Hi there


We have pro combi 85 HE combi boiler which suddenly started going into lock out with solid red light.
When this happens the only way to get it working is to turn the main electricity switch off for a while then the boiler will reset and will work for short period of time before it goes to lock out again.
Accidently I find out that if I increase the temp from the controls the boiler will work fine for weeks without any obvious problems.

any ideas as to what can be causing this?

I've added a boiler diagram:


Last edited by peterfb on Sun Mar 20, 2011 9:25 am, edited 4 times in total
Back to top
 Alert Moderators

If you do not want to see this advert, click here to login or if you are new click here to join free.
stef99

from United Kingdom

Joined: 01 Dec 2010
Posts: 90
Location: United Kingdom
Thanked: 1 time

PostPosted: Sun Mar 20, 2011 1:51 am Reply with quote

Im only offering help here as no-one else has, Your problem seems to be the temperature sensor inside the boiler, I know this is vague, but you could try looking at that first, There maybe some info about it in the installers instructions, failing that, remove it and give it a good clean?
Back to top
 Alert Moderators
Mrmethane

from Australia

Joined: 19 Mar 2011
Posts: 18
Location: South Australia,
Australia
Thanked: 2 times

PostPosted: Sun Mar 20, 2011 3:11 am Reply with quote

Hello

When the boiler locks out is it in heating or hot water mode, or both. It does sound a little like a flow problem which would maybe cause the appliance to cut out on over temp. Have you restricted the flow at all, shut down some radiators or removed some, or are the TRVs shutting down in warmer weather. A bit of history may help identify the issue.
Back to top
 Alert Moderators
peterfb

from United Kingdom

Joined: 19 Mar 2011
Posts: 7
Location: London,
United Kingdom

PostPosted: Sun Mar 20, 2011 8:58 am Reply with quote

Mrmethane wrote:
Hello

When the boiler locks out is it in heating or hot water mode, or both. It does sound a little like a flow problem which would maybe cause the appliance to cut out on over temp. Have you restricted the flow at all, shut down some radiators or removed some, or are the TRVs shutting down in warmer weather. A bit of history may help identify the issue.


Hi
I edited the original post as I meant that I have to turn the main electricity switch off for a while in order to get the boiler to reset.

It does this in both modes and started suddenly. It's a four year old boiler never had any problems before
Back to top
 Alert Moderators
peterfb

from United Kingdom

Joined: 19 Mar 2011
Posts: 7
Location: London,
United Kingdom

PostPosted: Sun Mar 20, 2011 9:05 am Reply with quote

stef99 wrote:
Im only offering help here as no-one else has, Your problem seems to be the temperature sensor inside the boiler, I know this is vague, but you could try looking at that first, There maybe some info about it in the installers instructions, failing that, remove it and give it a good clean?


Hi there are two thermistors inside the boiler according to the schematic. If I attempt to replace them is there a chance for water leakage or they are not in direct contact with the water passing through the boiler so no need to drain the system in order to replace?
Thanks
Back to top
 Alert Moderators
Mrmethane

from Australia

Joined: 19 Mar 2011
Posts: 18
Location: South Australia,
Australia
Thanked: 2 times

PostPosted: Sun Mar 20, 2011 9:16 am Reply with quote

I had a quick look online to see if I could find a user guide, I found one for the Vokera if its your model I am not sure, but it does say if the light is red and permanently on then it has a over temperature fault. This can be something has simple has a faulty sensor, a problem with the pump or a main pcb fault.
The over temperature sensor isolates the boiler to protect it from overheating, when the burner ignites for example when you turn on your hot tap the burner usually goes into high burn to generate hot water flow. If this flow is insufficient to remove the heat and the temperature within the heat exchanger rises to unacceptable levels the over temp sensor will shut the unit down.
This is why you have to wait a little while before it will reset, it has to cool down a little first.
Sensors are the first thing to look at, however there are a number of things that could generate that fault, the pump being another. I am not familiar with the Vokera so you should find yourself a decent service engineer and have it checked out fitting the wrong part could prove costly.
Back to top
 Alert Moderators
Mrmethane

from Australia

Joined: 19 Mar 2011
Posts: 18
Location: South Australia,
Australia
Thanked: 2 times

PostPosted: Sun Mar 20, 2011 9:18 am Reply with quote

Usually thermisitors clip on to pipe work and do not require water isolation to replace
Back to top
 Alert Moderators
Mrmethane

from Australia

Joined: 19 Mar 2011
Posts: 18
Location: South Australia,
Australia
Thanked: 2 times

PostPosted: Sun Mar 20, 2011 9:47 am Reply with quote

On the left is the over temperature sensor, is it 240V or low voltage, do you have a multimeter?
Back to top
 Alert Moderators
peterfb

from United Kingdom

Joined: 19 Mar 2011
Posts: 7
Location: London,
United Kingdom

PostPosted: Sun Mar 20, 2011 9:50 am Reply with quote

Mrmethane wrote:
I had a quick look online to see if I could find a user guide, I found one for the Vokera if its your model I am not sure, but it does say if the light is red and permanently on then it has a over temperature fault. This can be something has simple has a faulty sensor, a problem with the pump or a main pcb fault.
The over temperature sensor isolates the boiler to protect it from overheating, when the burner ignites for example when you turn on your hot tap the burner usually goes into high burn to generate hot water flow. If this flow is insufficient to remove the heat and the temperature within the heat exchanger rises to unacceptable levels the over temp sensor will shut the unit down.
This is why you have to wait a little while before it will reset, it has to cool down a little first.
Sensors are the first thing to look at, however there are a number of things that could generate that fault, the pump being another. I am not familiar with the Vokera so you should find yourself a decent service engineer and have it checked out fitting the wrong part could prove costly.


Thanks Mrmethane,

When I turn the hot water temp knob to a lower temp setting the produced hot water is not very hot but boiler lockouts very quickly. when I turn it to a high temp setting(almost to the end of the scale) the boiler works fine(at least worked for the last 2 weeks) and the produced hot water is very hot but it works.

I had an engineer to look at it who scratched his head for a while, checked the air pressure switch and the venturi, checked the radiator circulating water for impurities (it turned out there is a chemical inside which apparently keeps the system clean) then went away unable to diagnose the exact cause. He did mention the PCB but did not check the board itself.
This is the reason I'm looking for some help on here before another expensive visit of a "specialist".
Back to top
 Alert Moderators
peterfb

from United Kingdom

Joined: 19 Mar 2011
Posts: 7
Location: London,
United Kingdom

PostPosted: Sun Mar 20, 2011 9:54 am Reply with quote

Mrmethane wrote:
On the left is the over temperature sensor, is it 240V or low voltage, do you have a multimeter?


Yes I do. Everything inside the boiler attached to the PCB works on 24DC.
Do you mean 26. The hot water sensor?
Back to top
 Alert Moderators
Mrmethane

from Australia

Joined: 19 Mar 2011
Posts: 18
Location: South Australia,
Australia
Thanked: 2 times

PostPosted: Sun Mar 20, 2011 7:46 pm Reply with quote

No the high limit stat number 20, test this when the boiler next locks out and see if this has tripped, if it has then you have to determine if it is tripping at too low a temperature, or is the water in the boiler too hot, and if so why.
Yo stated earlier that if you increased the water temperature on the appliance it worked longer, did you mean the heating temperature or the domestic water temperature?
Back to top
 Alert Moderators
peterfb

from United Kingdom

Joined: 19 Mar 2011
Posts: 7
Location: London,
United Kingdom

PostPosted: Sun Mar 20, 2011 10:26 pm Reply with quote

Mrmethane wrote:
No the high limit stat number 20, test this when the boiler next locks out and see if this has tripped, if it has then you have to determine if it is tripping at too low a temperature, or is the water in the boiler too hot, and if so why.
Yo stated earlier that if you increased the water temperature on the appliance it worked longer, did you mean the heating temperature or the domestic water temperature?


Thanks Mrmethane,

I'll measure it next time it lock out. will the boiler require to be drained in order to replace the thermostat?
I did indeed increased both hot water and heating on the boiler. I haven't experimented anymore once i got it in sort of stable state until I have a solid idea what can be the culprit
Back to top
 Alert Moderators
Mrmethane

from Australia

Joined: 19 Mar 2011
Posts: 18
Location: South Australia,
Australia
Thanked: 2 times

PostPosted: Mon Mar 21, 2011 7:26 am Reply with quote

Try to determine through a process of elimination what the increase in temperature does to your appliance, does it increase the pump speed, does a bypass valve shut, what? Most boiler service instructions include a flow chart showing the operation.
I am still convinced that it is a over heat problem but what is causing it is the mystery, also all the information you have and can think of will help you get to the source of the problem. Think what is happening within the appliance, only with regard to the flow of water through it. It comes on following a call for heat, i.e a time control or thermostat, the pump starts and water flows through the heat exchanger, the burner fires and heat transfer occurs.
Simple calculations will show you what the flow rate should be through the appliance at various burner rates. As you can imagine if the flow rate is too slow the water increases in temperature too quickly and becomes dangerous, thats when the over heat cuts in and protects the appliance. By turning the water temperature up you have altered the way it operates and therefore overcome the problem. The trick is now, what does turning the temperature up do to the appliance?

Good luck
Back to top
 Alert Moderators
peterfb

from United Kingdom

Joined: 19 Mar 2011
Posts: 7
Location: London,
United Kingdom

PostPosted: Wed Mar 23, 2011 7:17 pm Reply with quote

Mrmethane wrote:
Try to determine through a process of elimination what the increase in temperature does to your appliance, does it increase the pump speed, does a bypass valve shut, what? Most boiler service instructions include a flow chart showing the operation.
I am still convinced that it is a over heat problem but what is causing it is the mystery, also all the information you have and can think of will help you get to the source of the problem. Think what is happening within the appliance, only with regard to the flow of water through it. It comes on following a call for heat, i.e a time control or thermostat, the pump starts and water flows through the heat exchanger, the burner fires and heat transfer occurs.
Simple calculations will show you what the flow rate should be through the appliance at various burner rates. As you can imagine if the flow rate is too slow the water increases in temperature too quickly and becomes dangerous, thats when the over heat cuts in and protects the appliance. By turning the water temperature up you have altered the way it operates and therefore overcome the problem. The trick is now, what does turning the temperature up do to the appliance?

Good luck

Thanks Mrmethane.
Back to top
 Alert Moderators
callumk1

from United Kingdom

Joined: 01 May 2013
Posts: 1
Location: Bedfordshire,
United Kingdom

PostPosted: Wed May 01, 2013 7:08 pm Reply with quote

hi. it sounds like your plated heat exchange is clogged
needs replacing or descaling.
Back to top
 Alert Moderators
Search this topic :: View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Plumbing and Central Heating All times are GMT
Goto page 1, 2  Next
Page 1 of 2

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
vokera lockout problem 12 7600 Sun Nov 21, 2004 10:42 pm
Vokera Mynute 20e lockout problem. 2 1120 Sun Jan 01, 2006 3:13 pm
Vokera 24e lockout 8 4580 Sat Nov 04, 2006 6:01 pm
vokera 24 compact lockout 3 100 Wed Jun 15, 2011 4:09 pm
Vokera Compact28 Lockout 5 640 Mon May 28, 2007 6:48 pm


 
DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
Network | Advertising | Newsletter
DIY | DIY How To | @home | DIY Wiki | DIY Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy. Copyright © 2000-2014 DIYnot Limited.