running mains cable

This topic originated from the How to page called Routing cable
Click here to return to the page called Routing cable.

 
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK
  View previous topic :: View next topic  
Author Message
victorvanderzel

from United Kingdom

Joined: 07 Sep 2005
Posts: 7
Location: United Kingdom
Thanked: 0 times

PostPosted: Wed Sep 07, 2005 1:41 pm    Post Subject:
running mains cable
Reply with quote Thanks

I want to put some power sockets in our new conservatory. I am planning to spur it off a socket in the living room (drill through the wall). In the conservatory I want to nail the cable to the concrete floor before the final floor screed goes down. Is this OK, or does the cable have to run in the Wall.
Thanks Victor
Back to top
 Alert Moderators

If you don't want to see this advert, click here to login or if you are new click here to join free.
Adam_151

from United Kingdom

Joined: 17 Jun 2004
Posts: 4542
Location: United Kingdom
Thanked: 10 times

PostPosted: Wed Sep 07, 2005 3:05 pm    Post Subject:
Reply with quote Thanks

Only if its in earthed metal conduit, which its doubtful you will have the tools to work with.

Quote:
I want to put some power sockets in our new conservatory. I am planning to spur it off a socket in the living room (drill through the wall).


You do realise that this is going to have to be a fused spur, right?
Back to top
 Alert Moderators
victorvanderzel

from United Kingdom

Joined: 07 Sep 2005
Posts: 7
Location: United Kingdom
Thanked: 0 times

PostPosted: Wed Sep 07, 2005 3:30 pm    Post Subject:
Reply with quote Thanks

Yep, I realise after reading some of the post on the forum I have to fuse the spur.

I guess I have to do a lot of chiseling in the wall then. The problem is how do I cross the doors? The only way is on the floor.

Thanks Victor
Back to top
 Alert Moderators
netsidedeveloper

from United Kingdom

Joined: 03 Oct 2005
Posts: 18
Location: United Kingdom
Thanked: 0 times

PostPosted: Mon Oct 03, 2005 7:11 pm    Post Subject:
Reply with quote Thanks

You can go vertically from the socket and run the cable horizontally along the top of the wall as long as it is no more than 150mm from the ceiling and then back down to a socket.
Back to top
 Alert Moderators
mapj1

from United Kingdom

Joined: 24 Nov 2004
Posts: 1040
Location: United Kingdom
Thanked: 0 times

PostPosted: Tue Oct 04, 2005 9:47 pm    Post Subject:
Reply with quote Thanks

Or bury in the floor as originally suggested, in plastic conduit if you can make it more than 2" below final surface, where its not directly beneath where it surfaces for a fitting.
Or use armourcald cable with an earthed armour.
Or equivalent mechanical protection, but this has to be very good to convince the sceptics.
Or surface wiring anywhere, as any damage will be seen, but unlikely to pass the domestic authority test!
hope that helps.

__________________
regards Mike(G7VZY)
-STICKY Reference Info @ top of forum, Has diagrams & answers to common probs-
Back to top
 Alert Moderators
Display posts from previous:   
  View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK All times are GMT
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
Ring mains cable running alongside mains gas? 6 540 Sun Jul 01, 2007 12:14 pm
Running a new mains cable 3 720 Sun Sep 14, 2003 2:48 pm
Running mains supply into Loft? 16 1040 Sat May 07, 2005 4:06 pm
Lots and lots of tiny LEDs running off the mains! 11 660 Fri Nov 30, 2007 2:17 pm
Running cable under a suspended floor. 8 580 Mon Aug 14, 2006 9:17 pm



DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
My DIYnot | Advertising | Newsletter
DIYnot.com | How to... | @home | Wiki | Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy.