Soupdragon43

from United Kingdom

Joined: 08 Aug 2005
Posts: 14
Location: United Kingdom

PostPosted: Mon Aug 08, 2005 8:59 pm Reply with quote

Hi, we moved into a house last year which has a 2 (now almost 3) year old Vaillant Combi Boiler (think it is the TurboMax). The water takes an absolute age to get hot - anything upwards of five minutes and even then it is never 'scalding' enough to get pans soaked etc! I have had two corgi engineers out who both reckon there is nothing wrong with it!

Anyway, my latest problem is that it has today shut itself down with error code F28 - boiler block out due to insufficient gas supply or faulty valve etc. It would appear that the boiler has done this before as the previous owners have made a note of this error code on the front cover of the manual.

Has anyone any ideas what this is and what is going on with this boiler. The heating side seems to work fine (obviously not today because it is totally off!)

So far I aint very impressed with Vaillant!
Back to top
 Alert Moderators

If you do not want to see this advert, click here to login or if you are new click here to join free.
chrishutt

from St. Pierre and Miquelon

Joined: 20 May 2005
Posts: 5344
Location: St. Pierre and Miquelon
Thanked: 19 times

PostPosted: Mon Aug 08, 2005 9:15 pm Reply with quote

Fault code F28 covers a variety of faults, but most likely in your case is a problem with ignition, i.e. defective igniter, ignition lead or ignition probe. It's unlikely that your gas supply has been lost, but just check that no one's turned it off! Anyway these things are Corgi territory, so you need a competent engineer.

As for the 5 minute delay before hot water comes through, this can't be right unless you've got a run of maybe 500 metres of pipe from boiler to hot tap! Might be best to get Vaillant's own engineers to look, since it seems you haven't been able to find anyone competent locally.
Back to top
 Alert Moderators
Soupdragon43

from United Kingdom

Joined: 08 Aug 2005
Posts: 14
Location: United Kingdom

PostPosted: Mon Aug 08, 2005 9:28 pm Reply with quote

Thanks Chris. I did check the meter just in case but everything looks okay and the lever for the supply is still on - it was working earlier today but by the evening it stopped.

I have a corgi engineer coming tomorrow first thing, hopefully they will sort it.

I will consider paying for a Vaillant engineer to come out, as you say it can't be right waiting that long for the hot water to get thru.
Back to top
 Alert Moderators
ChrisR

from United Kingdom

Joined: 24 Jul 2003
Posts: 23353
Location: London,
United Kingdom
Thanked: 1072 times

PostPosted: Mon Aug 08, 2005 10:05 pm Reply with quote

Consistent with the gas valve sticking. RRP is about 100 inc vat. It would be interesting to know what it is, especially if the problem's something else!
Back to top
 Alert Moderators
corgigazza

from United Kingdom

Joined: 29 Dec 2004
Posts: 1743
Location: Bedfordshire,
United Kingdom
Thanked: 301 times

PostPosted: Tue Aug 09, 2005 6:33 pm Reply with quote

pcb's are known to go faulty on these boilers causing lockout f28, to check ignition turn off gas supply and run through 4 or 5 ignition sequences checking for good strong blue spark at electrode with no missfires.

hw fault may be diverter valve may not be operating correctly(rads get warm when running hw for 5 mins), dwh heat exchanger blocked(hw not very hot but burner cycles on /off and flow from main h/e to dhw h/e hot but return cold to main h/e, undersized gas pipe ie only 15mm or gas meter set under pressure, aqua sensor may be sticking(when running hot tap green led flashes to show this is working).
all corgi job only
Back to top
 Alert Moderators
Soupdragon43

from United Kingdom

Joined: 08 Aug 2005
Posts: 14
Location: United Kingdom

PostPosted: Wed Aug 10, 2005 8:25 am Reply with quote

Thanks for you help guys. Engineer replaced gas control valve and now back to normal. He agrees that the water takes too long to get warm but states that this is due to boilers location (in an 'outbuilding' that has now been attached to the house) and the length of pipes etc!! I give up for now!
Back to top
 Alert Moderators
ChrisR

from United Kingdom

Joined: 24 Jul 2003
Posts: 23353
Location: London,
United Kingdom
Thanked: 1072 times

PostPosted: Wed Aug 10, 2005 9:28 am Reply with quote

Just checking - are you aware of the "keep a bit of water hot on standby" feature, which Vaillant call something more elegant? You turn it on by putting the water temp knob to max, so the green(?) light comes on permanently. Repeating turns the mode off.

This will reduce your waiting time.
Back to top
 Alert Moderators
Soupdragon43

from United Kingdom

Joined: 08 Aug 2005
Posts: 14
Location: United Kingdom

PostPosted: Wed Aug 10, 2005 8:08 pm Reply with quote

Thanks Chris, I'm sure we've tried this in the past, I think its called warmstart or something, and it didn't seem to make much difference. I guess we are just cursed or something! We're moving house anyway but was just trying to get an idea if Vaillant were a good make or not as we may have to put central heating into the house we are moving into. I heard Worcester and Bosch were the best boilers around (different topic I realise now!!)
Back to top
 Alert Moderators
Search this topic :: View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Plumbing and Central Heating All times are GMT
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
Vaillant TURBOmax Plus 824 E / 828 E Combi Boiler Problems 4 10620 Mon Oct 02, 2006 3:04 pm
Vaillant turbomax combi boiler problems 7 2500 Sat Aug 08, 2009 10:14 pm
Problems with Vaillant Turbomax combi not firing up on HW 35 620 Tue Aug 06, 2013 3:31 pm
vaillant combi vcw gb 242 e Hot water problems. 2 60 Fri Feb 10, 2012 3:07 pm
Problems with Vaillant Ecotec Pro 24 boiler and Danfoss ther 49 1320 Wed Oct 16, 2013 10:40 pm


 
DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
Network | Advertising | Newsletter
DIY | DIY How To | @home | DIY Wiki | DIY Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy. Copyright © 2000-2014 DIYnot Limited.