I am in the final stages of installing a new 10.5kW electric shower in our top bathrooom. I have installed the shower, cable goes into a 50A ceiling-mounted isolator switch, then down two floors, into new 30mA RCD, then into spare 40A MCB on existing consumer unit. Two questions/issues:
1. When I finally got it all going last night, turning on the isolator switch caused the switch to blow ("bang!") before tripping the MCB. Any ideas what would cause this? I'm sure I wired the switch correctly.
2. I know I probably need a 45A or 50A MCB rather than the 40A I am trying to use, but can't seem to find one of these for my CU (100A Wylex), and am I right in thinking this wouldn't be the cause of the problem above anyway?
Help really appreciated.
Thanks,
Steve Hadaway
Steve
A 10.5Kw shower will draw 46Amps so no wonder it blew a 40Amp MCB but it sounds like you have a short as drawing more the the MCB can handle is unlikely to cause a 'bang'
Try checking for a short between phase and neutral on the shower side of the switch.
Are you aware of part P and any circuit should be successfully tested before energising, this is for your safety.
What readings did you get for insulation resistance and earth continuity before you energised the circuit?
Testing????
Surely the cicuit was tested before energising!!!!!!!!!!!!!!!
Would anyone like to place any bets.
Thanks for your help, and no (as an amateur) I didn't carry out the level of testing you indicated (have no tools to measure insulation resistance or earth continuity), although I did as much research as I could, followed detailed instructions to the letter and checked and rechecked everything I did!!
That all said, clearly something is wrong so will check connections on shower side of the switch as suggested.
On the MCB point, will a 45A current definitely trip my 40A MCB (i.e. any chance I can get away with using that?) Have searched for a 45A/50A MCB for my CU, but can't seem to find one (e.g. screwfix sell this 40A one but nothing more:
http://www.screwfix.com/app/sfd/cat/pro.jsp?id=77992&ts=87803
Does anyone know if MCBs >40A of this type are available?
Thanks again for help
SH
A 45A current will eventually trip a 40A MCB but not instantly with a bang as you describe. A current of 1.45 x 40A = 58A must cause a trip within 1 hour. The bang you describe indicates there is a short circuit.
It is difficult to fault find without specialist equipment such as an insulation resistance tester. You are probably better calling in a sparky friend to sort this out.
You can buy a 45A (green base) cartridge fuse. This fuse / breaker must go next to the switch as it is keyed. http://www.tlc-direct.co.uk/Manufacturers/Wylex/Wylex_Standard_Carriers/index.html
Youve wired the double pole switch up wrong - youve wired the switch so it shorts live and neautral instead of live to live etc etc.
Maybe, but also could have damaged cable, insecure connections, faulty shower unit......
Will check but 99% certain that's how I did it (except switch was marked feed rather than supply - I'm sure semantics).
Thanks for everyone's help
Oh: one other question - as I said, switch made a pretty big flash and bang before flipping the MCB. Can I assume I should fit a new switch rather than reuse that one....?
Cheers.
Cheers.
By asking that question, I am sure you already know the answer.
Don't refit a switch which is too small again, fit a 45A fuse instead.
Better fix the problem first though, replacing the fuse and switching it on again isn't going to fix anything.
Qedelec said:
Steve
Probably not - the headline rating quoted by manufacturers is nearly always at 240V, i.e. 43.75A. Since our supply usually is 240V in practice, that's a likely actual current - if we ever do end up on 230V, it'll be 40.2A.
But anyway - 43.75A is 1.09 x In - the MCB will pass that for hours, possibly for ever.
Are you aware of part P.
A question still unanswered by our petitioner.
mrchook said:
switch made a pretty big flash and bang.
Strongly indicative of a supply/load rotation, or a downstream cable fault.
If so will almost certainly have knackered the switch.
Thanks - have ordered a new switch and will check my wiring and cabling again.
Wasn't aware of Part P., but have read about it now.....
Thanks - SH.