot of head scratching later on.
Just don't use the CPC / earth wire for anything other than earth.
Back to top
 Alert Moderators
joinerjohn

from United Kingdom

Joined: 28 Nov 2009
Posts: 6145
Location: Derby,
United Kingdom
Thanked: 198 times

PostPosted: Thu Dec 31, 2009 2:48 pm Reply with quote

TTC says "The earth must be used and connected to earth at the source end, even if the device it is feeding does not have an earth connection (eg for a double insulated device). ".

With my limited understanding of electrics, the question goes begging. If the device being fed is double insulated and has no earth connection, How does the OP terminate the earth at the device?? Does he just cut it as short as possible?????
Might seem a daft question but surely you wouldn't want an earth wire that can't be terminated ?
Back to top
 Alert Moderators
sparkwright

from United Kingdom

Joined: 20 Aug 2009
Posts: 4199
Location: Dorset,
United Kingdom
Thanked: 520 times

PostPosted: Thu Dec 31, 2009 2:54 pm Reply with quote

you connect the earth wire to a piece of connector block, which you'll probably have to supply yourself.
Back to top
 Alert Moderators
Taylortwocities

from United Kingdom

Joined: 27 Jul 2006
Posts: 12490
Location: Oxfordshire,
United Kingdom
Thanked: 1028 times

PostPosted: Thu Dec 31, 2009 3:51 pm Reply with quote

joinerjohn wrote:
Might seem a daft question but surely you wouldn't want an earth wire that can't be terminated ?


The earth (cpc) is not there to make the device function but it is installed in order to provide a guaranteed earth return path for the circuit. It is there so that the cpd will disconnect quickly in the event of an earth fault at any point in the circuit (and that includes the cabling itself).
Back to top
 Alert Moderators
rowanbradley

from United Kingdom

Joined: 30 Dec 2009
Posts: 3
Location: Suffolk,
United Kingdom

PostPosted: Thu Dec 31, 2009 4:25 pm Reply with quote

ericmark wrote:
In a single phase installation are Line (Phase) wires should be Brown and all Neutral wires should be Blue if colour system is used. With green and yellow for earth.
And if I'm using this scheme, what colour should switched-live be? If I have to sleeve it, what colour should the sleeve be? I've seen yellow, brown, black and grey mentioned. It seems odd that such a common function as switched live should not have a standard colour. Sleeving it brown (which I've seen suggested) seems very unhelpful, and provides no way of distinguishing between the live feed to the switch, which should always be live, and the output from the switch, which will sometimes be live, and sometimes not (so voltage-wise it will be picking up neutral through the load). Using black seems a bad idea to someone who remembers the old cable with black for neutral.

Thanks - Rowan
Back to top
 Alert Moderators
mikhailfaradayski

from United Kingdom

Joined: 21 Jul 2009
Posts: 1677
Location: Derby,
United Kingdom
Thanked: 86 times

PostPosted: Thu Dec 31, 2009 4:32 pm Reply with quote

the sleeve should be brown. you don't need to sleeve it 100% of its length, so you would still be able to see the colour of the insulation beneath and identification won't be a problem.

imagine the cost and manufacturing implications of having to supply cables with additional colours just to get rid of sleeves.
Back to top
 Alert Moderators
securespark

from United Kingdom

Joined: 11 Jan 2004
Posts: 25199
Location: Cheshire,
United Kingdom
Thanked: 441 times

PostPosted: Thu Dec 31, 2009 4:53 pm Reply with quote

Sorry to hijack this!

Hi Rowan!

Just like to ask you a Q, if it's not rude: how old are you?

It's just that we have a son called Rowan and we only know three others:

Mr Atkinson.

Mr Williams.

and

Ms Pelling.

None share a generation!!

Thanks.

Normal service will be resumed as soon as possible.

Our Rowan is 5 btw!

EDIT: icon_redface.gif

Atkinson b 06/01/55

Williams b 14/06/50

and

Pelling b 17/01/68
Back to top
 Alert Moderators
Paul_C

from United Kingdom

Joined: 19 Nov 2004
Posts: 2137
Location: United Kingdom
Thanked: 139 times

PostPosted: Thu Dec 31, 2009 7:52 pm Reply with quote

rowanbradley wrote:
It seems odd that such a common function as switched live should not have a standard colour. Sleeving it brown (which I've seen suggested) seems very unhelpful


If you want to follow BS7671 to the letter, then all live conductors on a single-phase installation should be brown, either by the original color of the insulation of the wire or by sleeving. It's been this way for a very long time, i.e. under the "old" color code both live feed and switched live were supposed to be red.

As noted already, you can apply the sleeving but still be able to identify which wire is which from the underlying color.

To clarify the key points:

* Green/yellow conductors may be used only for a protective earth and should not be sleeved and used for any other purpose.

* Any other color conductor may be sleeved to match its intended use, including the application of green/yellow sleeving for use as an earth.
Back to top
 Alert Moderators
Search this topic :: View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK All times are GMT
Goto page 1, 2  Next
Page 1 of 2

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
switched wire colour code 2 480 Wed Jul 14, 2004 2:25 pm
wiring colour code 3 640 Mon Nov 19, 2007 5:58 pm
A Question about Wiring Colour Code Conventions 115 20040 Mon Mar 01, 2010 8:38 am
PIR defect code opinions please 11 680 Tue Jan 27, 2009 11:30 am
17 edition PIR fault code 36 3640 Tue Mar 25, 2008 5:56 pm


 
DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
Network | Advertising | Newsletter
DIY | DIY How To | @home | DIY Wiki | DIY Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy. Copyright © 2000-2014 DIYnot Limited.