SethDavy

from United Kingdom

Joined: 16 Sep 2006
Posts: 2
Location: United Kingdom

PostPosted: Sat Sep 16, 2006 8:54 pm Reply with quote

Does BS 7671 require a 70mm 4 core SWA have to have a separate earth conductor, or is it legal to just use the armouring within the cable?
Back to top
 Alert Moderators

If you do not want to see this advert, click here to login or if you are new click here to join free.
RF Lighting

from United Kingdom

Joined: 31 Mar 2006
Posts: 17322
Location: Leeds,
United Kingdom
Thanked: 908 times

PostPosted: Sat Sep 16, 2006 9:05 pm Reply with quote

Not quite the answer you were after, but this may help you to work it out.

http://www.batt.co.uk/images/pics/7529ArmourResistanceBS5467.pdf

Select the actual csa of the cable from manufacturers data or BS 6346 for PVC cables or BS 5467 or 6724 for XLPE cables.

Then apply to this formula.Cable equivalent CSA =k2/k1 X actual SWA section.

Where k1 is the phase conductor k value from table 43A BS7671 and k2 is CPC k value from tables 54D and E BS7671.

This will give you an equivalent cable csa, sheathed in the same insulation as the cable you are dealing with.
Back to top
 Alert Moderators
ricicle

from United Kingdom

Joined: 14 Sep 2006
Posts: 6295
Location: Gloucestershire,
United Kingdom
Thanked: 374 times

PostPosted: Sat Sep 16, 2006 9:13 pm Reply with quote

I personally would run a seperate cpc with this size of cable.The size would be S/2 = 35mm.This size of cable would be either for a long run (high impedance armouring-steel higher resistance per meter than copper), or for a large single load with high fault current,again higher I2r means more heat under fault conditions or as a sub main needing to ensure that x number of circuits do not have a failed/poor earth if corrosion were to occur

Ricicle
Back to top
 Alert Moderators
Spark123

from United Kingdom

Joined: 02 Jun 2005
Posts: 14190
Location: Cumbria,
United Kingdom
Thanked: 398 times

PostPosted: Sat Sep 16, 2006 9:23 pm Reply with quote

70mm 4C XPLE SWA is compliant with table 54G so only the armour needs to be used (subject to normal design procedures.)
http://wiki.diynot.com/electrics:earthing_supply_types_and_bonding:swa_earthing
Back to top
 Alert Moderators
RF Lighting

from United Kingdom

Joined: 31 Mar 2006
Posts: 17322
Location: Leeds,
United Kingdom
Thanked: 908 times

PostPosted: Sat Sep 16, 2006 9:31 pm Reply with quote

I went looking for that table in the wiki, but looked under cable types > SWA icon_confused.gif

Could you put a link to it there aswell?
Back to top
 Alert Moderators
Spark123

from United Kingdom

Joined: 02 Jun 2005
Posts: 14190
Location: Cumbria,
United Kingdom
Thanked: 398 times

PostPosted: Sat Sep 16, 2006 9:39 pm Reply with quote

OKay, I've put a little link at the bottom icon_biggrin.gif
Back to top
 Alert Moderators
SethDavy

from United Kingdom

Joined: 16 Sep 2006
Posts: 2
Location: United Kingdom

PostPosted: Sat Sep 16, 2006 9:49 pm Reply with quote

Thanks for your replies. If I have done my sums right, I get Rf's formula to
CSA = K2/K1 x actual SWA section
51/115 x 70 = 31.043
If this is right, the answer is less than the 35mm that ricicle suggests.
The cable used is BS6343, so Spark123's table won't apply.
We have just completed an installation in an industrial unit. The customers landlord's electricians installed the 70mm incomer. Also this cable has been jointed. They haven't used a steel enclosure and glands, just with what looks like lugs and bolts and a lot of tape. I feel that there should be a separate earth but the landlord's people are having none of it.
Back to top
 Alert Moderators
Spark123

from United Kingdom

Joined: 02 Jun 2005
Posts: 14190
Location: Cumbria,
United Kingdom
Thanked: 398 times

PostPosted: Sat Sep 16, 2006 9:53 pm Reply with quote

The formula you need to use is K1s/2K2= Req min SWA size
Do you mean BS6346?
70mm has an armour CSA of 138mm, k1 = 115, k2 = 51, required size is 79mm so is compliant with 54G.
Bit OTT for a garden shed or garage though icon_biggrin.gif
Back to top
 Alert Moderators
fattony

from United Kingdom

Joined: 01 May 2006
Posts: 810
Location: United Kingdom
Thanked: 1 time

PostPosted: Sat Sep 16, 2006 10:31 pm Reply with quote

Are you saying that once the armour csa reaches a certain size a seperate earth is not required? I never knew that I would have run a seperate earth but dont use cables that size.

At what point do you stop using 3 core and start running a seperate cpc?
Back to top
 Alert Moderators
Spark123

from United Kingdom

Joined: 02 Jun 2005
Posts: 14190
Location: Cumbria,
United Kingdom
Thanked: 398 times

PostPosted: Sat Sep 16, 2006 10:40 pm Reply with quote

One of the main logical reasons for using 3 core on single phase is so it automatically complies with table 54G. In 3 phase and neutral installations though you may need to run an additional earth cable in adjacent.
You can use the armour as the earth providing it complies with table 54G or the adiabatic subject to normal design procedures i.e. if it is to be used as part of a main eq bonding in PME then it needs to be 10mm (or DNO requirement) copper equivalent etc.
Fattony wrote:

At what point do you stop using 3 core and start running a seperate cpc?

Firstly before you buy the 3 core you can determine wether or not the armour is sufficient to act as the CPC (or bonding conductor etc), either by 54G OR the adiabatic. If the armour on a 2 core is sufficient then why buy 3 core?
If 2 core does not comply on a single phase circuit then you can buy 3 core and are guaranteed for it to comply with 54G.

edit;
Have added a 70C SWA chart into the Wiki.
Back to top
 Alert Moderators
ban-all-sheds

from United Kingdom

Joined: 27 Aug 2003
Posts: 46651
Location: London,
United Kingdom
Thanked: 1686 times

PostPosted: Sun Sep 17, 2006 10:29 am Reply with quote

Spark123 wrote:
If the armour on a 2 core is sufficient then why buy 3 core?

1) So that you don't have to rely on the integrity of the armour, either the quality of its connection via the glands, or its long-term condition if any water gets in and rusts it?

2) To use one core as a main bonding conductor for PME installations?
Back to top
 Alert Moderators
Spark123

from United Kingdom

Joined: 02 Jun 2005
Posts: 14190
Location: Cumbria,
United Kingdom
Thanked: 398 times

PostPosted: Sun Sep 17, 2006 9:19 pm Reply with quote

Point taken on a cable corroding after being damaged by spade etc. You could argue the cable glands need to be connected to the CPC at both ends or even regular intervals for the armour to be effective in the event of it corroding due to water ingress possibly at more than one point, although as the armoured strands are galvanized this may be ott.
Is it a fair point to make that you cannot take into account every eventuallity however hard you try, the cable should not get damaged if installed correctly either in the ground or on a tray, if a cable is damaged by spade, impact etc it should be repaired before being back filled. The glands if made off correctly and the cable being secured correctly mean they shouldn't get pulled out.
Wouldn't the armour comply with being used as part of a main equipotential bond as long as its csa is greater than 10mm copper equivalent (providing 10mm acceptable by DNO)?
Back to top
 Alert Moderators
ban-all-sheds

from United Kingdom

Joined: 27 Aug 2003
Posts: 46651
Location: London,
United Kingdom
Thanked: 1686 times

PostPosted: Mon Sep 18, 2006 1:14 am Reply with quote

Spark123 wrote:
Wouldn't the armour comply with being used as part of a main equipotential bond as long as its csa is greater than 10mm copper equivalent (providing 10mm acceptable by DNO)?

Good point.
Back to top
 Alert Moderators
Search this topic :: View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK All times are GMT
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
Nicked live core - heat shrink OK? 8 300 Tue Mar 29, 2011 9:19 am
How to wire a 2 core plug for '60s Revox Tape Machine? Help! 30 1120 Sat Apr 02, 2011 8:02 pm
3-core SWA colours 18 720 Tue Apr 12, 2011 3:49 pm
Voltage on 5 core cable ? 3 160 Tue Mar 22, 2011 6:08 pm
Core drilling for extractor fan 14 920 Mon Feb 21, 2011 12:36 pm


 
DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
Network | Advertising | Newsletter
DIY | DIY How To | @home | DIY Wiki | DIY Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy. Copyright © 2000-2014 DIYnot Limited.