Posted: Sat Jul 15, 2006 10:57 am Post Subject: Shed Cable |
 |
|
Am considering running a power supply to my shed. I have been told that 2.5mm SWA will be ok for a socket and a light (thats all that will fit in it!!). Is this correct or am I better off going for 4mm or 6mm SWA??? |
|
breezer

Joined: 03 Jan 2003 Posts: 23346 Location: Sussex, United Kingdom Thanked: 5 times
|
Posted: Sat Jul 15, 2006 11:09 am Post Subject: |
 |
|
depends on loads of parameters, try a search __________________ Do you like music Mr Finch?
Forum = Opinions |
|
MadMatt

Joined: 14 Jul 2006 Posts: 6 Location: Cheshire, United Kingdom Thanked: 0 times
|
Posted: Sat Jul 15, 2006 2:59 pm Post Subject: |
 |
|
Its about 30 metres in cable terms from the CU to the shed. Intention is to run a double socket and an interior light from it, with the possibility of adding outside light(s) and possibly a pond pump at a later date. |
|
RF Lighting

Joined: 31 Mar 2006 Posts: 10752 Location: Birmingham, United Kingdom Thanked: 73 times
|
Posted: Sat Jul 15, 2006 3:41 pm Post Subject: |
 |
|
Personally I would go for a 4.0mm² armoured.
For the difference in price, which is about £6 for your 30 meter run (based on 2.5mm² Vs 4.0mm² 2 core SWA)
This will allow you to have a 32A supply to the shed. This will be plenty for a twin socket and a light. It will also have spare capacity for future expansion (as you mentioned)
You might want to consider fitting one of these |
|