I am hoping someone can help, as I have looked through this very helpful forum and nothing matches my boilers symptoms!

I have a Vaillant turbomax plus 828E and when the heating is not on and hot water is demanded the water comes out luke warm, the temperature on the display reads just under 40 deg C, and does not really change from this. However, the green light flashes and the orange light comes on, so it is seeing a demand for hot water, and you can hear the boiler starting up.

I thought it must be a diverter valve fault, but when this occurs the pipe to the central heating stays cold, so i don't think it can be this.

However, when the central heating has been on for a little while and then hot water is demanded then the water temperature is much better - although not as hot as it was a week or so ago when this fault first started.

Could this be the secondary heat exchanger being blocked up?

Any help appreciated?
Back to top
The following user says thank you to confusedmoon for this useful post:
jimmy36 (6 Jan 2012)
 Alert Moderators

If you do not want to see this advert, click here to login or if you are new click here to join free.
Agile

from United Kingdom

Joined: 26 Jun 2004
Posts: 53343
Location: London,
United Kingdom
Thanked: 3381 times

PostPosted: Tue Jan 25, 2011 3:06 pm Reply with quote

Without further diagnostic information, particularly a thermal survey, I cannot be so sure.

What do d40 and d41 read when providing hot water?

Tony
Back to top
The following user says thank you to Agile for this useful post:
confusedmoon (26 Jan 2011)
 Alert Moderators
confusedmoon

from United Kingdom

Joined: 25 Jan 2011
Posts: 4
Location: Sussex,
United Kingdom
Thanked: 1 time

PostPosted: Tue Jan 25, 2011 7:16 pm Reply with quote

Thanks for that, I had a look into it when I got back from work and found the following.

D40 was at 32 then when I ran the hot water it rose to 38.
D41 had no value associated with it.
D7 was set at 39.

When I played with the hot water temperature control dial, turning it up to max resulted in d7 reading 50. The minimum setting made d7 equal to 20.

So with the hot water control turned up to max, and so a d7 of 50 I then ran the hot water and it was warmer, with d40 rising to reach 50 degrees. I thought I had tried turning the control to max before but I obviously was not patient enough, and didnt know how to monitor what was happening.

This I think explains the behaviour of the boiler as with the central heating on the flow temperature rises to 65, and so when the hot water is demanded the primary circuit is at around 65 so the water comes out warmer, but then cools slowly.

So the problem now I think is that the maximum setting on the hot water system is only 50. Is there a way that I can increase this?
I know the boiler can do it as two weeks ago it was providing piping hot water!

Thanks for any advice you can give me!
Back to top
 Alert Moderators
Bunnyman

from United Kingdom

Joined: 22 Mar 2010
Posts: 3841
Location: Northamptonshire,
United Kingdom
Thanked: 1110 times

PostPosted: Tue Jan 25, 2011 10:14 pm Reply with quote

Run the tap press the I button what's the status code?
Back to top
 Alert Moderators
Bunnyman

from United Kingdom

Joined: 22 Mar 2010
Posts: 3841
Location: Northamptonshire,
United Kingdom
Thanked: 1110 times

PostPosted: Tue Jan 25, 2011 10:17 pm Reply with quote

It sounds like it's either doin warmstart,do u have the tap symbol shown on display or just the letter c flashing or u have snapped the hot water knob an the spindle is not turn in the pot on the pcb
Back to top
The following user says thank you to Bunnyman for this useful post:
confusedmoon (26 Jan 2011)
 Alert Moderators
confusedmoon

from United Kingdom

Joined: 25 Jan 2011
Posts: 4
Location: Sussex,
United Kingdom
Thanked: 1 time

PostPosted: Wed Jan 26, 2011 9:02 am Reply with quote

Run the tap press the I button what's the status code?

The status code is S 14
Back to top
 Alert Moderators
confusedmoon

from United Kingdom

Joined: 25 Jan 2011
Posts: 4
Location: Sussex,
United Kingdom
Thanked: 1 time

PostPosted: Mon Jan 31, 2011 11:26 am Reply with quote

Over the weekend I have been looking into the problem more. I can get the hot water to come out at a decent temperature when the heating is on by changing the settings for D73 (Warmstart offset Temperature), which makes it possible to change the setting D7 (warmstart temperature) to a higher value.

However, when the heating is off, the hot water does not work, the status code switches to S14 (hotwater operation), but the boiler does not provide enough heat to maintain the primary circuit temperature from the warm start setting, and so the temperature of the water starts off warm and then drops off untill cold.

Any ideas?
Back to top
 Alert Moderators
Agile

from United Kingdom

Joined: 26 Jun 2004
Posts: 53343
Location: London,
United Kingdom
Thanked: 3381 times

PostPosted: Tue Feb 01, 2011 5:32 pm Reply with quote

With the boiler completely cold, can you measure the resistance of each sensor ( with the plug disconnected ).

You have not mentioned the hot water flow rate. Lets consider the normal flow rate of 9 litres per minute.

Can you set the flow rate to half of that, namely 4.5 li/min, and tell us the relevant temperatures?

Tony
Back to top
 Alert Moderators
The831Bunny

from United Kingdom

Joined: 18 Mar 2008
Posts: 935
Location: United Kingdom
Thanked: 461 times

PostPosted: Sat Feb 12, 2011 10:45 pm Reply with quote

Has the PCB been changed recently?
Back to top
 Alert Moderators
Bunnyman

from United Kingdom

Joined: 22 Mar 2010
Posts: 3841
Location: Northamptonshire,
United Kingdom
Thanked: 1110 times

PostPosted: Sat Feb 12, 2011 11:43 pm Reply with quote

I know what ur thinking mr 831 !
Back to top
 Alert Moderators
Search this topic :: View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Plumbing and Central Heating All times are GMT
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
Vaillant Turbomax Plus 828e hot water problem 11 720 Sun Oct 16, 2011 9:56 am
Vaillant Turbomax plus 828e Hot water problem 8 140 Sun Apr 13, 2014 8:56 am
Vaillant Turbomax Plus 828E Problem 2 420 Sun Feb 14, 2010 2:41 pm
Vaillant 828E TurboMax Combi Boiler Pressure Gauge Problem 8 140 Sun Jan 27, 2013 8:09 pm
Vaillant Turbomax Plus 828e - No hot water 15 220 Fri Sep 20, 2013 7:45 am


 
DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
Network | Advertising | Newsletter
DIY | DIY How To | @home | DIY Wiki | DIY Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy. Copyright © 2000-2014 DIYnot Limited.