outdoor cable woes
Hi, need some help on what cable to use to power my Garage ?? well to cut a long story short my garage was powered when we moved into our house a few years ago but over the last couple of days the RCD to the garage keeps tripping out, the cable is armoured but it only looks like 4 core 2.5mm , my garage has a 3kw heater keeping my pride and joy dry (R1) 2 double plug sockets, 2 strip light and 6 outdoor lights (60w bulbs)..cant think of anything else so if ive missed any vital info that you need to know please ask.
Joined: 26 Sep 2006 Posts: 672 Location: London, United Kingdom Thanked: 6 times
Posted: Fri Dec 29, 2006 4:45 pm Post Subject:
Where is the RCD that is tripping out? Type and rating?
Is there a CU in the garage? What is in it? Suppling what circuits?
How is the feed connected back at the main CU?
What is providing overcurrent protection to the garage feed at the consumer unit in the house - MCB, RCBO? - what type and rating of device (picture if you are not sure).
What is the length of the cable run from Cu to Garage?
Joined: 26 Sep 2006 Posts: 672 Location: London, United Kingdom Thanked: 6 times
Posted: Fri Dec 29, 2006 5:00 pm Post Subject:
breezer wrote:
true, but its still unlikely to be the cable, also there is no rcd in the garage, since the op said..........."RCD to the garage
Maybe - I always like to have the full picture. Not everyone uses language in the same way and I've seen people say "to" when they mean "in" more than once.
Joined: 15 Nov 2005 Posts: 24037 Location: Hampshire, United Kingdom Thanked: 54 times
Posted: Fri Dec 29, 2006 5:25 pm Post Subject:
It is more likely to be something damp in the garage. Try unplugging everything and see if that fixes it. Then plug them back in one at a time.
If not, turn off the main switch of the garage CU. If it still trips it is something between the house CU and the garage CU (and there's not much there except the cable.)
If you have any external junction boxes,sockets, switches or lamps, examine them for water ingress. Water can also run down the cable where it enters the building unless it has a drip loop.
Edited: In your pic it is the MCB that looks tripped, not the RCD. Please elucidate.
Last edited by JohnD on Fri Dec 29, 2006 5:27 pm, edited 1 time in total
Joined: 29 Dec 2006 Posts: 10 Location: Derbyshire, United Kingdom Thanked: 0 times
Posted: Fri Dec 29, 2006 5:38 pm Post Subject:
cheers for the replys guys, i have done as instructed turned the main cu off in the garage but the rcd still trips in the house....i know you say its not the swa cable but i have had the whole area where the cable is block paved in november....personally i was putting it down to the cable only being 2.5 and thought it would me more suited to 4mm...but then again im no expert (thats why im here asking)