Can i create a new ring by running a spur off an existing ring to a 30 amp MCB then use this as the \\\'consumer unit\\\' for a new ring? |
|
BR

Joined: 31 Dec 2003 Posts: 334 Location: Ireland Thanked: 0 times
|
Posted: Mon Jan 05, 2004 4:18 pm Post Subject: |
 |
|
The simple answer to your question is – definitely NOT!!. A spur can only supply a single socket outlet (the outlet itself may be single or double).
You have two options:
1. Extend the existing ring
2. Install a new ring protected by 32A MCB/RCD at the board,
The second being the better option. |
|
Toml

Joined: 05 Jan 2004 Posts: 22 Location: United Kingdom Thanked: 0 times
|
Posted: Mon Jan 05, 2004 4:30 pm Post Subject: |
 |
|
thanks, i am in the middle of converting my loft, i will extend the ring from the floor below, it only has three double sockets on it. Is there a limit to the number of sockets i can have on a ring?
cheers  |
|
BR

Joined: 31 Dec 2003 Posts: 334 Location: Ireland Thanked: 0 times
|
Posted: Mon Jan 05, 2004 4:38 pm Post Subject: |
 |
|
No, provided the total floor area does not exceed 100m2 |
|