Outside Flood light
Reply with quote Thanks

Hya dudes,

I'd like to install an outside 300w flood light on my new house. I\\\'m curently wondering if I should run the power from a ring main or internal lighting circut.

Would I need to add a fuse spur and switch box in both cases?

I've got a 300w flood light and some 1.5mm twin & earth and I\\\'ve bought and dry lining box(you know one that sinks into the wall) and a switch fused spur 13Amp. and a 20Amp junction box.

So Have I got the right gear? and which way is usually best these days ring main or lighting circut?


Last edited by Rizlaman78 on Mon Oct 09, 2006 7:21 pm, edited 1 time in total
Back to top
 Alert Moderators

If you don't want to see this advert, click here to login or if you are new click here to join free.
DESL

from United Kingdom

Joined: 09 Oct 2006
Posts: 936
Location: Essex,
United Kingdom
Thanked: 0 times

PostPosted: Mon Oct 09, 2006 9:24 am    Post Subject:
Reply with quote Thanks

It can be done either way

A lot depends on where the nearest circuit is to connect to.

Probably better to take off from lighting circuit as the ring main will/should be protected by RCD and if it trips you'll have no flood light.

No problem using a FCU off lighting cicuit as long as you use a 3Amp fuse in it not 13Amp and to be honest it will be easier to wire in.
Back to top
 Alert Moderators
industryspark

from United Kingdom

Joined: 08 Jul 2006
Posts: 567
Location: Yorkshire,
United Kingdom
Thanked: 1 time

PostPosted: Mon Oct 09, 2006 5:53 pm    Post Subject:
Reply with quote Thanks

yep, go with the lighting circuit if possible, it'l be much easier to terminate and cram the wires in your fcu.

nice to see this being done properly for a change, seen loads with a flex from the light with a plug on that plugs into a socket inside the house, ok but ugly!

__________________
remember......a little bit of knowledge is often more dangerous than no knowledge at all!
Back to top
 Alert Moderators
Rizlaman78

from United Kingdom

Joined: 09 Oct 2006
Posts: 14
Location: Leeds,
United Kingdom
Thanked: 0 times

PostPosted: Mon Oct 09, 2006 7:20 pm    Post Subject:
Reply with quote Thanks

icon_wink.gif Cheers Dudes,

Looks like I'll be wiring up to lighting circut in the loft and then run it down to switch and out to light.

Whats the story with this artic flex stuff would I need to use some between the junction box and outside light?

And do you think I'll have part P iusses later.
Back to top
 Alert Moderators
securespark

from United Kingdom

Joined: 11 Jan 2004
Posts: 16490
Location: Cheshire,
United Kingdom
Thanked: 14 times

PostPosted: Mon Oct 09, 2006 7:57 pm    Post Subject:
Reply with quote Thanks

industryspark wrote:
yep, go with the lighting circuit if possible, it'l be much easier to terminate and cram the wires in your fcu.


But what about the load? And what if the 300W lamp is changed for a 500?

__________________
As George Michael once said, "..if you're gonna do it, do it right, right?"
Back to top
 Alert Moderators
industryspark

from United Kingdom

Joined: 08 Jul 2006
Posts: 567
Location: Yorkshire,
United Kingdom
Thanked: 1 time

PostPosted: Mon Oct 09, 2006 8:11 pm    Post Subject:
Reply with quote Thanks

Fair point secure spark, could be an issue.

300 watt is 1.25A so he should still have enough to play with even if he's got a lot of lights on!

unless he lives in a big house that is! icon_lol.gif

__________________
remember......a little bit of knowledge is often more dangerous than no knowledge at all!
Back to top
 Alert Moderators
Rizlaman78

from United Kingdom

Joined: 09 Oct 2006
Posts: 14
Location: Leeds,
United Kingdom
Thanked: 0 times

PostPosted: Mon Oct 09, 2006 8:29 pm    Post Subject:
Reply with quote Thanks

industryspark wrote:
Fair point secure spark, could be an issue.

300 watt is 1.25A so he should still have enough to play with even if he's got a lot of lights on!

unless he lives in a big house that is! icon_lol.gif


icon_rolleyes.gif A big house.....Dude I said it's a new house and these's days they build them small.

Anyway thanx man.

Erm what do you mean by secrure spark?

I figure that I'll take the power from the up stairs lighting ring (cos there's only about 5 lighting points up there and so I'll have more load to spare. I think icon_question.gif
Back to top
 Alert Moderators
Rizlaman78

from United Kingdom

Joined: 09 Oct 2006
Posts: 14
Location: Leeds,
United Kingdom
Thanked: 0 times

PostPosted: Mon Oct 09, 2006 9:00 pm    Post Subject:
The load
Reply with quote Thanks

MMMM Dudes,

I'just done some math and on this 300watt light is 1.25 Amps ok and I've 5x60 watt bulbs which gives me a total of 2.5 Amps.

So If I use 3 Amp fuse in the FCU it'll work yes OK, but If I change any lights later upwards in wattage then what will happen? Will the 3 amp fuse blow or will MCB cut out on CU. I think the MCB is rated at 6 amps, so that ok and should'nt trip out.

I have children so the lights up stairs are likely to be almost all on a some point.


Last edited by Rizlaman78 on Mon Oct 09, 2006 9:28 pm, edited 1 time in total
Back to top
 Alert Moderators
industryspark

from United Kingdom

Joined: 08 Jul 2006
Posts: 567
Location: Yorkshire,
United Kingdom
Thanked: 1 time

PostPosted: Mon Oct 09, 2006 9:18 pm    Post Subject:
Reply with quote Thanks

you will have a 6A mcb in the CU more than likely. this means the entire lighting circuit on this mcb(miniture circuit breaker) can take 6A before it trips.

if 1.25A is used up by your outside light you have over 4 and a half amps left for other fittings on the circuit.

a 60 watt bulb will use roughly 0.25A so you can see that you have enough for a few of these. overloading the circuit shouldnt ever really be a problem ( unless you add more outside lights)

the 3A fcu switch fuse protects only the outside light (or will when irs installed)

__________________
remember......a little bit of knowledge is often more dangerous than no knowledge at all!
Back to top
 Alert Moderators
Rizlaman78

from United Kingdom

Joined: 09 Oct 2006
Posts: 14
Location: Leeds,
United Kingdom
Thanked: 0 times

PostPosted: Mon Oct 09, 2006 9:36 pm    Post Subject:
Reply with quote Thanks

industryspark wrote:
you will have a 6A mcb in the CU more than likely. this means the entire lighting circuit on this mcb(miniture circuit breaker) can take 6A before it trips.

if 1.25A is used up by your outside light you have over 4 and a half amps left for other fittings on the circuit.

a 60 watt bulb will use roughly 0.25A so you can see that you have enough for a few of these. overloading the circuit shouldnt ever really be a problem ( unless you add more outside lights)

the 3A fcu switch fuse protects only the outside light (or will when irs installed)



icon_biggrin.gif Cheers mate thats right I'm abit rusty on this, I did a 236 part 1 about 10 years ago and I've never really a chance to use the knowledge.


Last edited by Rizlaman78 on Mon Oct 09, 2006 9:40 pm, edited 1 time in total
Back to top
 Alert Moderators
RF Lighting

from United Kingdom

Joined: 31 Mar 2006
Posts: 10752
Location: Birmingham,
United Kingdom
Thanked: 73 times

PostPosted: Mon Oct 09, 2006 9:39 pm    Post Subject:
Reply with quote Thanks

Rizlaman78 wrote:
I did a 236 part 1 about 10 years ago


So did I.

Where did you go to college?

__________________
I downlights
Back to top
 Alert Moderators
Rizlaman78

from United Kingdom

Joined: 09 Oct 2006
Posts: 14
Location: Leeds,
United Kingdom
Thanked: 0 times

PostPosted: Mon Oct 09, 2006 9:42 pm    Post Subject:
Reply with quote Thanks

RF Lighting wrote:
Rizlaman78 wrote:
I did a 236 part 1 about 10 years ago


So did I.

Where did you go to college?



Kitson college in Leeds west yorkshire.
Back to top
 Alert Moderators
RF Lighting

from United Kingdom

Joined: 31 Mar 2006
Posts: 10752
Location: Birmingham,
United Kingdom
Thanked: 73 times

PostPosted: Mon Oct 09, 2006 11:38 pm    Post Subject:
Reply with quote Thanks

wow me too.

Did you have the joys of lectures from Malcolm Jackson?

I was also taught by Paul Birkby, Andy raynor, Steve Brough and 'the legend' Mark Gallager

__________________
I downlights
Back to top
 Alert Moderators
Rizlaman78

from United Kingdom

Joined: 09 Oct 2006
Posts: 14
Location: Leeds,
United Kingdom
Thanked: 0 times

PostPosted: Tue Oct 10, 2006 7:37 pm    Post Subject:
Reply with quote Thanks

Dude

Afew of the names ring a bell
Back to top
 Alert Moderators
Rizlaman78

from United Kingdom

Joined: 09 Oct 2006
Posts: 14
Location: Leeds,
United Kingdom
Thanked: 0 times

PostPosted: Thu Oct 12, 2006 11:06 pm    Post Subject:
Reply with quote Thanks

HI there again,

I'am gonna have to chase a line down the wall to where I want to put the switch for the light.

But does anyone know the minium and maxium depth, for chasing out a wall for a T&E cable & capping?

As I seem to remember something about it, and it was to a certain depth and it had to have a protective capping over it.

My wall is brick and then cavitiy and then breeze block, and then there's a small gap between the plasterboard and the breeze block.
Back to top
 Alert Moderators
Display posts from previous:   
  View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK All times are GMT
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
500 watt flood light V 2 400 Mon Oct 22, 2007 9:25 pm
Quick question re installing a flood light 13 520 Sun Jun 29, 2008 6:48 pm
Flood light staying on 3 280 Thu Jul 24, 2008 8:50 pm
Flood light Cable 7 540 Mon Oct 22, 2007 12:45 pm
Flood light with a dimmer switch 6 260 Fri Sep 26, 2008 5:10 pm



DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
My DIYnot | Advertising | Newsletter
DIYnot.com | How to... | @home | Wiki | Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy.