What is the tightness test pressure fora medium pressureTEST

Goto page 1, 2  Next
 
Post new topic   Reply to topic    DIYnot.com Forum Index > Plumbing and Central Heating
Search this topic :: View previous topic :: View next topic  
Author Message
joeread

from United Kingdom

Joined: 03 Feb 2011
Posts: 29
Location: Surrey,
United Kingdom

PostPosted: Fri Jul 08, 2011 7:50 am Reply with quote

??????
Back to top
 Alert Moderators

If you do not want to see this advert, click here to login or if you are new click here to join free.
adlplumbing

from United Kingdom

Joined: 09 Dec 2009
Posts: 4475
Location: Lancashire,
United Kingdom
Thanked: 312 times

PostPosted: Fri Jul 08, 2011 7:57 am Reply with quote

read your books it is their
it also help you learn
and once you passed it chance are you never need it again as never seen one yet outside a class room
Back to top
 Alert Moderators
namsag

from United Kingdom

Joined: 12 May 2004
Posts: 9909
Location: United Kingdom
Thanked: 321 times

PostPosted: Fri Jul 08, 2011 10:40 am Reply with quote

edit . apologises for wrong answer earlier you test at 19mbar on some and 20 on others depndant on how it is configured.
Lots of new estates out there with it


Last edited by namsag on Fri Jul 08, 2011 7:47 pm, edited 2 times in total
Back to top
 Alert Moderators
numpty1

from United Kingdom

Joined: 30 Nov 2007
Posts: 1820
Location: United Kingdom
Thanked: 266 times

PostPosted: Fri Jul 08, 2011 3:48 pm Reply with quote

Quote:
and once you passed it chance are you never need it again as never seen one yet outside a class room


A little knowledge can be dangerous,have not seen a cubic ft dial in at least ten years nor worked on low pressure reg for the same amount but i still have to know how to test and rate them,its known as competence
Back to top
 Alert Moderators
adlplumbing

from United Kingdom

Joined: 09 Dec 2009
Posts: 4475
Location: Lancashire,
United Kingdom
Thanked: 312 times

PostPosted: Fri Jul 08, 2011 6:27 pm Reply with quote

yes or you can look it up when you need to know
or ring a freind
Back to top
 Alert Moderators
Boilerman2

from United Kingdom

Joined: 10 Jun 2009
Posts: 4900
Location: Suffolk,
United Kingdom
Thanked: 910 times

PostPosted: Fri Jul 08, 2011 6:34 pm Reply with quote

What do you mean by "Medium Pressure"???? if OP is more than 75Mb
you will need to test to IGE UP1 which is far and beyond a Domestic UP1/B test and will require the services of one or more operatives with the relevent qualifications!! icon_wink.gif
Back to top
 Alert Moderators
namsag

from United Kingdom

Joined: 12 May 2004
Posts: 9909
Location: United Kingdom
Thanked: 321 times

PostPosted: Fri Jul 08, 2011 7:49 pm Reply with quote

I take it he is on about standard domestic meter set up and that is nothing special
Back to top
 Alert Moderators
petit_pablo

from United Kingdom

Joined: 18 Nov 2007
Posts: 7085
Location: Lincolnshire,
United Kingdom
Thanked: 1176 times

PostPosted: Fri Jul 08, 2011 8:11 pm Reply with quote

Quote:
What do you mean by "Medium Pressure"????

Medium pressure is in scope for CCN1. Not a problem testing and purging it on domestic ticket.
Back to top
 Alert Moderators
monoxide62

from United Kingdom

Joined: 01 Jul 2011
Posts: 874
Location: United Kingdom
Thanked: 102 times

PostPosted: Fri Jul 08, 2011 10:40 pm Reply with quote

Maybe a bit confusing to some , gas service pipe up to medium pressue regulator will be 2 bar pressure as opposed to 75mb , tightness test is carried out @ 19mb.
Back to top
 Alert Moderators
Terrywookfit

from Antarctica

Joined: 19 Jul 2007
Posts: 2327
Location: Antarctica
Thanked: 270 times

PostPosted: Sat Jul 09, 2011 12:47 am Reply with quote

petit_pablo wrote:
Quote:
What do you mean by "Medium Pressure"????

Medium pressure is in scope for CCN1. Not a problem testing and purging it on domestic ticket.


Not in CCN1 any more.
A meter inlet valve should now be fitted after the governor to test installation.
Back to top
 Alert Moderators
namsag

from United Kingdom

Joined: 12 May 2004
Posts: 9909
Location: United Kingdom
Thanked: 321 times

PostPosted: Sat Jul 09, 2011 1:07 am Reply with quote

monoxide .read the pages in the book before it mentions19 mb
Back to top
 Alert Moderators
monoxide62

from United Kingdom

Joined: 01 Jul 2011
Posts: 874
Location: United Kingdom
Thanked: 102 times

PostPosted: Sat Jul 09, 2011 1:54 am Reply with quote

namsag wrote:
monoxide .read the pages in the book before it mentions19 mb


What book are you refering too? , 5th edition-revised?

TT without MIV........ Let-by @ zero mb , TT 19mb.

TT with MIV.....Let-by @ 10mb , TT 20mb.

No MIV = NCS.

Does your refference material suggest otherwise?

Thanks.
Back to top
 Alert Moderators
petit_pablo

from United Kingdom

Joined: 18 Nov 2007
Posts: 7085
Location: Lincolnshire,
United Kingdom
Thanked: 1176 times

PostPosted: Sat Jul 09, 2011 6:48 am Reply with quote

Terrywookfit wrote:


Not in CCN1 any more.
A meter inlet valve should now be fitted after the governor to test installation.


Thats a bonus, i am due to do acs end of this year. Thats one less thing to worry about then!
Back to top
 Alert Moderators
namsag

from United Kingdom

Joined: 12 May 2004
Posts: 9909
Location: United Kingdom
Thanked: 321 times

PostPosted: Sat Jul 09, 2011 8:21 am Reply with quote

Petite.
There is only 1 question on medium pressure and its a really basic one, think it was double ecv.


Monoxide yep its one of those trick questions where if asked it would be easy to answer either 19 or 20 but then have to explain what pressure is used and when.
Back to top
 Alert Moderators
bengasman

from United Kingdom

Joined: 28 Jan 2005
Posts: 30937
Location: London,
United Kingdom
Thanked: 2750 times

PostPosted: Sat Jul 09, 2011 10:25 am Reply with quote

Why don't you read your books in stead of asking silly questions here? All you need to know for you exam is in there.
Back to top
 Alert Moderators
Search this topic :: View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Plumbing and Central Heating All times are GMT
Goto page 1, 2  Next
Page 1 of 2

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
Medium Pressure Gas Meter - Bodged Installation 4 1040 Thu Feb 09, 2012 9:29 am
recommendations fora corgi bod to fix my boiler in tottenham 5 480 Tue Aug 22, 2006 4:25 pm
Tightness test 14 1020 Sat Mar 10, 2007 2:50 pm
How can I test solder joints for air tightness?.... 2 700 Wed Jan 10, 2007 9:57 am
reinstated fire - tightness test before????? 14 580 Mon Nov 22, 2010 10:22 am


 
DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
Network | Advertising | Newsletter
DIY | DIY How To | @home | DIY Wiki | DIY Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy. Copyright © 2000-2014 DIYnot Limited.