2 x power showers
I have one exsisting power shower and wish to add a second power shower. Can I take the electrical feed from the exsisting power supply for the original shower by using a junction box? If so, can both showers be run at the same time?
Joined: 19 Jan 2005 Posts: 594 Location: United Kingdom Thanked: 2 times
Posted: Sun Apr 16, 2006 10:52 am Post Subject:
Err, I doubt it!
The cable size and mcb/fuse size would have been calcuated for the power rating (watts) of your original shower - adding another onto it would at least double the power requirement - this would then overload your cables and cause your mcb to operate.
Joined: 16 Nov 2005 Posts: 146 Location: United Kingdom Thanked: 0 times
Posted: Sun Apr 16, 2006 11:39 am Post Subject:
Do you know how the existing power shower is fed? From the ring main or a spur off the ring for example?
If it's a ring main then you could just spur off the existing supply at the point that feeds the first shower and feed the second shower via a second switched fuse spur. You can also do that if the existing supply is a spur, or a radial. Slightly more complicated depending on what the set up is now.
No major load on power showers as it's just a supply for a pump really, but junction boxes are best avoided for reasons of access/testing at a later date.
Joined: 31 Mar 2006 Posts: 10752 Location: Birmingham, United Kingdom Thanked: 73 times
Posted: Sun Apr 16, 2006 1:18 pm Post Subject:
The power shower in our house is rated at just 75W. I assume most will be of a similar rating, so there should be no problems regarding overloading of cables. Just make sure both showers are definitely power showers. Also it is good practice to have your shower(s) protected by an RCD
Joined: 16 Apr 2006 Posts: 3 Location: Nairnshire, United Kingdom Thanked: 0 times
Posted: Mon Apr 17, 2006 7:58 am Post Subject:
Thanx....
Thanx to all who replied.
They both are power showers and thus just pumps. The paperwork supplied states that the cable required is 1mm and only needs to be 3 amp fused.
Original shower is fed by 2.5mm cable and was intending on taking a spur from that cable with a 2.5mm cable to feed the second shower. Original shower has it's own supply and comes from the main board with MCB protection.
Joined: 16 Nov 2005 Posts: 146 Location: United Kingdom Thanked: 0 times
Posted: Mon Apr 17, 2006 8:20 am Post Subject:
Yes, but better to continue the circuit from the existing fused spur, (first shower) and on to your second fused spur, (second shower) rather than use a junction box. Easier to carry out the required tests.
Have you considered the hot water requirement when running two showers? Might be worth asking the plumbers if you haven't?
Joined: 21 Oct 2004 Posts: 19532 Location: United Kingdom Thanked: 6 times
Posted: Mon Apr 17, 2006 8:58 am Post Subject:
Har_vey wrote:
YHave you considered the hot water requirement when running two showers?
Just check the manufacturer's instructions, and ensure that your cold storage is adequate. If you run out of hot water first then it's just uncomfortable, but running out of cold first is potentially dangerous, so also check that the DHW outlet from the CSS is higher than the cold outlet.
Joined: 16 Apr 2006 Posts: 3 Location: Nairnshire, United Kingdom Thanked: 0 times
Posted: Mon Apr 17, 2006 3:23 pm Post Subject:
Thanx again for your replies.
Have spoken to a plumber and a sparky mate of mine.
Plumber said no problems with cold water pressure. Would cope well with two running. Unlikely that both will be on at same time anyway.
Sparky said no problems with my plan of a spur from first shower, but recommended taking the feed for the second shower from the ring main for the sockets. Worked out much easier that way anyway.