water heater circuit

This topic originated from the How to page called Routing cable
Click here to return to the page called Routing cable.
Goto page 1, 2  Next
 
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK
  View previous topic :: View next topic  
Author Message
stet19

from United Kingdom

Joined: 30 Mar 2005
Posts: 20
Location: United Kingdom
Thanked: 0 times

PostPosted: Wed Mar 30, 2005 2:02 pm    Post Subject:
water heater circuit
Reply with quote Thanks

Hi

I'm installing a new radiator in the bathroom connected to the central heating system. I intend to have an electric element for occasional use in summer.

I want to use the separate supply to the immersion heater in the hot water tank to supply the element. I have never used the immersion heater - the water is normally heated from a gas-fired boiler - but I want to keep the capability.

I know it would be wrong to extend the heater circuit. My question is: is there a household changeover switch so that they can't both be on at the same time and is that legitimate icon_question.gif
Back to top
 Alert Moderators

If you don't want to see this advert, click here to login or if you are new click here to join free.
Diyisfun

from United Kingdom

Joined: 15 Jun 2004
Posts: 4113
Location: London,
United Kingdom
Thanked: 9 times

PostPosted: Wed Mar 30, 2005 2:29 pm    Post Subject:
Reply with quote Thanks

Its usual to have the immersion on a manual switch, to do what you want I don't think would be simple.
But why would you want it?, you will use the gas always unless you have a failure, then you would manually change to electric.
Thats how I and I am certain most people would use & do use it.
Back to top
 Alert Moderators
Scoby_Beasley

from United Kingdom

Joined: 01 May 2003
Posts: 1253
Location: United Kingdom
Thanked: 0 times

PostPosted: Wed Mar 30, 2005 3:06 pm    Post Subject:
Reply with quote Thanks

I've said this before, but if you live in a hard water area your immersion can fail due to lack of use/coating up. use it occasionally (monthly ???) to keep it "clean".

__________________
Scoby

Here for a good time,
Not a long one.
Back to top
 Alert Moderators
mapj1

from United Kingdom

Joined: 24 Nov 2004
Posts: 1040
Location: United Kingdom
Thanked: 0 times

PostPosted: Wed Mar 30, 2005 3:31 pm    Post Subject:
Reply with quote Thanks

It is OK, but non-standard, to use a suitable double pole double throw switch as a change-over so both cannot be on at once.
Similar things can be done with houses with 2 showers or 2 cookers.

However, like new exam questions confuse both students and examiners, and are not popular with either, so do departures from standard circuits, so these need to be clearly labelled and there needs to be a better reason than ' it was easier than running a new wire to the board' before you do it.

Note whne considering loading that a 16A MCB will blow before a 13A fuse, at all currents.

__________________
regards Mike(G7VZY)
-STICKY Reference Info @ top of forum, Has diagrams & answers to common probs-
Back to top
 Alert Moderators
kevplumb

from United States of America

Joined: 18 May 2004
Posts: 19144
Location: Tennessee,
United States of America
Thanked: 400 times

PostPosted: Wed Mar 30, 2005 3:32 pm    Post Subject:
Reply with quote Thanks

think he means an electric element in the rad/towel rail guys icon_confused.gif

__________________
a little thanks

goes a long way
Back to top
 Alert Moderators
mapj1

from United Kingdom

Joined: 24 Nov 2004
Posts: 1040
Location: United Kingdom
Thanked: 0 times

PostPosted: Wed Mar 30, 2005 5:24 pm    Post Subject:
Reply with quote Thanks

yes, thats how I read it too - but to heat his towel rail from the feed that would have done the immersion, but to wire it as either/or
and I stand by 'its non-standard and I dont recommend it' !

__________________
regards Mike(G7VZY)
-STICKY Reference Info @ top of forum, Has diagrams & answers to common probs-
Back to top
 Alert Moderators
plugwash

from United Kingdom

Joined: 28 Mar 2004
Posts: 6930
Location: United Kingdom
Thanked: 15 times

PostPosted: Thu Mar 31, 2005 3:19 am    Post Subject:
Re: water heater circuit
Reply with quote Thanks

stet19 wrote:
Hi

I'm installing a new radiator in the bathroom connected to the central heating system. I intend to have an electric element for occasional use in summer.

I want to use the separate supply to the immersion heater in the hot water tank to supply the element. I have never used the immersion heater - the water is normally heated from a gas-fired boiler - but I want to keep the capability.

I know it would be wrong to extend the heater circuit. My question is: is there a household changeover switch so that they can't both be on at the same time and is that legitimate icon_question.gif


you could use a switch like http://www.tlc-direct.co.uk/Products/KMT338212I.html

then you have one position for the immersion heater one for the heated towel rail and one for off

its unusual but i can't see anything wrong with doing it especially if the immersion is very rarely used.
Back to top
 Alert Moderators
stet19

from United Kingdom

Joined: 30 Mar 2005
Posts: 20
Location: United Kingdom
Thanked: 0 times

PostPosted: Thu Mar 31, 2005 3:03 pm    Post Subject:
Reply with quote Thanks

Thanks guys. Sorry I wasn't here to clarify but yes it is a heating element for a towel rail that I'm installing. icon_redface.gif

Scoby thanks for the advice on preserving the immersion heater. I'd never thought about it before.

I'm surprised that my proposal is so unusual, it seemed the most convenient solution. However, and much as I like the idea of fitting that impressive changeover switch (thanks Plugwash), it may be better to take a spur off the ring main as its only a 200W element I'm fitting (assuming that's ok ).
Back to top
 Alert Moderators
ban-all-sheds

from United Kingdom

Joined: 27 Aug 2003
Posts: 21985
Location: London,
United Kingdom
Thanked: 78 times

PostPosted: Thu Mar 31, 2005 4:54 pm    Post Subject:
Reply with quote Thanks

I can't see anything wrong with using the immersion circuit. Without a changeover switch. An extra 200W won't overload it, so provided you use an FCU with a 3A fuse and document what the circuit is for you won't be doing anything dangerous.

__________________
I mustn't warn people that the "experts" on the plumbing forum can't be trusted to tell the truth.
Back to top
 Alert Moderators
stet19

from United Kingdom

Joined: 30 Mar 2005
Posts: 20
Location: United Kingdom
Thanked: 0 times

PostPosted: Thu Mar 31, 2005 11:27 pm    Post Subject:
Reply with quote Thanks

Thanks sheds. That'll do for for me. icon_biggrin.gif I just assumed that such a spur (although not necessarily dangerous) would be illegal.
Back to top
 Alert Moderators
ban-all-sheds

from United Kingdom

Joined: 27 Aug 2003
Posts: 21985
Location: London,
United Kingdom
Thanked: 78 times

PostPosted: Fri Apr 01, 2005 11:04 am    Post Subject:
Reply with quote Thanks

It's not illegal, and it is not dangerous.

The worst it could be is contrary to the IEE Wiring Regulations, which does not make it illegal, but should give you pause to check that you have covered all the bases:

What's the capacity of the cable given how it's installed.
Is the maximum load less than the rating of the MCB which in turn is less than the capacity of the cable.
Is the circuit appropriately labelled at the CU so that it is obvious how to isolate the towel rail.

__________________
I mustn't warn people that the "experts" on the plumbing forum can't be trusted to tell the truth.
Back to top
 Alert Moderators
stet19

from United Kingdom

Joined: 30 Mar 2005
Posts: 20
Location: United Kingdom
Thanked: 0 times

PostPosted: Sat Apr 02, 2005 8:45 am    Post Subject:
Reply with quote Thanks

Thanks again. The 3kw immersion has its own labelled 16A MCB in the CU, so there is no problem with the additional 200w towel rail heater - 3A fused switch appropriately labelled of course icon_smile.gif

Just a thought - 1mm cable is more than adequate for the load, but would this be unacceptable for other reasons.
Back to top
 Alert Moderators
Adam_151

from United Kingdom

Joined: 17 Jun 2004
Posts: 4539
Location: United Kingdom
Thanked: 10 times

PostPosted: Sat Apr 02, 2005 9:12 am    Post Subject:
Reply with quote Thanks

You should connect the supply side of the fcu to your existing 16A radial circuit using 2.5mm cable, but if fuseing at 3A, you can connect the 200w load to the load side of the fcu with 1mm if you wish (though you might want to use 2.5mm cable to avoid purchasing a different size of cable, nothing wrong with using thicker cable than necessary, as long as you can connect the ends ok), also don't connect the twin+e direct to the heater, use a flex outlet plate, but make sure this goes in the appropiate part of the bathroom though (zone 3, or out of zones, IIRC)

EDIT:

or if you are putting the fcu near the load, (remember the zoneing) , get one with a built in flex outlet, 2.5mm twin+e earth from the 16A radial circuit to the supply terminals, flex from the load terminals, out through the flex outlet hole, and to the heater and stick a 3A fuse in it.
Back to top
 Alert Moderators
stet19

from United Kingdom

Joined: 30 Mar 2005
Posts: 20
Location: United Kingdom
Thanked: 0 times

PostPosted: Sat Apr 02, 2005 5:00 pm    Post Subject:
Reply with quote Thanks

Understood. Thanks for all the advice guys.
Back to top
 Alert Moderators
ban-all-sheds

from United Kingdom

Joined: 27 Aug 2003
Posts: 21985
Location: London,
United Kingdom
Thanked: 78 times

PostPosted: Sun Apr 03, 2005 12:32 am    Post Subject:
Reply with quote Thanks

And if it's going on a tiled wall, a bead of silicone sealant run around the edge of the faceplate just before you fully tighten the screws is a good idea.

__________________
I mustn't warn people that the "experts" on the plumbing forum can't be trusted to tell the truth.
Back to top
 Alert Moderators
Display posts from previous:   
  View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK All times are GMT
Goto page 1, 2  Next
Page 1 of 2

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
redundant water heater circuit - ok for new combi boiler 2 180 Thu Dec 04, 2008 12:23 pm
lost hot water, water heater fuse off 3 160 Thu Dec 18, 2008 11:05 pm
Electrical Immersion Heater - No Hot Water 5 160 Mon Dec 29, 2008 8:14 pm
4.6kw Water heater on a 10amp fuse??!! 9 460 Fri Apr 28, 2006 5:21 pm
Water heater wiring advice please 11 240 Tue May 26, 2009 3:59 pm