Split Load Consumer Unit or Not ??

This topic originated from the How to page called Changing a fuse on the consumer unit
Click here to return to the page called Changing a fuse on the consumer unit.

 
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK
  View previous topic :: View next topic  
Author Message
john_boy_02

from United Kingdom

Joined: 21 May 2005
Posts: 3
Location: Staffordshire,
United Kingdom
Thanked: 0 times

PostPosted: Sat May 21, 2005 3:14 pm    Post Subject:
Split Load Consumer Unit or Not ??
Reply with quote Thanks

Hi all.

Hope you can help me out with a little question I have.
I have just bought a Hager split load consumer unit ready for a local electrician to fit. When it has been delivered, and I have opened it up, to my untrained eyes it looks just like a normal (not split load) CU.
Should it have two separate metal bars (DIN bar?)???
Hope you can help me

Regards
john_boy
Back to top
 Alert Moderators

If you don't want to see this advert, click here to login or if you are new click here to join free.
andy

from United Kingdom

Joined: 14 Sep 2004
Posts: 3972
Location: United Kingdom
Thanked: 0 times

PostPosted: Sat May 21, 2005 4:04 pm    Post Subject:
Reply with quote Thanks

it should have an isolator and a RCD. 1 busbar goes from the isolator and 1 from the RCD. there are also 2 neutral blocks

there is only 1 din rail


Last edited by andy on Sat May 21, 2005 4:05 pm, edited 1 time in total
Back to top
 Alert Moderators
Screwi

from United Kingdom

Joined: 09 Mar 2005
Posts: 48
Location: United Kingdom
Thanked: 0 times

PostPosted: Sat May 21, 2005 4:04 pm    Post Subject:
Reply with quote Thanks

If you have the mcbs and the rcd then the bus bar gets cut to the required length by your spark.


There should be two seperate neutral connections and one earth bar also
Back to top
 Alert Moderators
Screwi

from United Kingdom

Joined: 09 Mar 2005
Posts: 48
Location: United Kingdom
Thanked: 0 times

PostPosted: Sat May 21, 2005 4:07 pm    Post Subject:
Reply with quote Thanks

If you get supplied with a couple of sets of internal tails - then these link out from the switch to the rcd - then the rcd to the top rail busbar to the rcd side of the mcbs, the switch connectors get linked to the bus bar going to the non rcd protected mcbs - if you understand all that LOL icon_razz.gif icon_evil.gif icon_question.gif icon_idea.gif

Neutrals from the rcd mcbs must be on a seperate connector strip than the non rcd protected mcbs.
_______________________
moderator

Screwi, please note 10a
Back to top
 Alert Moderators
kai

from United Kingdom

Joined: 15 Aug 2004
Posts: 729
Location: United Kingdom
Thanked: 5 times

PostPosted: Sat May 21, 2005 5:34 pm    Post Subject:
Re: Split Load Consumer Unit or Not ??
Reply with quote Thanks

john_boy_02 wrote:
Hi all.

Hope you can help me out with a little question I have.
I have just bought a Hager split load consumer unit ready for a local electrician to fit. When it has been delivered, and I have opened it up, to my untrained eyes it looks just like a normal (not split load) CU.
Should it have two separate metal bars (DIN bar?)???
Hope you can help me

Regards
john_boy


Most modern Consumer Units have just ONE din-rail, that is the 35mm wide rail on which the breakers clip onto.

The copper busbar i.e. the plate that feeds power from the mainswitch to the breakers, is mounted separately, and there is one busbar for each side of the split load unit.
Back to top
 Alert Moderators
john_boy_02

from United Kingdom

Joined: 21 May 2005
Posts: 3
Location: Staffordshire,
United Kingdom
Thanked: 0 times

PostPosted: Sat May 21, 2005 8:14 pm    Post Subject:
Reply with quote Thanks

Thanks for all of your [very comprehensive] replies.

I already have the mcbs, but . .

there were no busbars with it, no internal tails (i guess these are he cables) - only the case with a din rail (yes 35mm width) and two terminal blocks.

The model is a Hager VU8D, but I can't really find enough info on it on their website, and no reference to it being split-load. The bloke whgo sold it me says "The manufacturers described it as a MKII which has the option of a 4 + 4 split load or a straight 8 way load, the split requiring 2 isolators"

I will need more help (and parts !!!) from my lecci I suppose. I was only trying to save time, but it's not been too successful

Once again, thanks for your help
Back to top
 Alert Moderators
andy

from United Kingdom

Joined: 14 Sep 2004
Posts: 3972
Location: United Kingdom
Thanked: 0 times

PostPosted: Sat May 21, 2005 8:59 pm    Post Subject:
Reply with quote Thanks

john_boy_02 wrote:
Thanks for all of your [very comprehensive] replies.

I already have the mcbs, but . .

there were no busbars with it, no internal tails (i guess these are he cables) - only the case with a din rail (yes 35mm width) and two terminal blocks.

The model is a Hager VU8D, but I can't really find enough info on it on their website, and no reference to it being split-load. The bloke whgo sold it me says "The manufacturers described it as a MKII which has the option of a 4 + 4 split load or a straight 8 way load, the split requiring 2 isolators"

I will need more help (and parts !!!) from my lecci I suppose. I was only trying to save time, but it's not been too successful

Once again, thanks for your help


it sas it has the option of split load... it doesnt say it is split load... best to let your spark get the stuff needed, since he actually knows what he's lookin for
Back to top
 Alert Moderators
ban-all-sheds

from United Kingdom

Joined: 27 Aug 2003
Posts: 21990
Location: London,
United Kingdom
Thanked: 78 times

PostPosted: Sun May 22, 2005 9:35 am    Post Subject:
Reply with quote Thanks

1) 4 + 4 is a bit small.

2) Did the guy in the shop ask you what type of supply you have (i.e. what type of earthing arrangement) when he sold you this?

3) Are you sure that your electrician is OK with you supplying the parts?

__________________
I mustn't warn people that the "experts" on the plumbing forum can't be trusted to tell the truth.
Back to top
 Alert Moderators
john_boy_02

from United Kingdom

Joined: 21 May 2005
Posts: 3
Location: Staffordshire,
United Kingdom
Thanked: 0 times

PostPosted: Sun May 22, 2005 7:11 pm    Post Subject:
Reply with quote Thanks

Bought off eBay on the strength of the description - live and learn

Yes, he was OK me buying the bits - i was only trying to get things ready for when he can do the job next month !!!

You reckon 4+4 is a bit small for my house then ??? I only have a 4 way old style fusebox at the moment
Back to top
 Alert Moderators
andy

from United Kingdom

Joined: 14 Sep 2004
Posts: 3972
Location: United Kingdom
Thanked: 0 times

PostPosted: Sun May 22, 2005 7:46 pm    Post Subject:
Reply with quote Thanks

john_boy_02 wrote:
Bought off eBay on the strength of the description - live and learn

Yes, he was OK me buying the bits - i was only trying to get things ready for when he can do the job next month !!!

You reckon 4+4 is a bit small for my house then ??? I only have a 4 way old style fusebox at the moment
when houses are re-wired there is often a lot more than 8 circuits...
Back to top
 Alert Moderators
plugwash

from United Kingdom

Joined: 28 Mar 2004
Posts: 6930
Location: United Kingdom
Thanked: 15 times

PostPosted: Sun May 22, 2005 7:53 pm    Post Subject:
Reply with quote Thanks

well before we had our extention built we only had 6 cuircuits (2 lighting 3 rings and an immersion heater cuircuit)

now we have
2 lighting cuircuits
3 rings
1 16A radial for loft socket (it was formally on the immersion cuircuit which the electrician told us wasn't acceptable)
1 outside power cuircuit (was formally on a fcu from a ring)
1 electric shower
1 immersion heater cuircuit

i'd imagine that this count is fairly typical for a reasonablly sized house with fairly modern wiring.
Back to top
 Alert Moderators
ban-all-sheds

from United Kingdom

Joined: 27 Aug 2003
Posts: 21990
Location: London,
United Kingdom
Thanked: 78 times

PostPosted: Mon May 23, 2005 6:24 am    Post Subject:
Reply with quote Thanks

john_boy_02 wrote:
Bought off eBay on the strength of the description - live and learn

I hope that 4+4 refers to the number of ways that the box provides after you've installed an incomer and an RCD...

Quote:
Yes, he was OK me buying the bits - i was only trying to get things ready for when he can do the job next month !!!

Before you go any further with your purchasing, this is important - do you have a TT supply? (See the For Reference topic for explanations and diagrams)

Quote:
You reckon 4+4 is a bit small for my house then ??? I only have a 4 way old style fusebox at the moment


OK - now, the items on the list below may not all apply to you, but they are worth thinking about:


  1. Upstairs ring
  2. Downstairs ring
  3. Kitchen ring
  4. Radial for appliances
  5. Cooker circuit
  6. Non-RCD circuit for F/F
  7. Non-RCD circuit for CH boiler
  8. Dedicated circuit for hifi
  9. Dedicated circuit for IT equipment
  10. Upstairs lights
  11. Downstairs lights
  12. Immersion heater
  13. Shower
  14. Alarm
  15. Supply for outside lights
  16. Supply for garden electrics
  17. Supply for shed/garage


Plus any peculiarities brought about by your house layout & construction - e.g. in mine because of solid floors and where the rings run, I have a radial just for a socket in the hall, the doorbell and the porch lights.

Plus a few spares on RCD & non-RCD sides for expansion beyond that for future unforeseen needs.

__________________
I mustn't warn people that the "experts" on the plumbing forum can't be trusted to tell the truth.
Back to top
 Alert Moderators
Display posts from previous:   
  View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK All times are GMT
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
Split load consumer unit in garage 26 1320 Sat Nov 10, 2007 12:31 pm
Question about recently fitted split load consumer unit 15 2180 Mon Oct 25, 2004 9:35 pm
RCD Problems on new split load consumer unit 21 2820 Sun Oct 24, 2004 10:06 am
Split Load Consumer Unit 20 1400 Mon May 30, 2005 1:17 pm
SPLIT LOAD CONSUMER UNIT now with photos of present consumer 24 2400 Wed Aug 15, 2007 4:04 pm