distance from sink for 13amp fused spur

This topic originated from the How to page called Installing a power socket
Click here to return to the page called Installing a power socket.
Goto page 1, 2  Next
 
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK
  View previous topic :: View next topic  
Author Message
multitradenick

from United Kingdom

Joined: 26 Aug 2006
Posts: 5
Location: London,
United Kingdom
Thanked: 0 times

PostPosted: Sat Aug 26, 2006 7:47 pm    Post Subject:
distance from sink for 13amp fused spur
Reply with quote Thanks

I have been trying to locate regulations on how far a fused spur switch has to be from the kitchen sink doese anyone know latest regs? icon_question.gif
Back to top
 Alert Moderators

If you don't want to see this advert, click here to login or if you are new click here to join free.
RMS

from United Kingdom

Joined: 08 May 2006
Posts: 409
Location: United Kingdom
Thanked: 1 time

PostPosted: Sat Aug 26, 2006 8:00 pm    Post Subject:
Reply with quote Thanks

no specific regs to my knowledge,

300mm is common practice.
Back to top
 Alert Moderators
lcgs

from United Kingdom

Joined: 19 Feb 2006
Posts: 1653
Location: Nottingham,
United Kingdom
Thanked: 33 times

PostPosted: Sat Aug 26, 2006 8:21 pm    Post Subject:
Reply with quote Thanks

Nothing in the OSG or 16th but part p states that a minimum of 300mm is advisable.
Back to top
 Alert Moderators
Softus

from United Kingdom

Joined: 21 Oct 2004
Posts: 19532
Location: United Kingdom
Thanked: 6 times

PostPosted: Sun Aug 27, 2006 12:02 am    Post Subject:
Reply with quote Thanks

Back to top
 Alert Moderators
multitradenick

from United Kingdom

Joined: 26 Aug 2006
Posts: 5
Location: London,
United Kingdom
Thanked: 0 times

PostPosted: Sun Aug 27, 2006 12:44 am    Post Subject:
Thanks for the advice
Reply with quote Thanks

lcgs wrote:
Nothing in the OSG or 16th but part p states that a minimum of 300mm is advisable.
icon_smile.gif
Back to top
 Alert Moderators
dingbat

from United Kingdom

Joined: 29 Sep 2003
Posts: 2205
Location: West Midlands,
United Kingdom
Thanked: 0 times

PostPosted: Sun Aug 27, 2006 5:51 am    Post Subject:
Reply with quote Thanks

lcgs wrote:
Nothing in the OSG or 16th but part p states that a minimum of 300mm is advisable.


Part P actually states, "Reasonable provision shall be made in the design and installation of electrical installations in order to protect persons operating, maintaining or altering the installations from fire or injury." icon_wink.gif
Back to top
 Alert Moderators
lcgs

from United Kingdom

Joined: 19 Feb 2006
Posts: 1653
Location: Nottingham,
United Kingdom
Thanked: 33 times

PostPosted: Sun Aug 27, 2006 9:34 am    Post Subject:
Reply with quote Thanks

Part P and the IEE's guide to the building regs state "5.2.2.4 Accessories should be installed a minimum of 300mm from the edge of kitchen sinks and draining boards to reduce the risk of being splashed" icon_wink.gif
Back to top
 Alert Moderators
multitradenick

from United Kingdom

Joined: 26 Aug 2006
Posts: 5
Location: London,
United Kingdom
Thanked: 0 times

PostPosted: Sun Aug 27, 2006 9:39 am    Post Subject:
Thanks for the info brilliant site eh!
Reply with quote Thanks

dingbat wrote:
lcgs wrote:
Nothing in the OSG or 16th but part p states that a minimum of 300mm is advisable.


Part P actually states, "Reasonable provision shall be made in the design and installation of electrical installations in order to protect persons operating, maintaining or altering the installations from fire or injury." icon_wink.gif
icon_smile.gif icon_smile.gif icon_smile.gif
Back to top
 Alert Moderators
multitradenick

from United Kingdom

Joined: 26 Aug 2006
Posts: 5
Location: London,
United Kingdom
Thanked: 0 times

PostPosted: Sun Aug 27, 2006 9:45 am    Post Subject:
usefull discussion I will advise my client thankyou
Reply with quote Thanks

Back to top
 Alert Moderators
dingbat

from United Kingdom

Joined: 29 Sep 2003
Posts: 2205
Location: West Midlands,
United Kingdom
Thanked: 0 times

PostPosted: Sun Aug 27, 2006 11:50 am    Post Subject:
Reply with quote Thanks

lcgs wrote:
Part P and the IEE's guide to the building regs state "5.2.2.4 Accessories should be installed a minimum of 300mm from the edge of kitchen sinks and draining boards to reduce the risk of being splashed" icon_wink.gif


Icgs, you are confusing regulations with advice. Part P has nothing to say about how to carry out the work in order to comply; the Building Regulations tell you what you have to achieve, not how you achieve it. The Approved Documents do offer some advice, but in the case of AD-P the main advice is to follow BS 7671. There is no regulation whatsoever that specifies a minimum distance, rather that accessories should be suitable and suitably protected for their location, but the 300mm recommendation is generally recognised as being good practice. This recommendation appears in a number of publications but it is not a rule.

My objection to your posts is simply the inaccuarcy of your terminology.
Back to top
 Alert Moderators
lcgs

from United Kingdom

Joined: 19 Feb 2006
Posts: 1653
Location: Nottingham,
United Kingdom
Thanked: 33 times

PostPosted: Sun Aug 27, 2006 1:46 pm    Post Subject:
Reply with quote Thanks

Ok i agree not the best wording but from what i've been led to believe the regs when they cahnge to 17th will also include kitchens as they are notifiable under part p and are not covered anywhere yet.i thought part p is the rules and if you work to BS7671 you will fulfill most of the criteria but you need to refer to the part p document and other information to ensure that your work also meets LABC criteria.
we are happy with 300mm if suitability allows though aren't we? icon_lol.gif
Back to top
 Alert Moderators
Spark123

from United Kingdom

Joined: 02 Jun 2005
Posts: 10887
Location: Cumbria,
United Kingdom
Thanked: 39 times

PostPosted: Sun Aug 27, 2006 2:10 pm    Post Subject:
Reply with quote Thanks

In a nutshell, Part P is part of the Building regs which are law. In order to comply with P1 of Part P (see dingbats post), one recognised method is to work to BS7671. The wiring regs for other EU member states can also be used instead of BS7671.
The rest of Part P babbles on about whats notifiable and whats not.
Back to top
 Alert Moderators
securespark

from United Kingdom

Joined: 11 Jan 2004
Posts: 16485
Location: Cheshire,
United Kingdom
Thanked: 14 times

PostPosted: Mon Aug 28, 2006 3:54 pm    Post Subject:
Reply with quote Thanks

It's VERY easy to come on here and berate all the folk who post the building regs about their "advisory" 300mm rule.

The simple fact is that the regs are not specific about distances - all they say is that equipment shall be suitable for the conditions in which it is installed.

So why not take common sense, and use the advisory guidance of the building regs?

Most people here know that putting an electrical accessory too close to a sink is not sensible.
As for us pro's, if we put a switch too close to sink and our customers had an accident, our necks would be on the block. So why put yourselves at risk?

__________________
As George Michael once said, "..if you're gonna do it, do it right, right?"
Back to top
 Alert Moderators
didthathurt

from United Kingdom

Joined: 19 Aug 2006
Posts: 311
Location: Kent,
United Kingdom
Thanked: 0 times

PostPosted: Tue Aug 29, 2006 6:38 am    Post Subject:
Reply with quote Thanks

Just to add another little nugget; whilst the 300mm "rule" is, indeed, not a rule at all, one of the defences in common law to a negligence claim is to show that industry norms were followed such that a reasonable group of professionals would consider that the job was done to current professional standards. Conversely, not following such norms would, effectively, shift the burden of proof to the installer such that he or she would have to show why it was reasonable, in all the circumstances of the case, to have worked outside of accepted practises. In a nutshell, it's one of those areas that you'd have to make sure you had a convincing reasoned argument for doing. The Law does not, generally, accept convenience or the avoidance of extra work - even a lot of extra work - as a defence in these areas.

__________________
Being a professional doesn't mean I'm any good - just that I get paid for doing it!
Back to top
 Alert Moderators
dingbat

from United Kingdom

Joined: 29 Sep 2003
Posts: 2205
Location: West Midlands,
United Kingdom
Thanked: 0 times

PostPosted: Tue Aug 29, 2006 8:03 am    Post Subject:
Reply with quote Thanks

lcgs wrote:
... from what i've been led to believe the regs when they cahnge to 17th will also include kitchens as they are notifiable under part p and are not covered anywhere yet.i thought part p is the rules and if you work to BS7671 you will fulfill most of the criteria but you need to refer to the part p document and other information to ensure that your work also meets LABC criteria.


Terminology again. Even many so-called professionals have been too lazy to read anything for themselves and have accepted the 'advice' of colleagues, etc, without question. So let's be clear about what we mean.

Kitchens are covered by BS 7671; practically all electrical installations are (read page 11).
But they are not considered a 'special location' - locations with an inherent increased risk due to their nature (water, nakedness, mud and animals, principally... although not necessarily all at the same time. icon_wink.gif ).

P is just a section/chapter/part of the Building Regulations. The principle means of complying with the single sentence that actually is Part P (see my first post in this thread) is to comply with BS 7671. Part P does not introduce any additional electrical regulations.

Kitchens have been one of the most abused areas of domestic electrical installations and usually house the highest demand appliances, hence their special status for notification, in order to better control the atrocities oft-committed therein.

You must also comply with all other relevant sections of the building regs. This has always been the case (well, since 1965 anyway) but has been largely ignored where building control has not been involved.

LABC enforce those very same Building Regs - those are their criteria.

So, you see, it's all very logical and quite clear if you take the time to understand what everything actually means.
Back to top
 Alert Moderators
Display posts from previous:   
  View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK All times are GMT
Goto page 1, 2  Next
Page 1 of 2

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
13amp spur wired with only 1mm T&E - change to a fused s 9 2500 Mon May 16, 2005 10:32 pm
socket spur safe distance from kitchen sink 7 820 Sat Mar 22, 2008 10:55 pm
What is the safe distance between kitchen sink and cooker? 4 400 Thu May 21, 2009 9:26 am
Socket distance to sink and shaver socket distance to basin 17 2220 Mon Jan 08, 2007 7:40 pm
SOCKET DISTANCE FROM SINK? 16 1960 Thu Nov 08, 2007 12:08 am



DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
My DIYnot | Advertising | Newsletter
DIYnot.com | How to... | @home | Wiki | Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy.