ferroli falcon repeating lockout

This topic originated from the How to page called Problems associated with noises from the central heating system
Click here to return to the page called Problems associated with noises from the central heating system.

 
Post new topic   Reply to topic    DIYnot.com Forum Index > Plumbing and Central Heating
Search this topic :: View previous topic :: View next topic  
Author Message
bengasman

from United Kingdom

Joined: 28 Jan 2005
Posts: 30894
Location: London,
United Kingdom
Thanked: 2736 times

PostPosted: Tue Mar 15, 2005 3:34 pm Reply with quote

The boiler: ferroli falcon probably mark I.
The problem: lock out light comes on requiring reset; sometimes in heating mode sometimes in dhw mode.
When: usually after several hours working, but once gone in to lock out mode a second reset needed after only ten minutes. Once the boiler has to be reset it is usually a matter of resetting it for the rest of the day.
Tests done so far:
Valve. Modulates fine between 2 and 12 mb. Heating is range rated to minimum.
Inlet pressure fine.
Continuity between sensing electrode and board connection: less than 1 ohm.
100 degree stat is replaced, and has heat conducting paste on it.
System pressure is constant and never needs topping up.
Polarity is fine.
Boiler is about 5 years old.
No noticable blockage of the rads, they heat up quickly and completely from top to bottom.
Back to top
 Alert Moderators

If you do not want to see this advert, click here to login or if you are new click here to join free.
ollski

from United Kingdom

Joined: 08 Oct 2003
Posts: 4906
Location: Birmingham,
United Kingdom
Thanked: 55 times

PostPosted: Tue Mar 15, 2005 7:06 pm Reply with quote

Isn't that one the same as the modena 80e?, if it is try new ignition and flame rec electrodes......they bend, reduce the gap and cause lockout.
Back to top
 Alert Moderators
theplank

from United Kingdom

Joined: 26 Sep 2006
Posts: 2
Location: Coventry,
United Kingdom

PostPosted: Tue Sep 26, 2006 11:24 am Reply with quote

Fault :- lock out , boiler booming sound, unreliable ignition
indication :- black mark on inside of ignition chamber cover just below the flame/spark inspection window.

Between A Corgi reg engineer and myself (engineer) we have just found a fault within the Falcon Boiler. To describe the problem, the gas jets sit within a supporting assembly and some of the jets are looser than others. The spark electrode is above the gas jet at about 3mm, if this jet is loose in the assembly and the cover is too close to the electrode it sparks to the case, the effect of this is to make the ignition unreliable, also if the gas ignites when the sparking is to the case the boiler tends to make a "boom" sound since the chamber is full of gas at the time of ignition. We are in the process of eliminating this problem firstly a piece of mica has been inserted between the case and electrode, this worked for a couple of days, next is to earth the jet. We will see how it goes icon_confused.gif
Back to top
 Alert Moderators
ChrisR

from United Kingdom

Joined: 24 Jul 2003
Posts: 23273
Location: London,
United Kingdom
Thanked: 1034 times

PostPosted: Tue Sep 26, 2006 11:50 am Reply with quote

Interesting. As an aside, these can be useful in finding out whether an intermittently locking out boiler is overheating or not. Stick one on the flow pipe and see how hot it has been.

The pic shows it as the vertical, 8 level type.
Back to top
 Alert Moderators
Prodigy1978

from United Kingdom

Joined: 12 Feb 2009
Posts: 11
Location: Cardiff,
United Kingdom

PostPosted: Thu Mar 19, 2009 9:55 am Reply with quote

My Ferroli Falcon boiler has been playing up. I have had a new pressure release valve fitted after a problem with loss in pressure. That was roughly 2 months ago.

Recently I have been experiencing lock out problems which means I need to reset the boiler. This works fine for a day or two but the problem would continue. There has also been a booming sound, almost as id the boiler is about to blow of the wall! a little worrying icon_eek.gif

Could anyone advise me on the possible problem? is this something I could fix myself or would i need an engineer and they sting me for a new MCB board or similiar!

Thanks.
Back to top
 Alert Moderators
Search this topic :: View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Plumbing and Central Heating All times are GMT
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
Ferroli Falcon II Boiler - losing pressure 3 460 Thu Feb 05, 2009 12:03 pm
ferroli falcon boiler problem 5 760 Mon Apr 13, 2009 9:45 am
Ferroli FER Falcon Boiler CH problem 3 980 Fri Jan 09, 2009 2:19 pm
Ferroli Falcon boiler - heating not working 6 3020 Thu Jan 25, 2007 9:00 pm
Help needed - Ferroli falcon II boiler. Pump runs randomly 3 600 Sat Aug 29, 2009 10:33 am


 
DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
Network | Advertising | Newsletter
DIY | DIY How To | @home | DIY Wiki | DIY Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy. Copyright © 2000-2014 DIYnot Limited.