Does BS 7671 require a 70mm 4 core SWA have to have a separate earth conductor, or is it legal to just use the armouring within the cable? |
|
| Back to top |
|
|
|
If you do not want to see this advert, click here to login or if you are new click here to join free. |
 |
RF Lighting

Joined: 31 Mar 2006 Posts: 16159 Location: Leeds, United Kingdom Thanked: 723 times
|
Posted: Sat Sep 16, 2006 9:05 pm |
|
|
Not quite the answer you were after, but this may help you to work it out.
http://www.batt.co.uk/images/pics/7529ArmourResistanceBS5467.pdf
Select the actual csa of the cable from manufacturers data or BS 6346 for PVC cables or BS 5467 or 6724 for XLPE cables.
Then apply to this formula.Cable equivalent CSA =k2/k1 X actual SWA section.
Where k1 is the phase conductor k value from table 43A BS7671 and k2 is CPC k value from tables 54D and E BS7671.
This will give you an equivalent cable csa, sheathed in the same insulation as the cable you are dealing with. |
|
| Back to top |
|
|
|
 |
ricicle

Joined: 14 Sep 2006 Posts: 6040 Location: Gloucestershire, United Kingdom Thanked: 342 times
|
Posted: Sat Sep 16, 2006 9:13 pm |
|
|
I personally would run a seperate cpc with this size of cable.The size would be S/2 = 35mm.This size of cable would be either for a long run (high impedance armouring-steel higher resistance per meter than copper), or for a large single load with high fault current,again higher I2r means more heat under fault conditions or as a sub main needing to ensure that x number of circuits do not have a failed/poor earth if corrosion were to occur
Ricicle |
|
| Back to top |
|
|
|
 |
Spark123

Joined: 02 Jun 2005 Posts: 13760 Location: Cumbria, United Kingdom Thanked: 343 times
|
Posted: Sat Sep 16, 2006 9:23 pm |
|
|
|
|
| Back to top |
|
|
|
 |
RF Lighting

Joined: 31 Mar 2006 Posts: 16159 Location: Leeds, United Kingdom Thanked: 723 times
|
Posted: Sat Sep 16, 2006 9:31 pm |
|
|
I went looking for that table in the wiki, but looked under cable types > SWA
Could you put a link to it there aswell? |
|
| Back to top |
|
|
|
 |
Spark123

Joined: 02 Jun 2005 Posts: 13760 Location: Cumbria, United Kingdom Thanked: 343 times
|
|
| Back to top |
|
|
|
 |
SethDavy

Joined: 16 Sep 2006 Posts: 2 Location: United Kingdom
|
Posted: Sat Sep 16, 2006 9:49 pm |
|
|
Thanks for your replies. If I have done my sums right, I get Rf's formula to
CSA = K2/K1 x actual SWA section
51/115 x 70 = 31.043
If this is right, the answer is less than the 35mm that ricicle suggests.
The cable used is BS6343, so Spark123's table won't apply.
We have just completed an installation in an industrial unit. The customers landlord's electricians installed the 70mm incomer. Also this cable has been jointed. They haven't used a steel enclosure and glands, just with what looks like lugs and bolts and a lot of tape. I feel that there should be a separate earth but the landlord's people are having none of it. |
|
| Back to top |
|
|
|
|
|
 |
Spark123

Joined: 02 Jun 2005 Posts: 13760 Location: Cumbria, United Kingdom Thanked: 343 times
|
Posted: Sat Sep 16, 2006 9:53 pm |
|
|
The formula you need to use is K1s/2K2= Req min SWA size
Do you mean BS6346?
70mm² has an armour CSA of 138mm², k1 = 115, k2 = 51, required size is 79mm² so is compliant with 54G.
Bit OTT for a garden shed or garage though  |
|
| Back to top |
|
|
|
 |
fattony

Joined: 01 May 2006 Posts: 804 Location: United Kingdom Thanked: 1 time
|
Posted: Sat Sep 16, 2006 10:31 pm |
|
|
Are you saying that once the armour csa reaches a certain size a seperate earth is not required? I never knew that I would have run a seperate earth but dont use cables that size.
At what point do you stop using 3 core and start running a seperate cpc? |
|
| Back to top |
|
|
|
 |
Spark123

Joined: 02 Jun 2005 Posts: 13760 Location: Cumbria, United Kingdom Thanked: 343 times
|
Posted: Sat Sep 16, 2006 10:40 pm |
|
|
One of the main logical reasons for using 3 core on single phase is so it automatically complies with table 54G. In 3 phase and neutral installations though you may need to run an additional earth cable in adjacent.
You can use the armour as the earth providing it complies with table 54G or the adiabatic subject to normal design procedures i.e. if it is to be used as part of a main eq bonding in PME then it needs to be 10mm² (or DNO requirement) copper equivalent etc.
| Fattony wrote: |
At what point do you stop using 3 core and start running a seperate cpc?
|
Firstly before you buy the 3 core you can determine wether or not the armour is sufficient to act as the CPC (or bonding conductor etc), either by 54G OR the adiabatic. If the armour on a 2 core is sufficient then why buy 3 core?
If 2 core does not comply on a single phase circuit then you can buy 3 core and are guaranteed for it to comply with 54G.
edit;
Have added a 70ºC SWA chart into the Wiki. |
|
| Back to top |
|
|
|
 |
ban-all-sheds

Joined: 27 Aug 2003 Posts: 41403 Location: London, United Kingdom Thanked: 1339 times
|
Posted: Sun Sep 17, 2006 10:29 am |
|
|
| Spark123 wrote: | | If the armour on a 2 core is sufficient then why buy 3 core? |
1) So that you don't have to rely on the integrity of the armour, either the quality of its connection via the glands, or its long-term condition if any water gets in and rusts it?
2) To use one core as a main bonding conductor for PME installations? |
|
| Back to top |
|
|
|
 |
Spark123

Joined: 02 Jun 2005 Posts: 13760 Location: Cumbria, United Kingdom Thanked: 343 times
|
Posted: Sun Sep 17, 2006 9:19 pm |
|
|
Point taken on a cable corroding after being damaged by spade etc. You could argue the cable glands need to be connected to the CPC at both ends or even regular intervals for the armour to be effective in the event of it corroding due to water ingress possibly at more than one point, although as the armoured strands are galvanized this may be ott.
Is it a fair point to make that you cannot take into account every eventuallity however hard you try, the cable should not get damaged if installed correctly either in the ground or on a tray, if a cable is damaged by spade, impact etc it should be repaired before being back filled. The glands if made off correctly and the cable being secured correctly mean they shouldn't get pulled out.
Wouldn't the armour comply with being used as part of a main equipotential bond as long as its csa is greater than 10mm² copper equivalent (providing 10mm² acceptable by DNO)? |
|
| Back to top |
|
|
|
 |
ban-all-sheds

Joined: 27 Aug 2003 Posts: 41403 Location: London, United Kingdom Thanked: 1339 times
|
Posted: Mon Sep 18, 2006 1:14 am |
|
|
| Spark123 wrote: | | Wouldn't the armour comply with being used as part of a main equipotential bond as long as its csa is greater than 10mm² copper equivalent (providing 10mm² acceptable by DNO)? |
Good point. |
|